175A Inverter input panel breaker

Started by EW Zuber, May 16, 2014, 06:37:16 PM

Previous topic - Next topic

EW Zuber

I have a 175A Midnite panel breaker that has markings on the terminals listed as 1 and 2. From what I have been reading on these forums there is no assigned line or load on these, is that correct?
(6) Solar World 175 watt, (14) Arco Solar 33 Watt, (15) REC 250 watt, 2KW Whirlwind turbine on 85' rohn 25 tower, Outback VFX 3648, Outback FM80 and Midnite Classic 150 w/WBJR, ( 8 ) Trojan L-16REB, 
WL7BDK

Halfcrazy

the 175 is not polarized so there is no line or load. Actually thats true for ALL of our panel mount MNEDC breakers
Changing the way wind turbines operate one smoke filled box at a time