Wiring 2 totally different panels in series...ok?

Started by Wxboy, July 03, 2012, 08:49:13 AM

Previous topic - Next topic

Vic

OK,  Mike,

Then we do agree on that.

The only other point that I was trying to make,  was that the SW 255's voltage will rise above the stated Vmp,  because THAT Vmp was for the stated Imp of 8.15 A.  The smaller PV will limit the string current to 7.11 A,  so the 255 will have a bit higher Vmp.

This was what I was referring to when I said that I was too lazy to calc the String Vmp.
Vic