05/29/2016	13:00:04	System: Web user 'apc' logged in from 192.168.1.60.
05/29/2016	12:55:59	UPS: Switched to battery backup power.
05/29/2016	12:55:55	UPS: Returned from AVR Trim.
05/29/2016	12:55:52	UPS: Invalid internal diagnostic self-test.
05/29/2016	12:55:52	UPS: Battery charger failure.
05/29/2016	12:55:52	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	12:55:52	UPS: Communications established.
05/29/2016	12:55:41	System: Network service started. System IP is 192.168.1.220 from manually configured settings.
05/29/2016	12:55:34	System: Coldstart.
05/29/2016	12:55:00	System: Network service started. System IP is 192.168.1.220 from manually configured settings.
05/29/2016	12:54:52	System: Coldstart.
05/29/2016	07:09:13	UPS: Turned off due to a low battery.
05/29/2016	07:00:31	UPS: Switched to battery backup power.
05/29/2016	07:00:27	UPS: Returned from AVR Trim.
05/29/2016	07:00:22	UPS: Returned from battery backup power.
05/29/2016	07:00:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	07:00:17	UPS: Switched to battery backup power.
05/29/2016	07:00:13	UPS: Returned from AVR Trim.
05/29/2016	07:00:09	UPS: Returned from battery backup power.
05/29/2016	07:00:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:59:19	UPS: Switched to battery backup power.
05/29/2016	06:59:16	UPS: Returned from AVR Trim.
05/29/2016	06:59:11	UPS: Returned from battery backup power.
05/29/2016	06:59:11	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:58:45	UPS: Switched to battery backup power.
05/29/2016	06:58:41	UPS: Returned from AVR Trim.
05/29/2016	06:58:37	UPS: Returned from battery backup power.
05/29/2016	06:58:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:58:31	UPS: Switched to battery backup power.
05/29/2016	06:58:27	UPS: Returned from AVR Trim.
05/29/2016	06:58:22	UPS: Returned from battery backup power.
05/29/2016	06:58:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:58:16	UPS: Switched to battery backup power.
05/29/2016	06:58:12	UPS: Returned from AVR Trim.
05/29/2016	06:58:07	UPS: Returned from battery backup power.
05/29/2016	06:58:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:57:39	UPS: Switched to battery backup power.
05/29/2016	06:57:35	UPS: Returned from AVR Trim.
05/29/2016	06:57:30	UPS: Returned from battery backup power.
05/29/2016	06:57:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:56:52	UPS: Switched to battery backup power.
05/29/2016	06:56:49	UPS: Returned from AVR Trim.
05/29/2016	06:56:44	UPS: Returned from battery backup power.
05/29/2016	06:56:44	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:56:36	UPS: Switched to battery backup power.
05/29/2016	06:56:32	UPS: Returned from AVR Trim.
05/29/2016	06:56:27	UPS: Returned from battery backup power.
05/29/2016	06:56:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:56:13	UPS: Switched to battery backup power.
05/29/2016	06:56:09	UPS: Returned from AVR Trim.
05/29/2016	06:56:04	UPS: Returned from battery backup power.
05/29/2016	06:56:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:55:50	UPS: Switched to battery backup power.
05/29/2016	06:55:46	UPS: Returned from AVR Trim.
05/29/2016	06:55:41	UPS: Returned from battery backup power.
05/29/2016	06:55:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:55:27	UPS: Switched to battery backup power.
05/29/2016	06:55:24	UPS: Returned from AVR Trim.
05/29/2016	06:55:19	UPS: Returned from battery backup power.
05/29/2016	06:55:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:55:07	UPS: Switched to battery backup power.
05/29/2016	06:55:03	UPS: Returned from AVR Trim.
05/29/2016	06:55:00	UPS: Returned from battery backup power.
05/29/2016	06:55:00	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:54:51	UPS: Switched to battery backup power.
05/29/2016	06:54:47	UPS: Returned from AVR Trim.
05/29/2016	06:54:42	UPS: Returned from battery backup power.
05/29/2016	06:54:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:54:36	UPS: Switched to battery backup power.
05/29/2016	06:54:32	UPS: Returned from AVR Trim.
05/29/2016	06:54:27	UPS: Returned from battery backup power.
05/29/2016	06:54:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:54:11	UPS: Switched to battery backup power.
05/29/2016	06:54:08	UPS: Returned from AVR Trim.
05/29/2016	06:54:03	UPS: Returned from battery backup power.
05/29/2016	06:54:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:53:52	UPS: Switched to battery backup power.
05/29/2016	06:53:48	UPS: Returned from AVR Trim.
05/29/2016	06:53:43	UPS: Returned from battery backup power.
05/29/2016	06:53:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:53:32	UPS: Switched to battery backup power.
05/29/2016	06:53:28	UPS: Returned from AVR Trim.
05/29/2016	06:53:23	UPS: Returned from battery backup power.
05/29/2016	06:53:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:53:12	UPS: Switched to battery backup power.
05/29/2016	06:53:08	UPS: Returned from AVR Trim.
05/29/2016	06:53:03	UPS: Returned from battery backup power.
05/29/2016	06:53:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:52:57	UPS: Switched to battery backup power.
05/29/2016	06:52:53	UPS: Returned from AVR Trim.
05/29/2016	06:52:48	UPS: Returned from battery backup power.
05/29/2016	06:52:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:52:38	UPS: Switched to battery backup power.
05/29/2016	06:52:35	UPS: Returned from AVR Trim.
05/29/2016	06:52:30	UPS: Returned from battery backup power.
05/29/2016	06:52:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:52:19	UPS: Switched to battery backup power.
05/29/2016	06:52:16	UPS: Returned from AVR Trim.
05/29/2016	06:52:11	UPS: Returned from battery backup power.
05/29/2016	06:52:11	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:52:00	UPS: Switched to battery backup power.
05/29/2016	06:51:56	UPS: Returned from AVR Trim.
05/29/2016	06:51:51	UPS: Returned from battery backup power.
05/29/2016	06:51:51	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:51:42	UPS: Switched to battery backup power.
05/29/2016	06:51:38	UPS: Returned from AVR Trim.
05/29/2016	06:51:33	UPS: Returned from battery backup power.
05/29/2016	06:51:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:51:22	UPS: Switched to battery backup power.
05/29/2016	06:51:18	UPS: Returned from AVR Trim.
05/29/2016	06:51:14	UPS: Returned from battery backup power.
05/29/2016	06:51:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:51:07	UPS: Switched to battery backup power.
05/29/2016	06:51:03	UPS: Returned from AVR Trim.
05/29/2016	06:50:58	UPS: Returned from battery backup power.
05/29/2016	06:50:58	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:50:49	UPS: Switched to battery backup power.
05/29/2016	06:50:45	UPS: Returned from AVR Trim.
05/29/2016	06:50:40	UPS: Returned from battery backup power.
05/29/2016	06:50:40	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:50:32	UPS: Switched to battery backup power.
05/29/2016	06:50:28	UPS: Returned from AVR Trim.
05/29/2016	06:50:23	UPS: Returned from battery backup power.
05/29/2016	06:50:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:50:14	UPS: Switched to battery backup power.
05/29/2016	06:50:10	UPS: Returned from AVR Trim.
05/29/2016	06:50:06	UPS: Returned from battery backup power.
05/29/2016	06:50:06	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:49:56	UPS: Switched to battery backup power.
05/29/2016	06:49:52	UPS: Returned from AVR Trim.
05/29/2016	06:49:48	UPS: Returned from battery backup power.
05/29/2016	06:49:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:49:38	UPS: Switched to battery backup power.
05/29/2016	06:49:34	UPS: Returned from AVR Trim.
05/29/2016	06:49:30	UPS: Returned from battery backup power.
05/29/2016	06:49:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:49:22	UPS: Switched to battery backup power.
05/29/2016	06:49:18	UPS: Returned from AVR Trim.
05/29/2016	06:49:13	UPS: Returned from battery backup power.
05/29/2016	06:49:13	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:49:04	UPS: Switched to battery backup power.
05/29/2016	06:49:00	UPS: Returned from AVR Trim.
05/29/2016	06:48:55	UPS: Returned from battery backup power.
05/29/2016	06:48:55	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:48:45	UPS: Switched to battery backup power.
05/29/2016	06:48:41	UPS: Returned from AVR Trim.
05/29/2016	06:48:36	UPS: Returned from battery backup power.
05/29/2016	06:48:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:48:27	UPS: Switched to battery backup power.
05/29/2016	06:48:24	UPS: Returned from AVR Trim.
05/29/2016	06:48:19	UPS: Returned from battery backup power.
05/29/2016	06:48:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:48:09	UPS: Switched to battery backup power.
05/29/2016	06:48:05	UPS: Returned from AVR Trim.
05/29/2016	06:48:00	UPS: Returned from battery backup power.
05/29/2016	06:48:00	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:47:50	UPS: Switched to battery backup power.
05/29/2016	06:47:47	UPS: Returned from AVR Trim.
05/29/2016	06:47:42	UPS: Returned from battery backup power.
05/29/2016	06:47:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:47:34	UPS: Switched to battery backup power.
05/29/2016	06:47:30	UPS: Returned from AVR Trim.
05/29/2016	06:47:26	UPS: Returned from battery backup power.
05/29/2016	06:47:26	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:47:17	UPS: Switched to battery backup power.
05/29/2016	06:47:14	UPS: Returned from AVR Trim.
05/29/2016	06:47:09	UPS: Returned from battery backup power.
05/29/2016	06:47:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:46:59	UPS: Switched to battery backup power.
05/29/2016	06:46:56	UPS: Returned from AVR Trim.
05/29/2016	06:46:51	UPS: Returned from battery backup power.
05/29/2016	06:46:51	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:46:41	UPS: Switched to battery backup power.
05/29/2016	06:46:38	UPS: Returned from AVR Trim.
05/29/2016	06:46:33	UPS: Returned from battery backup power.
05/29/2016	06:46:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:46:25	UPS: Switched to battery backup power.
05/29/2016	06:46:21	UPS: Returned from AVR Trim.
05/29/2016	06:46:16	UPS: Returned from battery backup power.
05/29/2016	06:46:16	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:46:07	UPS: Switched to battery backup power.
05/29/2016	06:46:04	UPS: Returned from AVR Trim.
05/29/2016	06:45:59	UPS: Returned from battery backup power.
05/29/2016	06:45:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:45:50	UPS: Switched to battery backup power.
05/29/2016	06:45:46	UPS: Returned from AVR Trim.
05/29/2016	06:45:42	UPS: Returned from battery backup power.
05/29/2016	06:45:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:45:33	UPS: Switched to battery backup power.
05/29/2016	06:45:29	UPS: Returned from AVR Trim.
05/29/2016	06:45:24	UPS: Returned from battery backup power.
05/29/2016	06:45:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:45:15	UPS: Switched to battery backup power.
05/29/2016	06:45:11	UPS: Returned from AVR Trim.
05/29/2016	06:45:07	UPS: Returned from battery backup power.
05/29/2016	06:45:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:44:55	UPS: Switched to battery backup power.
05/29/2016	06:44:52	UPS: Returned from AVR Trim.
05/29/2016	06:44:47	UPS: Returned from battery backup power.
05/29/2016	06:44:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:44:36	UPS: Switched to battery backup power.
05/29/2016	06:44:32	UPS: Returned from AVR Trim.
05/29/2016	06:44:27	UPS: Returned from battery backup power.
05/29/2016	06:44:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:44:16	UPS: Switched to battery backup power.
05/29/2016	06:44:12	UPS: Returned from AVR Trim.
05/29/2016	06:44:07	UPS: Returned from battery backup power.
05/29/2016	06:44:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:43:56	UPS: Switched to battery backup power.
05/29/2016	06:43:52	UPS: Returned from AVR Trim.
05/29/2016	06:43:47	UPS: Returned from battery backup power.
05/29/2016	06:43:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:43:37	UPS: Switched to battery backup power.
05/29/2016	06:43:34	UPS: Returned from AVR Trim.
05/29/2016	06:43:29	UPS: Returned from battery backup power.
05/29/2016	06:43:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:43:18	UPS: Switched to battery backup power.
05/29/2016	06:43:14	UPS: Returned from AVR Trim.
05/29/2016	06:43:09	UPS: Returned from battery backup power.
05/29/2016	06:43:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:42:58	UPS: Switched to battery backup power.
05/29/2016	06:42:54	UPS: Returned from AVR Trim.
05/29/2016	06:42:49	UPS: Returned from battery backup power.
05/29/2016	06:42:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:42:39	UPS: Switched to battery backup power.
05/29/2016	06:42:35	UPS: Returned from AVR Trim.
05/29/2016	06:42:32	UPS: Returned from battery backup power.
05/29/2016	06:42:32	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:42:24	UPS: Switched to battery backup power.
05/29/2016	06:42:20	UPS: Returned from AVR Trim.
05/29/2016	06:42:15	UPS: Returned from battery backup power.
05/29/2016	06:42:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:42:06	UPS: Switched to battery backup power.
05/29/2016	06:42:02	UPS: Returned from AVR Trim.
05/29/2016	06:41:57	UPS: Returned from battery backup power.
05/29/2016	06:41:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:41:47	UPS: Switched to battery backup power.
05/29/2016	06:41:43	UPS: Returned from AVR Trim.
05/29/2016	06:41:38	UPS: Returned from battery backup power.
05/29/2016	06:41:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:41:26	UPS: Switched to battery backup power.
05/29/2016	06:41:22	UPS: Returned from AVR Trim.
05/29/2016	06:41:17	UPS: Returned from battery backup power.
05/29/2016	06:41:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:41:08	UPS: Switched to battery backup power.
05/29/2016	06:41:04	UPS: Returned from AVR Trim.
05/29/2016	06:40:59	UPS: Returned from battery backup power.
05/29/2016	06:40:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:40:49	UPS: Switched to battery backup power.
05/29/2016	06:40:45	UPS: Returned from AVR Trim.
05/29/2016	06:40:41	UPS: Returned from battery backup power.
05/29/2016	06:40:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:40:34	UPS: Switched to battery backup power.
05/29/2016	06:40:30	UPS: Returned from AVR Trim.
05/29/2016	06:40:25	UPS: Returned from battery backup power.
05/29/2016	06:40:25	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:40:18	UPS: Switched to battery backup power.
05/29/2016	06:40:14	UPS: Returned from AVR Trim.
05/29/2016	06:40:09	UPS: Returned from battery backup power.
05/29/2016	06:40:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:40:01	UPS: Switched to battery backup power.
05/29/2016	06:39:57	UPS: Returned from AVR Trim.
05/29/2016	06:39:53	UPS: Returned from battery backup power.
05/29/2016	06:39:53	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:39:44	UPS: Switched to battery backup power.
05/29/2016	06:39:41	UPS: Returned from AVR Trim.
05/29/2016	06:39:36	UPS: Returned from battery backup power.
05/29/2016	06:39:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:39:28	UPS: Switched to battery backup power.
05/29/2016	06:39:25	UPS: Returned from AVR Trim.
05/29/2016	06:39:20	UPS: Returned from battery backup power.
05/29/2016	06:39:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:39:11	UPS: Switched to battery backup power.
05/29/2016	06:39:07	UPS: Returned from AVR Trim.
05/29/2016	06:39:03	UPS: Returned from battery backup power.
05/29/2016	06:39:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:38:54	UPS: Switched to battery backup power.
05/29/2016	06:38:51	UPS: Returned from AVR Trim.
05/29/2016	06:38:46	UPS: Returned from battery backup power.
05/29/2016	06:38:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:38:38	UPS: Switched to battery backup power.
05/29/2016	06:38:35	UPS: Returned from AVR Trim.
05/29/2016	06:38:30	UPS: Returned from battery backup power.
05/29/2016	06:38:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:38:21	UPS: Switched to battery backup power.
05/29/2016	06:38:18	UPS: Returned from AVR Trim.
05/29/2016	06:38:13	UPS: Returned from battery backup power.
05/29/2016	06:38:13	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:38:04	UPS: Switched to battery backup power.
05/29/2016	06:38:01	UPS: Returned from AVR Trim.
05/29/2016	06:37:56	UPS: Returned from battery backup power.
05/29/2016	06:37:56	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:37:47	UPS: Switched to battery backup power.
05/29/2016	06:37:43	UPS: Returned from AVR Trim.
05/29/2016	06:37:39	UPS: Returned from battery backup power.
05/29/2016	06:37:39	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:37:30	UPS: Switched to battery backup power.
05/29/2016	06:37:26	UPS: Returned from AVR Trim.
05/29/2016	06:37:21	UPS: Returned from battery backup power.
05/29/2016	06:37:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:37:12	UPS: Switched to battery backup power.
05/29/2016	06:37:08	UPS: Returned from AVR Trim.
05/29/2016	06:37:04	UPS: Returned from battery backup power.
05/29/2016	06:37:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:36:58	UPS: Switched to battery backup power.
05/29/2016	06:36:54	UPS: Returned from AVR Trim.
05/29/2016	06:36:49	UPS: Returned from battery backup power.
05/29/2016	06:36:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:36:41	UPS: Switched to battery backup power.
05/29/2016	06:36:38	UPS: Returned from AVR Trim.
05/29/2016	06:36:33	UPS: Returned from battery backup power.
05/29/2016	06:36:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:36:26	UPS: Switched to battery backup power.
05/29/2016	06:36:22	UPS: Returned from AVR Trim.
05/29/2016	06:36:17	UPS: Returned from battery backup power.
05/29/2016	06:36:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:36:09	UPS: Switched to battery backup power.
05/29/2016	06:36:05	UPS: Returned from AVR Trim.
05/29/2016	06:36:00	UPS: Returned from battery backup power.
05/29/2016	06:36:00	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:35:53	UPS: Switched to battery backup power.
05/29/2016	06:35:49	UPS: Returned from AVR Trim.
05/29/2016	06:35:44	UPS: Returned from battery backup power.
05/29/2016	06:35:44	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:35:37	UPS: Switched to battery backup power.
05/29/2016	06:35:33	UPS: Returned from AVR Trim.
05/29/2016	06:35:28	UPS: Returned from battery backup power.
05/29/2016	06:35:28	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:35:20	UPS: Switched to battery backup power.
05/29/2016	06:35:17	UPS: Returned from AVR Trim.
05/29/2016	06:35:12	UPS: Returned from battery backup power.
05/29/2016	06:35:12	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:35:05	UPS: Switched to battery backup power.
05/29/2016	06:35:02	UPS: Returned from AVR Trim.
05/29/2016	06:34:57	UPS: Returned from battery backup power.
05/29/2016	06:34:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:34:48	UPS: Switched to battery backup power.
05/29/2016	06:34:44	UPS: Returned from AVR Trim.
05/29/2016	06:34:40	UPS: Returned from battery backup power.
05/29/2016	06:34:40	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:34:29	UPS: Switched to battery backup power.
05/29/2016	06:34:26	UPS: Returned from AVR Trim.
05/29/2016	06:34:21	UPS: Returned from battery backup power.
05/29/2016	06:34:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:34:10	UPS: Switched to battery backup power.
05/29/2016	06:34:06	UPS: Returned from AVR Trim.
05/29/2016	06:34:01	UPS: Returned from battery backup power.
05/29/2016	06:34:01	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:33:50	UPS: Switched to battery backup power.
05/29/2016	06:33:47	UPS: Returned from AVR Trim.
05/29/2016	06:33:42	UPS: Returned from battery backup power.
05/29/2016	06:33:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:33:30	UPS: Switched to battery backup power.
05/29/2016	06:33:26	UPS: Returned from AVR Trim.
05/29/2016	06:33:22	UPS: Returned from battery backup power.
05/29/2016	06:33:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:33:15	UPS: Switched to battery backup power.
05/29/2016	06:33:12	UPS: Returned from AVR Trim.
05/29/2016	06:33:07	UPS: Returned from battery backup power.
05/29/2016	06:33:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:32:58	UPS: Switched to battery backup power.
05/29/2016	06:32:54	UPS: Returned from AVR Trim.
05/29/2016	06:32:49	UPS: Returned from battery backup power.
05/29/2016	06:32:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:32:37	UPS: Switched to battery backup power.
05/29/2016	06:32:33	UPS: Returned from AVR Trim.
05/29/2016	06:32:29	UPS: Returned from battery backup power.
05/29/2016	06:32:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:32:12	UPS: Switched to battery backup power.
05/29/2016	06:32:08	UPS: Returned from AVR Trim.
05/29/2016	06:32:04	UPS: Returned from battery backup power.
05/29/2016	06:32:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:31:43	UPS: Switched to battery backup power.
05/29/2016	06:31:39	UPS: Returned from AVR Trim.
05/29/2016	06:31:34	UPS: Returned from battery backup power.
05/29/2016	06:31:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:31:28	UPS: Switched to battery backup power.
05/29/2016	06:31:24	UPS: Returned from AVR Trim.
05/29/2016	06:31:19	UPS: Returned from battery backup power.
05/29/2016	06:31:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:31:12	UPS: Switched to battery backup power.
05/29/2016	06:31:08	UPS: Returned from AVR Trim.
05/29/2016	06:31:04	UPS: Returned from battery backup power.
05/29/2016	06:31:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:30:49	UPS: Switched to battery backup power.
05/29/2016	06:30:45	UPS: Returned from AVR Trim.
05/29/2016	06:30:40	UPS: Returned from battery backup power.
05/29/2016	06:30:40	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:30:24	UPS: Switched to battery backup power.
05/29/2016	06:30:20	UPS: Returned from AVR Trim.
05/29/2016	06:30:15	UPS: Returned from battery backup power.
05/29/2016	06:30:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:29:59	UPS: Switched to battery backup power.
05/29/2016	06:29:55	UPS: Returned from AVR Trim.
05/29/2016	06:29:50	UPS: Returned from battery backup power.
05/29/2016	06:29:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:29:29	UPS: Switched to battery backup power.
05/29/2016	06:29:25	UPS: Returned from AVR Trim.
05/29/2016	06:29:20	UPS: Returned from battery backup power.
05/29/2016	06:29:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:28:59	UPS: Switched to battery backup power.
05/29/2016	06:28:55	UPS: Returned from AVR Trim.
05/29/2016	06:28:50	UPS: Returned from battery backup power.
05/29/2016	06:28:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:28:38	UPS: Switched to battery backup power.
05/29/2016	06:28:34	UPS: Returned from AVR Trim.
05/29/2016	06:28:29	UPS: Returned from battery backup power.
05/29/2016	06:28:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:28:17	UPS: Switched to battery backup power.
05/29/2016	06:28:13	UPS: Returned from AVR Trim.
05/29/2016	06:28:08	UPS: Returned from battery backup power.
05/29/2016	06:28:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:27:54	UPS: Switched to battery backup power.
05/29/2016	06:27:51	UPS: Returned from AVR Trim.
05/29/2016	06:27:46	UPS: Returned from battery backup power.
05/29/2016	06:27:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:27:32	UPS: Switched to battery backup power.
05/29/2016	06:27:28	UPS: Returned from AVR Trim.
05/29/2016	06:27:24	UPS: Returned from battery backup power.
05/29/2016	06:27:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:27:10	UPS: Switched to battery backup power.
05/29/2016	06:27:06	UPS: Returned from AVR Trim.
05/29/2016	06:27:02	UPS: Returned from battery backup power.
05/29/2016	06:27:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:26:49	UPS: Switched to battery backup power.
05/29/2016	06:26:46	UPS: Returned from AVR Trim.
05/29/2016	06:26:41	UPS: Returned from battery backup power.
05/29/2016	06:26:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:26:28	UPS: Switched to battery backup power.
05/29/2016	06:26:24	UPS: Returned from AVR Trim.
05/29/2016	06:26:19	UPS: Returned from battery backup power.
05/29/2016	06:26:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:26:06	UPS: Switched to battery backup power.
05/29/2016	06:26:02	UPS: Returned from AVR Trim.
05/29/2016	06:25:58	UPS: Returned from battery backup power.
05/29/2016	06:25:58	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:25:44	UPS: Switched to battery backup power.
05/29/2016	06:25:41	UPS: Returned from AVR Trim.
05/29/2016	06:25:36	UPS: Returned from battery backup power.
05/29/2016	06:25:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:25:22	UPS: Switched to battery backup power.
05/29/2016	06:25:19	UPS: Returned from AVR Trim.
05/29/2016	06:25:14	UPS: Returned from battery backup power.
05/29/2016	06:25:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:23:30	UPS: Switched to battery backup power.
05/29/2016	06:23:26	UPS: Returned from AVR Trim.
05/29/2016	06:23:21	UPS: Returned from battery backup power.
05/29/2016	06:23:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:23:16	UPS: Switched to battery backup power.
05/29/2016	06:23:12	UPS: Returned from AVR Trim.
05/29/2016	06:23:08	UPS: Returned from battery backup power.
05/29/2016	06:23:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:21:24	UPS: Switched to battery backup power.
05/29/2016	06:21:20	UPS: Returned from AVR Trim.
05/29/2016	06:21:15	UPS: Returned from battery backup power.
05/29/2016	06:21:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:20:56	UPS: Switched to battery backup power.
05/29/2016	06:20:52	UPS: Returned from AVR Trim.
05/29/2016	06:20:47	UPS: Returned from battery backup power.
05/29/2016	06:20:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:20:43	UPS: Switched to battery backup power.
05/29/2016	06:20:39	UPS: Returned from AVR Trim.
05/29/2016	06:20:34	UPS: Returned from battery backup power.
05/29/2016	06:20:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:20:30	UPS: Switched to battery backup power.
05/29/2016	06:20:26	UPS: Returned from AVR Trim.
05/29/2016	06:20:21	UPS: Returned from battery backup power.
05/29/2016	06:20:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:20:17	UPS: Switched to battery backup power.
05/29/2016	06:20:13	UPS: Returned from AVR Trim.
05/29/2016	06:20:08	UPS: Returned from battery backup power.
05/29/2016	06:20:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:20:04	UPS: Switched to battery backup power.
05/29/2016	06:20:00	UPS: Returned from AVR Trim.
05/29/2016	06:19:55	UPS: Returned from battery backup power.
05/29/2016	06:19:55	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:19:51	UPS: Switched to battery backup power.
05/29/2016	06:19:47	UPS: Returned from AVR Trim.
05/29/2016	06:19:43	UPS: Returned from battery backup power.
05/29/2016	06:19:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:19:38	UPS: Switched to battery backup power.
05/29/2016	06:19:34	UPS: Returned from AVR Trim.
05/29/2016	06:19:29	UPS: Returned from battery backup power.
05/29/2016	06:19:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:19:25	UPS: Switched to battery backup power.
05/29/2016	06:19:21	UPS: Returned from AVR Trim.
05/29/2016	06:19:16	UPS: Returned from battery backup power.
05/29/2016	06:19:16	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:19:11	UPS: Switched to battery backup power.
05/29/2016	06:19:07	UPS: Returned from AVR Trim.
05/29/2016	06:19:02	UPS: Returned from battery backup power.
05/29/2016	06:19:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:18:57	UPS: Switched to battery backup power.
05/29/2016	06:18:53	UPS: Returned from AVR Trim.
05/29/2016	06:18:48	UPS: Returned from battery backup power.
05/29/2016	06:18:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:18:43	UPS: Switched to battery backup power.
05/29/2016	06:18:39	UPS: Returned from AVR Trim.
05/29/2016	06:18:35	UPS: Returned from battery backup power.
05/29/2016	06:18:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:18:31	UPS: Switched to battery backup power.
05/29/2016	06:18:27	UPS: Returned from AVR Trim.
05/29/2016	06:18:22	UPS: Returned from battery backup power.
05/29/2016	06:18:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:18:18	UPS: Switched to battery backup power.
05/29/2016	06:18:14	UPS: Returned from AVR Trim.
05/29/2016	06:18:09	UPS: Returned from battery backup power.
05/29/2016	06:18:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:18:05	UPS: Switched to battery backup power.
05/29/2016	06:18:01	UPS: Returned from AVR Trim.
05/29/2016	06:17:56	UPS: Returned from battery backup power.
05/29/2016	06:17:56	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:17:52	UPS: Switched to battery backup power.
05/29/2016	06:17:48	UPS: Returned from AVR Trim.
05/29/2016	06:17:43	UPS: Returned from battery backup power.
05/29/2016	06:17:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:17:40	UPS: Switched to battery backup power.
05/29/2016	06:17:37	UPS: Returned from AVR Trim.
05/29/2016	06:17:32	UPS: Returned from battery backup power.
05/29/2016	06:17:32	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:17:28	UPS: Switched to battery backup power.
05/29/2016	06:17:24	UPS: Returned from AVR Trim.
05/29/2016	06:17:19	UPS: Returned from battery backup power.
05/29/2016	06:17:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:17:15	UPS: Switched to battery backup power.
05/29/2016	06:17:12	UPS: Returned from AVR Trim.
05/29/2016	06:17:07	UPS: Returned from battery backup power.
05/29/2016	06:17:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:17:03	UPS: Switched to battery backup power.
05/29/2016	06:16:59	UPS: Returned from AVR Trim.
05/29/2016	06:16:54	UPS: Returned from battery backup power.
05/29/2016	06:16:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:16:50	UPS: Switched to battery backup power.
05/29/2016	06:16:47	UPS: Returned from AVR Trim.
05/29/2016	06:16:42	UPS: Returned from battery backup power.
05/29/2016	06:16:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:16:38	UPS: Switched to battery backup power.
05/29/2016	06:16:34	UPS: Returned from AVR Trim.
05/29/2016	06:16:29	UPS: Returned from battery backup power.
05/29/2016	06:16:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:16:25	UPS: Switched to battery backup power.
05/29/2016	06:16:22	UPS: Returned from AVR Trim.
05/29/2016	06:16:17	UPS: Returned from battery backup power.
05/29/2016	06:16:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:16:13	UPS: Switched to battery backup power.
05/29/2016	06:16:09	UPS: Returned from AVR Trim.
05/29/2016	06:16:05	UPS: Returned from battery backup power.
05/29/2016	06:16:05	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:16:01	UPS: Switched to battery backup power.
05/29/2016	06:15:58	UPS: Returned from AVR Trim.
05/29/2016	06:15:53	UPS: Returned from battery backup power.
05/29/2016	06:15:53	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:15:49	UPS: Switched to battery backup power.
05/29/2016	06:15:45	UPS: Returned from AVR Trim.
05/29/2016	06:15:41	UPS: Returned from battery backup power.
05/29/2016	06:15:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:15:37	UPS: Switched to battery backup power.
05/29/2016	06:15:33	UPS: Returned from AVR Trim.
05/29/2016	06:15:28	UPS: Returned from battery backup power.
05/29/2016	06:15:28	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:15:24	UPS: Switched to battery backup power.
05/29/2016	06:15:20	UPS: Returned from AVR Trim.
05/29/2016	06:15:15	UPS: Returned from battery backup power.
05/29/2016	06:15:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:15:11	UPS: Switched to battery backup power.
05/29/2016	06:15:07	UPS: Returned from AVR Trim.
05/29/2016	06:15:03	UPS: Returned from battery backup power.
05/29/2016	06:15:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:14:58	UPS: Switched to battery backup power.
05/29/2016	06:14:54	UPS: Returned from AVR Trim.
05/29/2016	06:14:49	UPS: Returned from battery backup power.
05/29/2016	06:14:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:14:44	UPS: Switched to battery backup power.
05/29/2016	06:14:41	UPS: Returned from AVR Trim.
05/29/2016	06:14:36	UPS: Returned from battery backup power.
05/29/2016	06:14:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:14:31	UPS: Switched to battery backup power.
05/29/2016	06:14:27	UPS: Returned from AVR Trim.
05/29/2016	06:14:22	UPS: Returned from battery backup power.
05/29/2016	06:14:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:14:17	UPS: Switched to battery backup power.
05/29/2016	06:14:14	UPS: Returned from AVR Trim.
05/29/2016	06:14:09	UPS: Returned from battery backup power.
05/29/2016	06:14:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:14:04	UPS: Switched to battery backup power.
05/29/2016	06:14:00	UPS: Returned from AVR Trim.
05/29/2016	06:13:55	UPS: Returned from battery backup power.
05/29/2016	06:13:55	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:13:51	UPS: Switched to battery backup power.
05/29/2016	06:13:47	UPS: Returned from AVR Trim.
05/29/2016	06:13:42	UPS: Returned from battery backup power.
05/29/2016	06:13:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:13:37	UPS: Switched to battery backup power.
05/29/2016	06:13:34	UPS: Returned from AVR Trim.
05/29/2016	06:13:29	UPS: Returned from battery backup power.
05/29/2016	06:13:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:13:24	UPS: Switched to battery backup power.
05/29/2016	06:13:20	UPS: Returned from AVR Trim.
05/29/2016	06:13:15	UPS: Returned from battery backup power.
05/29/2016	06:13:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:13:11	UPS: Switched to battery backup power.
05/29/2016	06:13:08	UPS: Returned from AVR Trim.
05/29/2016	06:13:03	UPS: Returned from battery backup power.
05/29/2016	06:13:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:12:58	UPS: Switched to battery backup power.
05/29/2016	06:12:54	UPS: Returned from AVR Trim.
05/29/2016	06:12:50	UPS: Returned from battery backup power.
05/29/2016	06:12:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:12:46	UPS: Switched to battery backup power.
05/29/2016	06:12:42	UPS: Returned from AVR Trim.
05/29/2016	06:12:37	UPS: Returned from battery backup power.
05/29/2016	06:12:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:12:33	UPS: Switched to battery backup power.
05/29/2016	06:12:29	UPS: Returned from AVR Trim.
05/29/2016	06:12:24	UPS: Returned from battery backup power.
05/29/2016	06:12:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:12:20	UPS: Switched to battery backup power.
05/29/2016	06:12:17	UPS: Returned from AVR Trim.
05/29/2016	06:12:12	UPS: Returned from battery backup power.
05/29/2016	06:12:12	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:12:05	UPS: Switched to battery backup power.
05/29/2016	06:12:01	UPS: Returned from AVR Trim.
05/29/2016	06:11:56	UPS: Returned from battery backup power.
05/29/2016	06:11:56	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:11:52	UPS: Switched to battery backup power.
05/29/2016	06:11:48	UPS: Returned from AVR Trim.
05/29/2016	06:11:43	UPS: Returned from battery backup power.
05/29/2016	06:11:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:11:39	UPS: Switched to battery backup power.
05/29/2016	06:11:35	UPS: Returned from AVR Trim.
05/29/2016	06:11:31	UPS: Returned from battery backup power.
05/29/2016	06:11:31	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:11:27	UPS: Switched to battery backup power.
05/29/2016	06:11:23	UPS: Returned from AVR Trim.
05/29/2016	06:11:18	UPS: Returned from battery backup power.
05/29/2016	06:11:18	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:11:13	UPS: Switched to battery backup power.
05/29/2016	06:11:09	UPS: Returned from AVR Trim.
05/29/2016	06:11:04	UPS: Returned from battery backup power.
05/29/2016	06:11:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:11:00	UPS: Switched to battery backup power.
05/29/2016	06:10:56	UPS: Returned from AVR Trim.
05/29/2016	06:10:52	UPS: Returned from battery backup power.
05/29/2016	06:10:52	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:10:48	UPS: Switched to battery backup power.
05/29/2016	06:10:44	UPS: Returned from AVR Trim.
05/29/2016	06:10:39	UPS: Returned from battery backup power.
05/29/2016	06:10:39	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:10:35	UPS: Switched to battery backup power.
05/29/2016	06:10:32	UPS: Returned from AVR Trim.
05/29/2016	06:10:26	UPS: Returned from battery backup power.
05/29/2016	06:10:26	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:10:22	UPS: Switched to battery backup power.
05/29/2016	06:10:18	UPS: Returned from AVR Trim.
05/29/2016	06:10:13	UPS: Returned from battery backup power.
05/29/2016	06:10:13	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:10:08	UPS: Switched to battery backup power.
05/29/2016	06:10:04	UPS: Returned from AVR Trim.
05/29/2016	06:09:59	UPS: Returned from battery backup power.
05/29/2016	06:09:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:09:55	UPS: Switched to battery backup power.
05/29/2016	06:09:51	UPS: Returned from AVR Trim.
05/29/2016	06:09:46	UPS: Returned from battery backup power.
05/29/2016	06:09:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:09:42	UPS: Switched to battery backup power.
05/29/2016	06:09:38	UPS: Returned from AVR Trim.
05/29/2016	06:09:33	UPS: Returned from battery backup power.
05/29/2016	06:09:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:09:28	UPS: Switched to battery backup power.
05/29/2016	06:09:24	UPS: Returned from AVR Trim.
05/29/2016	06:09:19	UPS: Returned from battery backup power.
05/29/2016	06:09:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:09:15	UPS: Switched to battery backup power.
05/29/2016	06:09:11	UPS: Returned from AVR Trim.
05/29/2016	06:09:07	UPS: Returned from battery backup power.
05/29/2016	06:09:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:09:03	UPS: Switched to battery backup power.
05/29/2016	06:08:59	UPS: Returned from AVR Trim.
05/29/2016	06:08:54	UPS: Returned from battery backup power.
05/29/2016	06:08:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:08:47	UPS: Switched to battery backup power.
05/29/2016	06:08:43	UPS: Returned from AVR Trim.
05/29/2016	06:08:38	UPS: Returned from battery backup power.
05/29/2016	06:08:38	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:08:35	UPS: Switched to battery backup power.
05/29/2016	06:08:31	UPS: Returned from AVR Trim.
05/29/2016	06:08:26	UPS: Returned from battery backup power.
05/29/2016	06:08:26	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:08:21	UPS: Switched to battery backup power.
05/29/2016	06:08:17	UPS: Returned from AVR Trim.
05/29/2016	06:08:12	UPS: Returned from battery backup power.
05/29/2016	06:08:12	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:08:08	UPS: Switched to battery backup power.
05/29/2016	06:08:04	UPS: Returned from AVR Trim.
05/29/2016	06:07:59	UPS: Returned from battery backup power.
05/29/2016	06:07:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:07:54	UPS: Switched to battery backup power.
05/29/2016	06:07:50	UPS: Returned from AVR Trim.
05/29/2016	06:07:45	UPS: Returned from battery backup power.
05/29/2016	06:07:45	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:07:41	UPS: Switched to battery backup power.
05/29/2016	06:07:37	UPS: Returned from AVR Trim.
05/29/2016	06:07:32	UPS: Returned from battery backup power.
05/29/2016	06:07:32	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:07:27	UPS: Switched to battery backup power.
05/29/2016	06:07:24	UPS: Returned from AVR Trim.
05/29/2016	06:07:19	UPS: Returned from battery backup power.
05/29/2016	06:07:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:07:14	UPS: Switched to battery backup power.
05/29/2016	06:07:11	UPS: Returned from AVR Trim.
05/29/2016	06:07:06	UPS: Returned from battery backup power.
05/29/2016	06:07:06	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:06:59	UPS: Switched to battery backup power.
05/29/2016	06:06:55	UPS: Returned from AVR Trim.
05/29/2016	06:06:50	UPS: Returned from battery backup power.
05/29/2016	06:06:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:06:46	UPS: Switched to battery backup power.
05/29/2016	06:06:42	UPS: Returned from AVR Trim.
05/29/2016	06:06:37	UPS: Returned from battery backup power.
05/29/2016	06:06:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:06:32	UPS: Switched to battery backup power.
05/29/2016	06:06:29	UPS: Returned from AVR Trim.
05/29/2016	06:06:24	UPS: Returned from battery backup power.
05/29/2016	06:06:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:06:19	UPS: Switched to battery backup power.
05/29/2016	06:06:15	UPS: Returned from AVR Trim.
05/29/2016	06:06:10	UPS: Returned from battery backup power.
05/29/2016	06:06:10	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:06:06	UPS: Switched to battery backup power.
05/29/2016	06:06:02	UPS: Returned from AVR Trim.
05/29/2016	06:05:57	UPS: Returned from battery backup power.
05/29/2016	06:05:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:05:52	UPS: Switched to battery backup power.
05/29/2016	06:05:48	UPS: Returned from AVR Trim.
05/29/2016	06:05:43	UPS: Returned from battery backup power.
05/29/2016	06:05:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:05:39	UPS: Switched to battery backup power.
05/29/2016	06:05:35	UPS: Returned from AVR Trim.
05/29/2016	06:05:30	UPS: Returned from battery backup power.
05/29/2016	06:05:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:05:25	UPS: Switched to battery backup power.
05/29/2016	06:05:22	UPS: Returned from AVR Trim.
05/29/2016	06:05:17	UPS: Returned from battery backup power.
05/29/2016	06:05:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:05:10	UPS: Switched to battery backup power.
05/29/2016	06:05:06	UPS: Returned from AVR Trim.
05/29/2016	06:05:02	UPS: Returned from battery backup power.
05/29/2016	06:05:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:04:57	UPS: Switched to battery backup power.
05/29/2016	06:04:53	UPS: Returned from AVR Trim.
05/29/2016	06:04:48	UPS: Returned from battery backup power.
05/29/2016	06:04:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:04:43	UPS: Switched to battery backup power.
05/29/2016	06:04:40	UPS: Returned from AVR Trim.
05/29/2016	06:04:35	UPS: Returned from battery backup power.
05/29/2016	06:04:35	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:04:30	UPS: Switched to battery backup power.
05/29/2016	06:04:26	UPS: Returned from AVR Trim.
05/29/2016	06:04:21	UPS: Returned from battery backup power.
05/29/2016	06:04:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:04:17	UPS: Switched to battery backup power.
05/29/2016	06:04:13	UPS: Returned from AVR Trim.
05/29/2016	06:04:08	UPS: Returned from battery backup power.
05/29/2016	06:04:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:04:03	UPS: Switched to battery backup power.
05/29/2016	06:03:59	UPS: Returned from AVR Trim.
05/29/2016	06:03:55	UPS: Returned from battery backup power.
05/29/2016	06:03:55	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:03:50	UPS: Switched to battery backup power.
05/29/2016	06:03:46	UPS: Returned from AVR Trim.
05/29/2016	06:03:41	UPS: Returned from battery backup power.
05/29/2016	06:03:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:03:36	UPS: Switched to battery backup power.
05/29/2016	06:03:33	UPS: Returned from AVR Trim.
05/29/2016	06:03:28	UPS: Returned from battery backup power.
05/29/2016	06:03:28	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:03:23	UPS: Switched to battery backup power.
05/29/2016	06:03:19	UPS: Returned from AVR Trim.
05/29/2016	06:03:14	UPS: Returned from battery backup power.
05/29/2016	06:03:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:03:09	UPS: Switched to battery backup power.
05/29/2016	06:03:06	UPS: Returned from AVR Trim.
05/29/2016	06:03:01	UPS: Returned from battery backup power.
05/29/2016	06:03:01	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:02:56	UPS: Switched to battery backup power.
05/29/2016	06:02:52	UPS: Returned from AVR Trim.
05/29/2016	06:02:47	UPS: Returned from battery backup power.
05/29/2016	06:02:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:02:43	UPS: Switched to battery backup power.
05/29/2016	06:02:39	UPS: Returned from AVR Trim.
05/29/2016	06:02:34	UPS: Returned from battery backup power.
05/29/2016	06:02:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:02:29	UPS: Switched to battery backup power.
05/29/2016	06:02:25	UPS: Returned from AVR Trim.
05/29/2016	06:02:20	UPS: Returned from battery backup power.
05/29/2016	06:02:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:02:16	UPS: Switched to battery backup power.
05/29/2016	06:02:12	UPS: Returned from AVR Trim.
05/29/2016	06:02:07	UPS: Returned from battery backup power.
05/29/2016	06:02:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:02:02	UPS: Switched to battery backup power.
05/29/2016	06:01:59	UPS: Returned from AVR Trim.
05/29/2016	06:01:54	UPS: Returned from battery backup power.
05/29/2016	06:01:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:01:49	UPS: Switched to battery backup power.
05/29/2016	06:01:46	UPS: Returned from AVR Trim.
05/29/2016	06:01:41	UPS: Returned from battery backup power.
05/29/2016	06:01:40	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:01:36	UPS: Switched to battery backup power.
05/29/2016	06:01:32	UPS: Returned from AVR Trim.
05/29/2016	06:01:28	UPS: Returned from battery backup power.
05/29/2016	06:01:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:01:23	UPS: Switched to battery backup power.
05/29/2016	06:01:19	UPS: Returned from AVR Trim.
05/29/2016	06:01:14	UPS: Returned from battery backup power.
05/29/2016	06:01:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:01:10	UPS: Switched to battery backup power.
05/29/2016	06:01:06	UPS: Returned from AVR Trim.
05/29/2016	06:01:01	UPS: Returned from battery backup power.
05/29/2016	06:01:01	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:00:57	UPS: Switched to battery backup power.
05/29/2016	06:00:53	UPS: Returned from AVR Trim.
05/29/2016	06:00:47	UPS: Returned from battery backup power.
05/29/2016	06:00:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:00:43	UPS: Switched to battery backup power.
05/29/2016	06:00:39	UPS: Returned from AVR Trim.
05/29/2016	06:00:34	UPS: Returned from battery backup power.
05/29/2016	06:00:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:00:30	UPS: Switched to battery backup power.
05/29/2016	06:00:26	UPS: Returned from AVR Trim.
05/29/2016	06:00:21	UPS: Returned from battery backup power.
05/29/2016	06:00:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:00:16	UPS: Switched to battery backup power.
05/29/2016	06:00:12	UPS: Returned from AVR Trim.
05/29/2016	06:00:08	UPS: Returned from battery backup power.
05/29/2016	06:00:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	06:00:03	UPS: Switched to battery backup power.
05/29/2016	05:59:59	UPS: Returned from AVR Trim.
05/29/2016	05:59:54	UPS: Returned from battery backup power.
05/29/2016	05:59:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:59:50	UPS: Switched to battery backup power.
05/29/2016	05:59:46	UPS: Returned from AVR Trim.
05/29/2016	05:59:41	UPS: Returned from battery backup power.
05/29/2016	05:59:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:59:37	UPS: Switched to battery backup power.
05/29/2016	05:59:33	UPS: Returned from AVR Trim.
05/29/2016	05:59:28	UPS: Returned from battery backup power.
05/29/2016	05:59:28	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:59:24	UPS: Switched to battery backup power.
05/29/2016	05:59:20	UPS: Returned from AVR Trim.
05/29/2016	05:59:15	UPS: Returned from battery backup power.
05/29/2016	05:59:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:59:11	UPS: Switched to battery backup power.
05/29/2016	05:59:07	UPS: Returned from AVR Trim.
05/29/2016	05:59:02	UPS: Returned from battery backup power.
05/29/2016	05:59:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:58:58	UPS: Switched to battery backup power.
05/29/2016	05:58:54	UPS: Returned from AVR Trim.
05/29/2016	05:58:49	UPS: Returned from battery backup power.
05/29/2016	05:58:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:58:45	UPS: Switched to battery backup power.
05/29/2016	05:58:41	UPS: Returned from AVR Trim.
05/29/2016	05:58:36	UPS: Returned from battery backup power.
05/29/2016	05:58:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:58:32	UPS: Switched to battery backup power.
05/29/2016	05:58:28	UPS: Returned from AVR Trim.
05/29/2016	05:58:24	UPS: Returned from battery backup power.
05/29/2016	05:58:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:58:19	UPS: Switched to battery backup power.
05/29/2016	05:58:15	UPS: Returned from AVR Trim.
05/29/2016	05:58:10	UPS: Returned from battery backup power.
05/29/2016	05:58:10	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:58:06	UPS: Switched to battery backup power.
05/29/2016	05:58:02	UPS: Returned from AVR Trim.
05/29/2016	05:57:57	UPS: Returned from battery backup power.
05/29/2016	05:57:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:57:53	UPS: Switched to battery backup power.
05/29/2016	05:57:49	UPS: Returned from AVR Trim.
05/29/2016	05:57:44	UPS: Returned from battery backup power.
05/29/2016	05:57:44	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:57:40	UPS: Switched to battery backup power.
05/29/2016	05:57:37	UPS: Returned from AVR Trim.
05/29/2016	05:57:32	UPS: Returned from battery backup power.
05/29/2016	05:57:32	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:57:28	UPS: Switched to battery backup power.
05/29/2016	05:57:24	UPS: Returned from AVR Trim.
05/29/2016	05:57:19	UPS: Returned from battery backup power.
05/29/2016	05:57:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:57:15	UPS: Switched to battery backup power.
05/29/2016	05:57:11	UPS: Returned from AVR Trim.
05/29/2016	05:57:06	UPS: Returned from battery backup power.
05/29/2016	05:57:06	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:57:02	UPS: Switched to battery backup power.
05/29/2016	05:56:59	UPS: Returned from AVR Trim.
05/29/2016	05:56:54	UPS: Returned from battery backup power.
05/29/2016	05:56:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:56:50	UPS: Switched to battery backup power.
05/29/2016	05:56:47	UPS: Returned from AVR Trim.
05/29/2016	05:56:42	UPS: Returned from battery backup power.
05/29/2016	05:56:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:56:38	UPS: Switched to battery backup power.
05/29/2016	05:56:34	UPS: Returned from AVR Trim.
05/29/2016	05:56:30	UPS: Returned from battery backup power.
05/29/2016	05:56:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:56:26	UPS: Switched to battery backup power.
05/29/2016	05:56:22	UPS: Returned from AVR Trim.
05/29/2016	05:56:17	UPS: Returned from battery backup power.
05/29/2016	05:56:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:56:13	UPS: Switched to battery backup power.
05/29/2016	05:56:10	UPS: Returned from AVR Trim.
05/29/2016	05:56:05	UPS: Returned from battery backup power.
05/29/2016	05:56:05	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:56:01	UPS: Switched to battery backup power.
05/29/2016	05:55:57	UPS: Returned from AVR Trim.
05/29/2016	05:55:52	UPS: Returned from battery backup power.
05/29/2016	05:55:52	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:55:48	UPS: Switched to battery backup power.
05/29/2016	05:55:44	UPS: Returned from AVR Trim.
05/29/2016	05:55:40	UPS: Returned from battery backup power.
05/29/2016	05:55:39	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:55:36	UPS: Switched to battery backup power.
05/29/2016	05:55:32	UPS: Returned from AVR Trim.
05/29/2016	05:55:27	UPS: Returned from battery backup power.
05/29/2016	05:55:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:55:23	UPS: Switched to battery backup power.
05/29/2016	05:55:19	UPS: Returned from AVR Trim.
05/29/2016	05:55:14	UPS: Returned from battery backup power.
05/29/2016	05:55:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:55:10	UPS: Switched to battery backup power.
05/29/2016	05:55:06	UPS: Returned from AVR Trim.
05/29/2016	05:55:01	UPS: Returned from battery backup power.
05/29/2016	05:55:01	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:54:57	UPS: Switched to battery backup power.
05/29/2016	05:54:54	UPS: Returned from AVR Trim.
05/29/2016	05:54:49	UPS: Returned from battery backup power.
05/29/2016	05:54:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:54:44	UPS: Switched to battery backup power.
05/29/2016	05:54:41	UPS: Returned from AVR Trim.
05/29/2016	05:54:36	UPS: Returned from battery backup power.
05/29/2016	05:54:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:54:31	UPS: Switched to battery backup power.
05/29/2016	05:54:28	UPS: Returned from AVR Trim.
05/29/2016	05:54:23	UPS: Returned from battery backup power.
05/29/2016	05:54:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:54:18	UPS: Switched to battery backup power.
05/29/2016	05:54:15	UPS: Returned from AVR Trim.
05/29/2016	05:54:10	UPS: Returned from battery backup power.
05/29/2016	05:54:10	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:54:05	UPS: Switched to battery backup power.
05/29/2016	05:54:01	UPS: Returned from AVR Trim.
05/29/2016	05:53:56	UPS: Returned from battery backup power.
05/29/2016	05:53:56	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:53:52	UPS: Switched to battery backup power.
05/29/2016	05:53:48	UPS: Returned from AVR Trim.
05/29/2016	05:53:43	UPS: Returned from battery backup power.
05/29/2016	05:53:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:53:39	UPS: Switched to battery backup power.
05/29/2016	05:53:35	UPS: Returned from AVR Trim.
05/29/2016	05:53:30	UPS: Returned from battery backup power.
05/29/2016	05:53:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:53:26	UPS: Switched to battery backup power.
05/29/2016	05:53:22	UPS: Returned from AVR Trim.
05/29/2016	05:53:17	UPS: Returned from battery backup power.
05/29/2016	05:53:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:53:13	UPS: Switched to battery backup power.
05/29/2016	05:53:09	UPS: Returned from AVR Trim.
05/29/2016	05:53:04	UPS: Returned from battery backup power.
05/29/2016	05:53:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:53:00	UPS: Switched to battery backup power.
05/29/2016	05:52:56	UPS: Returned from AVR Trim.
05/29/2016	05:52:51	UPS: Returned from battery backup power.
05/29/2016	05:52:51	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:52:47	UPS: Switched to battery backup power.
05/29/2016	05:52:43	UPS: Returned from AVR Trim.
05/29/2016	05:52:38	UPS: Returned from battery backup power.
05/29/2016	05:52:38	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:52:34	UPS: Switched to battery backup power.
05/29/2016	05:52:30	UPS: Returned from AVR Trim.
05/29/2016	05:52:25	UPS: Returned from battery backup power.
05/29/2016	05:52:25	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:52:21	UPS: Switched to battery backup power.
05/29/2016	05:52:17	UPS: Returned from AVR Trim.
05/29/2016	05:52:12	UPS: Returned from battery backup power.
05/29/2016	05:52:12	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:52:08	UPS: Switched to battery backup power.
05/29/2016	05:52:04	UPS: Returned from AVR Trim.
05/29/2016	05:51:59	UPS: Returned from battery backup power.
05/29/2016	05:51:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:51:55	UPS: Switched to battery backup power.
05/29/2016	05:51:51	UPS: Returned from AVR Trim.
05/29/2016	05:51:46	UPS: Returned from battery backup power.
05/29/2016	05:51:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:51:42	UPS: Switched to battery backup power.
05/29/2016	05:51:38	UPS: Returned from AVR Trim.
05/29/2016	05:51:33	UPS: Returned from battery backup power.
05/29/2016	05:51:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:51:29	UPS: Switched to battery backup power.
05/29/2016	05:51:25	UPS: Returned from AVR Trim.
05/29/2016	05:51:22	UPS: Returned from battery backup power.
05/29/2016	05:51:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:51:16	UPS: Switched to battery backup power.
05/29/2016	05:51:12	UPS: Returned from AVR Trim.
05/29/2016	05:51:07	UPS: Returned from battery backup power.
05/29/2016	05:51:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:51:03	UPS: Switched to battery backup power.
05/29/2016	05:50:59	UPS: Returned from AVR Trim.
05/29/2016	05:50:54	UPS: Returned from battery backup power.
05/29/2016	05:50:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:50:49	UPS: Switched to battery backup power.
05/29/2016	05:50:45	UPS: Returned from AVR Trim.
05/29/2016	05:50:41	UPS: Returned from battery backup power.
05/29/2016	05:50:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:50:36	UPS: Switched to battery backup power.
05/29/2016	05:50:32	UPS: Returned from AVR Trim.
05/29/2016	05:50:27	UPS: Returned from battery backup power.
05/29/2016	05:50:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:50:23	UPS: Switched to battery backup power.
05/29/2016	05:50:19	UPS: Returned from AVR Trim.
05/29/2016	05:50:14	UPS: Returned from battery backup power.
05/29/2016	05:50:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:50:10	UPS: Switched to battery backup power.
05/29/2016	05:50:06	UPS: Returned from AVR Trim.
05/29/2016	05:50:01	UPS: Returned from battery backup power.
05/29/2016	05:50:01	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:49:57	UPS: Switched to battery backup power.
05/29/2016	05:49:53	UPS: Returned from AVR Trim.
05/29/2016	05:49:48	UPS: Returned from battery backup power.
05/29/2016	05:49:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:49:44	UPS: Switched to battery backup power.
05/29/2016	05:49:40	UPS: Returned from AVR Trim.
05/29/2016	05:49:35	UPS: Returned from battery backup power.
05/29/2016	05:49:35	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:49:31	UPS: Switched to battery backup power.
05/29/2016	05:49:27	UPS: Returned from AVR Trim.
05/29/2016	05:49:22	UPS: Returned from battery backup power.
05/29/2016	05:49:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:49:18	UPS: Switched to battery backup power.
05/29/2016	05:49:14	UPS: Returned from AVR Trim.
05/29/2016	05:49:09	UPS: Returned from battery backup power.
05/29/2016	05:49:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:49:05	UPS: Switched to battery backup power.
05/29/2016	05:49:01	UPS: Returned from AVR Trim.
05/29/2016	05:48:56	UPS: Returned from battery backup power.
05/29/2016	05:48:56	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:48:52	UPS: Switched to battery backup power.
05/29/2016	05:48:48	UPS: Returned from AVR Trim.
05/29/2016	05:48:43	UPS: Returned from battery backup power.
05/29/2016	05:48:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:48:39	UPS: Switched to battery backup power.
05/29/2016	05:48:35	UPS: Returned from AVR Trim.
05/29/2016	05:48:30	UPS: Returned from battery backup power.
05/29/2016	05:48:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:48:25	UPS: Switched to battery backup power.
05/29/2016	05:48:21	UPS: Returned from AVR Trim.
05/29/2016	05:48:17	UPS: Returned from battery backup power.
05/29/2016	05:48:16	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:48:12	UPS: Switched to battery backup power.
05/29/2016	05:48:08	UPS: Returned from AVR Trim.
05/29/2016	05:48:04	UPS: Returned from battery backup power.
05/29/2016	05:48:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:47:59	UPS: Switched to battery backup power.
05/29/2016	05:47:55	UPS: Returned from AVR Trim.
05/29/2016	05:47:50	UPS: Returned from battery backup power.
05/29/2016	05:47:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:47:46	UPS: Switched to battery backup power.
05/29/2016	05:47:42	UPS: Returned from AVR Trim.
05/29/2016	05:47:37	UPS: Returned from battery backup power.
05/29/2016	05:47:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:47:33	UPS: Switched to battery backup power.
05/29/2016	05:47:29	UPS: Returned from AVR Trim.
05/29/2016	05:47:25	UPS: Returned from battery backup power.
05/29/2016	05:47:25	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:47:20	UPS: Switched to battery backup power.
05/29/2016	05:47:16	UPS: Returned from AVR Trim.
05/29/2016	05:47:11	UPS: Returned from battery backup power.
05/29/2016	05:47:11	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:47:07	UPS: Switched to battery backup power.
05/29/2016	05:47:03	UPS: Returned from AVR Trim.
05/29/2016	05:46:58	UPS: Returned from battery backup power.
05/29/2016	05:46:58	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:46:54	UPS: Switched to battery backup power.
05/29/2016	05:46:50	UPS: Returned from AVR Trim.
05/29/2016	05:46:45	UPS: Returned from battery backup power.
05/29/2016	05:46:45	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:46:41	UPS: Switched to battery backup power.
05/29/2016	05:46:37	UPS: Returned from AVR Trim.
05/29/2016	05:46:32	UPS: Returned from battery backup power.
05/29/2016	05:46:32	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:46:28	UPS: Switched to battery backup power.
05/29/2016	05:46:25	UPS: Returned from AVR Trim.
05/29/2016	05:46:20	UPS: Returned from battery backup power.
05/29/2016	05:46:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:46:16	UPS: Switched to battery backup power.
05/29/2016	05:46:13	UPS: Returned from AVR Trim.
05/29/2016	05:46:07	UPS: Returned from battery backup power.
05/29/2016	05:46:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:46:02	UPS: Switched to battery backup power.
05/29/2016	05:45:59	UPS: Returned from AVR Trim.
05/29/2016	05:45:54	UPS: Returned from battery backup power.
05/29/2016	05:45:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:45:50	UPS: Switched to battery backup power.
05/29/2016	05:45:46	UPS: Returned from AVR Trim.
05/29/2016	05:45:41	UPS: Returned from battery backup power.
05/29/2016	05:45:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:45:36	UPS: Switched to battery backup power.
05/29/2016	05:45:32	UPS: Returned from AVR Trim.
05/29/2016	05:45:27	UPS: Returned from battery backup power.
05/29/2016	05:45:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:45:24	UPS: Switched to battery backup power.
05/29/2016	05:45:20	UPS: Returned from AVR Trim.
05/29/2016	05:45:14	UPS: Returned from battery backup power.
05/29/2016	05:45:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:45:10	UPS: Switched to battery backup power.
05/29/2016	05:45:06	UPS: Returned from AVR Trim.
05/29/2016	05:45:01	UPS: Returned from battery backup power.
05/29/2016	05:45:01	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:44:56	UPS: Switched to battery backup power.
05/29/2016	05:44:53	UPS: Returned from AVR Trim.
05/29/2016	05:44:48	UPS: Returned from battery backup power.
05/29/2016	05:44:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:44:43	UPS: Switched to battery backup power.
05/29/2016	05:44:39	UPS: Returned from AVR Trim.
05/29/2016	05:44:34	UPS: Returned from battery backup power.
05/29/2016	05:44:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:44:30	UPS: Switched to battery backup power.
05/29/2016	05:44:26	UPS: Returned from AVR Trim.
05/29/2016	05:44:21	UPS: Returned from battery backup power.
05/29/2016	05:44:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:44:17	UPS: Switched to battery backup power.
05/29/2016	05:44:13	UPS: Returned from AVR Trim.
05/29/2016	05:44:08	UPS: Returned from battery backup power.
05/29/2016	05:44:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:44:03	UPS: Switched to battery backup power.
05/29/2016	05:44:00	UPS: Returned from AVR Trim.
05/29/2016	05:43:55	UPS: Returned from battery backup power.
05/29/2016	05:43:55	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:43:51	UPS: Switched to battery backup power.
05/29/2016	05:43:47	UPS: Returned from AVR Trim.
05/29/2016	05:43:42	UPS: Returned from battery backup power.
05/29/2016	05:43:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:43:37	UPS: Switched to battery backup power.
05/29/2016	05:43:34	UPS: Returned from AVR Trim.
05/29/2016	05:43:29	UPS: Returned from battery backup power.
05/29/2016	05:43:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:43:24	UPS: Switched to battery backup power.
05/29/2016	05:43:20	UPS: Returned from AVR Trim.
05/29/2016	05:43:16	UPS: Returned from battery backup power.
05/29/2016	05:43:16	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:43:11	UPS: Switched to battery backup power.
05/29/2016	05:43:07	UPS: Returned from AVR Trim.
05/29/2016	05:43:02	UPS: Returned from battery backup power.
05/29/2016	05:43:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:42:58	UPS: Switched to battery backup power.
05/29/2016	05:42:54	UPS: Returned from AVR Trim.
05/29/2016	05:42:49	UPS: Returned from battery backup power.
05/29/2016	05:42:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:42:44	UPS: Switched to battery backup power.
05/29/2016	05:42:41	UPS: Returned from AVR Trim.
05/29/2016	05:42:36	UPS: Returned from battery backup power.
05/29/2016	05:42:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:42:31	UPS: Switched to battery backup power.
05/29/2016	05:42:27	UPS: Returned from AVR Trim.
05/29/2016	05:42:23	UPS: Returned from battery backup power.
05/29/2016	05:42:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:42:18	UPS: Switched to battery backup power.
05/29/2016	05:42:14	UPS: Returned from AVR Trim.
05/29/2016	05:42:09	UPS: Returned from battery backup power.
05/29/2016	05:42:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:42:05	UPS: Switched to battery backup power.
05/29/2016	05:42:01	UPS: Returned from AVR Trim.
05/29/2016	05:41:56	UPS: Returned from battery backup power.
05/29/2016	05:41:56	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:41:52	UPS: Switched to battery backup power.
05/29/2016	05:41:48	UPS: Returned from AVR Trim.
05/29/2016	05:41:43	UPS: Returned from battery backup power.
05/29/2016	05:41:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:41:39	UPS: Switched to battery backup power.
05/29/2016	05:41:35	UPS: Returned from AVR Trim.
05/29/2016	05:41:30	UPS: Returned from battery backup power.
05/29/2016	05:41:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:41:25	UPS: Switched to battery backup power.
05/29/2016	05:41:21	UPS: Returned from AVR Trim.
05/29/2016	05:41:17	UPS: Returned from battery backup power.
05/29/2016	05:41:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:41:12	UPS: Switched to battery backup power.
05/29/2016	05:41:08	UPS: Returned from AVR Trim.
05/29/2016	05:41:03	UPS: Returned from battery backup power.
05/29/2016	05:41:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:40:59	UPS: Switched to battery backup power.
05/29/2016	05:40:55	UPS: Returned from AVR Trim.
05/29/2016	05:40:50	UPS: Returned from battery backup power.
05/29/2016	05:40:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:40:46	UPS: Switched to battery backup power.
05/29/2016	05:40:42	UPS: Returned from AVR Trim.
05/29/2016	05:40:37	UPS: Returned from battery backup power.
05/29/2016	05:40:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:40:33	UPS: Switched to battery backup power.
05/29/2016	05:40:29	UPS: Returned from AVR Trim.
05/29/2016	05:40:24	UPS: Returned from battery backup power.
05/29/2016	05:40:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:40:20	UPS: Switched to battery backup power.
05/29/2016	05:40:16	UPS: Returned from AVR Trim.
05/29/2016	05:40:11	UPS: Returned from battery backup power.
05/29/2016	05:40:11	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:40:07	UPS: Switched to battery backup power.
05/29/2016	05:40:03	UPS: Returned from AVR Trim.
05/29/2016	05:39:58	UPS: Returned from battery backup power.
05/29/2016	05:39:58	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:39:54	UPS: Switched to battery backup power.
05/29/2016	05:39:50	UPS: Returned from AVR Trim.
05/29/2016	05:39:45	UPS: Returned from battery backup power.
05/29/2016	05:39:45	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:39:41	UPS: Switched to battery backup power.
05/29/2016	05:39:37	UPS: Returned from AVR Trim.
05/29/2016	05:39:33	UPS: Returned from battery backup power.
05/29/2016	05:39:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:39:28	UPS: Switched to battery backup power.
05/29/2016	05:39:24	UPS: Returned from AVR Trim.
05/29/2016	05:39:20	UPS: Returned from battery backup power.
05/29/2016	05:39:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:39:15	UPS: Switched to battery backup power.
05/29/2016	05:39:11	UPS: Returned from AVR Trim.
05/29/2016	05:39:06	UPS: Returned from battery backup power.
05/29/2016	05:39:06	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:39:02	UPS: Switched to battery backup power.
05/29/2016	05:38:58	UPS: Returned from AVR Trim.
05/29/2016	05:38:53	UPS: Returned from battery backup power.
05/29/2016	05:38:53	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:38:49	UPS: Switched to battery backup power.
05/29/2016	05:38:45	UPS: Returned from AVR Trim.
05/29/2016	05:38:40	UPS: Returned from battery backup power.
05/29/2016	05:38:40	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:38:36	UPS: Switched to battery backup power.
05/29/2016	05:38:32	UPS: Returned from AVR Trim.
05/29/2016	05:38:27	UPS: Returned from battery backup power.
05/29/2016	05:38:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:38:24	UPS: Switched to battery backup power.
05/29/2016	05:38:20	UPS: Returned from AVR Trim.
05/29/2016	05:38:15	UPS: Returned from battery backup power.
05/29/2016	05:38:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:38:11	UPS: Switched to battery backup power.
05/29/2016	05:38:07	UPS: Returned from AVR Trim.
05/29/2016	05:38:02	UPS: Returned from battery backup power.
05/29/2016	05:38:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:37:58	UPS: Switched to battery backup power.
05/29/2016	05:37:54	UPS: Returned from AVR Trim.
05/29/2016	05:37:49	UPS: Returned from battery backup power.
05/29/2016	05:37:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:37:45	UPS: Switched to battery backup power.
05/29/2016	05:37:42	UPS: Returned from AVR Trim.
05/29/2016	05:37:37	UPS: Returned from battery backup power.
05/29/2016	05:37:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:37:33	UPS: Switched to battery backup power.
05/29/2016	05:37:30	UPS: Returned from AVR Trim.
05/29/2016	05:37:25	UPS: Returned from battery backup power.
05/29/2016	05:37:25	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:37:20	UPS: Switched to battery backup power.
05/29/2016	05:37:17	UPS: Returned from AVR Trim.
05/29/2016	05:37:12	UPS: Returned from battery backup power.
05/29/2016	05:37:12	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:37:08	UPS: Switched to battery backup power.
05/29/2016	05:37:04	UPS: Returned from AVR Trim.
05/29/2016	05:36:59	UPS: Returned from battery backup power.
05/29/2016	05:36:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:36:54	UPS: Switched to battery backup power.
05/29/2016	05:36:51	UPS: Returned from AVR Trim.
05/29/2016	05:36:46	UPS: Returned from battery backup power.
05/29/2016	05:36:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:36:41	UPS: Switched to battery backup power.
05/29/2016	05:36:38	UPS: Returned from AVR Trim.
05/29/2016	05:36:33	UPS: Returned from battery backup power.
05/29/2016	05:36:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:36:28	UPS: Switched to battery backup power.
05/29/2016	05:36:25	UPS: Returned from AVR Trim.
05/29/2016	05:36:20	UPS: Returned from battery backup power.
05/29/2016	05:36:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:36:15	UPS: Switched to battery backup power.
05/29/2016	05:36:12	UPS: Returned from AVR Trim.
05/29/2016	05:36:07	UPS: Returned from battery backup power.
05/29/2016	05:36:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:36:02	UPS: Switched to battery backup power.
05/29/2016	05:35:58	UPS: Returned from AVR Trim.
05/29/2016	05:35:54	UPS: Returned from battery backup power.
05/29/2016	05:35:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:35:49	UPS: Switched to battery backup power.
05/29/2016	05:35:46	UPS: Returned from AVR Trim.
05/29/2016	05:35:41	UPS: Returned from battery backup power.
05/29/2016	05:35:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:35:36	UPS: Switched to battery backup power.
05/29/2016	05:35:33	UPS: Returned from AVR Trim.
05/29/2016	05:35:28	UPS: Returned from battery backup power.
05/29/2016	05:35:28	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:35:24	UPS: Switched to battery backup power.
05/29/2016	05:35:20	UPS: Returned from AVR Trim.
05/29/2016	05:35:15	UPS: Returned from battery backup power.
05/29/2016	05:35:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:35:12	UPS: Switched to battery backup power.
05/29/2016	05:35:08	UPS: Returned from AVR Trim.
05/29/2016	05:35:03	UPS: Returned from battery backup power.
05/29/2016	05:35:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:34:58	UPS: Switched to battery backup power.
05/29/2016	05:34:55	UPS: Returned from AVR Trim.
05/29/2016	05:34:50	UPS: Returned from battery backup power.
05/29/2016	05:34:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:34:46	UPS: Switched to battery backup power.
05/29/2016	05:34:42	UPS: Returned from AVR Trim.
05/29/2016	05:34:38	UPS: Returned from battery backup power.
05/29/2016	05:34:38	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:34:33	UPS: Switched to battery backup power.
05/29/2016	05:34:29	UPS: Returned from AVR Trim.
05/29/2016	05:34:24	UPS: Returned from battery backup power.
05/29/2016	05:34:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:34:20	UPS: Switched to battery backup power.
05/29/2016	05:34:16	UPS: Returned from AVR Trim.
05/29/2016	05:34:11	UPS: Returned from battery backup power.
05/29/2016	05:34:11	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:34:07	UPS: Switched to battery backup power.
05/29/2016	05:34:03	UPS: Returned from AVR Trim.
05/29/2016	05:33:58	UPS: Returned from battery backup power.
05/29/2016	05:33:58	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:33:54	UPS: Switched to battery backup power.
05/29/2016	05:33:50	UPS: Returned from AVR Trim.
05/29/2016	05:33:46	UPS: Returned from battery backup power.
05/29/2016	05:33:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:33:42	UPS: Switched to battery backup power.
05/29/2016	05:33:38	UPS: Returned from AVR Trim.
05/29/2016	05:33:33	UPS: Returned from battery backup power.
05/29/2016	05:33:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:33:30	UPS: Switched to battery backup power.
05/29/2016	05:33:26	UPS: Returned from AVR Trim.
05/29/2016	05:33:21	UPS: Returned from battery backup power.
05/29/2016	05:33:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:33:17	UPS: Switched to battery backup power.
05/29/2016	05:33:13	UPS: Returned from AVR Trim.
05/29/2016	05:33:08	UPS: Returned from battery backup power.
05/29/2016	05:33:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:33:05	UPS: Switched to battery backup power.
05/29/2016	05:33:01	UPS: Returned from AVR Trim.
05/29/2016	05:32:56	UPS: Returned from battery backup power.
05/29/2016	05:32:56	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:32:52	UPS: Switched to battery backup power.
05/29/2016	05:32:49	UPS: Returned from AVR Trim.
05/29/2016	05:32:44	UPS: Returned from battery backup power.
05/29/2016	05:32:44	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:32:40	UPS: Switched to battery backup power.
05/29/2016	05:32:36	UPS: Returned from AVR Trim.
05/29/2016	05:32:31	UPS: Returned from battery backup power.
05/29/2016	05:32:31	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:32:28	UPS: Switched to battery backup power.
05/29/2016	05:32:25	UPS: Returned from AVR Trim.
05/29/2016	05:32:20	UPS: Returned from battery backup power.
05/29/2016	05:32:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:32:16	UPS: Switched to battery backup power.
05/29/2016	05:32:13	UPS: Returned from AVR Trim.
05/29/2016	05:32:08	UPS: Returned from battery backup power.
05/29/2016	05:32:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:32:05	UPS: Switched to battery backup power.
05/29/2016	05:32:01	UPS: Returned from AVR Trim.
05/29/2016	05:31:56	UPS: Returned from battery backup power.
05/29/2016	05:31:55	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:31:52	UPS: Switched to battery backup power.
05/29/2016	05:31:48	UPS: Returned from AVR Trim.
05/29/2016	05:31:43	UPS: Returned from battery backup power.
05/29/2016	05:31:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:31:39	UPS: Switched to battery backup power.
05/29/2016	05:31:36	UPS: Returned from AVR Trim.
05/29/2016	05:31:31	UPS: Returned from battery backup power.
05/29/2016	05:31:31	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:31:27	UPS: Switched to battery backup power.
05/29/2016	05:31:23	UPS: Returned from AVR Trim.
05/29/2016	05:31:20	UPS: Returned from battery backup power.
05/29/2016	05:31:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:31:15	UPS: Switched to battery backup power.
05/29/2016	05:31:11	UPS: Returned from AVR Trim.
05/29/2016	05:31:06	UPS: Returned from battery backup power.
05/29/2016	05:31:06	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:31:03	UPS: Switched to battery backup power.
05/29/2016	05:30:59	UPS: Returned from AVR Trim.
05/29/2016	05:30:54	UPS: Returned from battery backup power.
05/29/2016	05:30:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:30:50	UPS: Switched to battery backup power.
05/29/2016	05:30:47	UPS: Returned from AVR Trim.
05/29/2016	05:30:42	UPS: Returned from battery backup power.
05/29/2016	05:30:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:30:38	UPS: Switched to battery backup power.
05/29/2016	05:30:34	UPS: Returned from AVR Trim.
05/29/2016	05:30:29	UPS: Returned from battery backup power.
05/29/2016	05:30:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:30:27	UPS: Switched to battery backup power.
05/29/2016	05:30:23	UPS: Returned from AVR Trim.
05/29/2016	05:30:18	UPS: Returned from battery backup power.
05/29/2016	05:30:18	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:30:14	UPS: Switched to battery backup power.
05/29/2016	05:30:10	UPS: Returned from AVR Trim.
05/29/2016	05:30:05	UPS: Returned from battery backup power.
05/29/2016	05:30:05	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:30:01	UPS: Switched to battery backup power.
05/29/2016	05:29:57	UPS: Returned from AVR Trim.
05/29/2016	05:29:52	UPS: Returned from battery backup power.
05/29/2016	05:29:52	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:29:48	UPS: Switched to battery backup power.
05/29/2016	05:29:44	UPS: Returned from AVR Trim.
05/29/2016	05:29:39	UPS: Returned from battery backup power.
05/29/2016	05:29:39	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:29:35	UPS: Switched to battery backup power.
05/29/2016	05:29:31	UPS: Returned from AVR Trim.
05/29/2016	05:29:26	UPS: Returned from battery backup power.
05/29/2016	05:29:26	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:29:21	UPS: Switched to battery backup power.
05/29/2016	05:29:17	UPS: Returned from AVR Trim.
05/29/2016	05:29:13	UPS: Returned from battery backup power.
05/29/2016	05:29:13	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:29:09	UPS: Switched to battery backup power.
05/29/2016	05:29:05	UPS: Returned from AVR Trim.
05/29/2016	05:29:00	UPS: Returned from battery backup power.
05/29/2016	05:29:00	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:28:55	UPS: Switched to battery backup power.
05/29/2016	05:28:51	UPS: Returned from AVR Trim.
05/29/2016	05:28:46	UPS: Returned from battery backup power.
05/29/2016	05:28:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:28:42	UPS: Switched to battery backup power.
05/29/2016	05:28:38	UPS: Returned from AVR Trim.
05/29/2016	05:28:33	UPS: Returned from battery backup power.
05/29/2016	05:28:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:28:29	UPS: Switched to battery backup power.
05/29/2016	05:28:25	UPS: Returned from AVR Trim.
05/29/2016	05:28:20	UPS: Returned from battery backup power.
05/29/2016	05:28:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:28:16	UPS: Switched to battery backup power.
05/29/2016	05:28:12	UPS: Returned from AVR Trim.
05/29/2016	05:28:07	UPS: Returned from battery backup power.
05/29/2016	05:28:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:28:03	UPS: Switched to battery backup power.
05/29/2016	05:27:59	UPS: Returned from AVR Trim.
05/29/2016	05:27:54	UPS: Returned from battery backup power.
05/29/2016	05:27:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:27:50	UPS: Switched to battery backup power.
05/29/2016	05:27:46	UPS: Returned from AVR Trim.
05/29/2016	05:27:41	UPS: Returned from battery backup power.
05/29/2016	05:27:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:27:37	UPS: Switched to battery backup power.
05/29/2016	05:27:34	UPS: Returned from AVR Trim.
05/29/2016	05:27:29	UPS: Returned from battery backup power.
05/29/2016	05:27:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:27:25	UPS: Switched to battery backup power.
05/29/2016	05:27:21	UPS: Returned from AVR Trim.
05/29/2016	05:27:17	UPS: Returned from battery backup power.
05/29/2016	05:27:16	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:27:13	UPS: Switched to battery backup power.
05/29/2016	05:27:09	UPS: Returned from AVR Trim.
05/29/2016	05:27:04	UPS: Returned from battery backup power.
05/29/2016	05:27:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:27:00	UPS: Switched to battery backup power.
05/29/2016	05:26:56	UPS: Returned from AVR Trim.
05/29/2016	05:26:51	UPS: Returned from battery backup power.
05/29/2016	05:26:51	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:26:47	UPS: Switched to battery backup power.
05/29/2016	05:26:43	UPS: Returned from AVR Trim.
05/29/2016	05:26:38	UPS: Returned from battery backup power.
05/29/2016	05:26:38	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:26:34	UPS: Switched to battery backup power.
05/29/2016	05:26:30	UPS: Returned from AVR Trim.
05/29/2016	05:26:25	UPS: Returned from battery backup power.
05/29/2016	05:26:25	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:26:21	UPS: Switched to battery backup power.
05/29/2016	05:26:17	UPS: Returned from AVR Trim.
05/29/2016	05:26:12	UPS: Returned from battery backup power.
05/29/2016	05:26:12	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:26:08	UPS: Switched to battery backup power.
05/29/2016	05:26:04	UPS: Returned from AVR Trim.
05/29/2016	05:25:59	UPS: Returned from battery backup power.
05/29/2016	05:25:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:25:55	UPS: Switched to battery backup power.
05/29/2016	05:25:51	UPS: Returned from AVR Trim.
05/29/2016	05:25:46	UPS: Returned from battery backup power.
05/29/2016	05:25:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:25:42	UPS: Switched to battery backup power.
05/29/2016	05:25:38	UPS: Returned from AVR Trim.
05/29/2016	05:25:33	UPS: Returned from battery backup power.
05/29/2016	05:25:33	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:25:29	UPS: Switched to battery backup power.
05/29/2016	05:25:25	UPS: Returned from AVR Trim.
05/29/2016	05:25:20	UPS: Returned from battery backup power.
05/29/2016	05:25:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:25:16	UPS: Switched to battery backup power.
05/29/2016	05:25:12	UPS: Returned from AVR Trim.
05/29/2016	05:25:07	UPS: Returned from battery backup power.
05/29/2016	05:25:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:25:03	UPS: Switched to battery backup power.
05/29/2016	05:24:59	UPS: Returned from AVR Trim.
05/29/2016	05:24:54	UPS: Returned from battery backup power.
05/29/2016	05:24:54	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:24:50	UPS: Switched to battery backup power.
05/29/2016	05:24:46	UPS: Returned from AVR Trim.
05/29/2016	05:24:41	UPS: Returned from battery backup power.
05/29/2016	05:24:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:24:37	UPS: Switched to battery backup power.
05/29/2016	05:24:33	UPS: Returned from AVR Trim.
05/29/2016	05:24:28	UPS: Returned from battery backup power.
05/29/2016	05:24:28	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:24:24	UPS: Switched to battery backup power.
05/29/2016	05:24:20	UPS: Returned from AVR Trim.
05/29/2016	05:24:15	UPS: Returned from battery backup power.
05/29/2016	05:24:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:24:11	UPS: Switched to battery backup power.
05/29/2016	05:24:07	UPS: Returned from AVR Trim.
05/29/2016	05:24:02	UPS: Returned from battery backup power.
05/29/2016	05:24:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:23:58	UPS: Switched to battery backup power.
05/29/2016	05:23:54	UPS: Returned from AVR Trim.
05/29/2016	05:23:49	UPS: Returned from battery backup power.
05/29/2016	05:23:49	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:23:45	UPS: Switched to battery backup power.
05/29/2016	05:23:41	UPS: Returned from AVR Trim.
05/29/2016	05:23:36	UPS: Returned from battery backup power.
05/29/2016	05:23:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:23:32	UPS: Switched to battery backup power.
05/29/2016	05:23:28	UPS: Returned from AVR Trim.
05/29/2016	05:23:23	UPS: Returned from battery backup power.
05/29/2016	05:23:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:23:18	UPS: Switched to battery backup power.
05/29/2016	05:23:15	UPS: Returned from AVR Trim.
05/29/2016	05:23:10	UPS: Returned from battery backup power.
05/29/2016	05:23:10	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:23:05	UPS: Switched to battery backup power.
05/29/2016	05:23:02	UPS: Returned from AVR Trim.
05/29/2016	05:22:57	UPS: Returned from battery backup power.
05/29/2016	05:22:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:22:53	UPS: Switched to battery backup power.
05/29/2016	05:22:49	UPS: Returned from AVR Trim.
05/29/2016	05:22:44	UPS: Returned from battery backup power.
05/29/2016	05:22:44	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:22:40	UPS: Switched to battery backup power.
05/29/2016	05:22:36	UPS: Returned from AVR Trim.
05/29/2016	05:22:31	UPS: Returned from battery backup power.
05/29/2016	05:22:31	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:22:27	UPS: Switched to battery backup power.
05/29/2016	05:22:23	UPS: Returned from AVR Trim.
05/29/2016	05:22:18	UPS: Returned from battery backup power.
05/29/2016	05:22:18	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:22:14	UPS: Switched to battery backup power.
05/29/2016	05:22:10	UPS: Returned from AVR Trim.
05/29/2016	05:22:05	UPS: Returned from battery backup power.
05/29/2016	05:22:05	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:22:01	UPS: Switched to battery backup power.
05/29/2016	05:21:57	UPS: Returned from AVR Trim.
05/29/2016	05:21:52	UPS: Returned from battery backup power.
05/29/2016	05:21:52	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:21:48	UPS: Switched to battery backup power.
05/29/2016	05:21:44	UPS: Returned from AVR Trim.
05/29/2016	05:21:39	UPS: Returned from battery backup power.
05/29/2016	05:21:39	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:21:35	UPS: Switched to battery backup power.
05/29/2016	05:21:31	UPS: Returned from AVR Trim.
05/29/2016	05:21:26	UPS: Returned from battery backup power.
05/29/2016	05:21:26	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:21:22	UPS: Switched to battery backup power.
05/29/2016	05:21:18	UPS: Returned from AVR Trim.
05/29/2016	05:21:13	UPS: Returned from battery backup power.
05/29/2016	05:21:13	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:21:09	UPS: Switched to battery backup power.
05/29/2016	05:21:05	UPS: Returned from AVR Trim.
05/29/2016	05:21:00	UPS: Returned from battery backup power.
05/29/2016	05:21:00	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:20:56	UPS: Switched to battery backup power.
05/29/2016	05:20:52	UPS: Returned from AVR Trim.
05/29/2016	05:20:47	UPS: Returned from battery backup power.
05/29/2016	05:20:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:20:43	UPS: Switched to battery backup power.
05/29/2016	05:20:39	UPS: Returned from AVR Trim.
05/29/2016	05:20:34	UPS: Returned from battery backup power.
05/29/2016	05:20:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:20:31	UPS: Switched to battery backup power.
05/29/2016	05:20:27	UPS: Returned from AVR Trim.
05/29/2016	05:20:22	UPS: Returned from battery backup power.
05/29/2016	05:20:22	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:20:18	UPS: Switched to battery backup power.
05/29/2016	05:20:15	UPS: Returned from AVR Trim.
05/29/2016	05:20:10	UPS: Returned from battery backup power.
05/29/2016	05:20:10	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:20:05	UPS: Switched to battery backup power.
05/29/2016	05:20:01	UPS: Returned from AVR Trim.
05/29/2016	05:19:57	UPS: Returned from battery backup power.
05/29/2016	05:19:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:19:52	UPS: Switched to battery backup power.
05/29/2016	05:19:48	UPS: Returned from AVR Trim.
05/29/2016	05:19:44	UPS: Returned from battery backup power.
05/29/2016	05:19:44	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:19:41	UPS: Switched to battery backup power.
05/29/2016	05:19:37	UPS: Returned from AVR Trim.
05/29/2016	05:19:31	UPS: Returned from battery backup power.
05/29/2016	05:19:31	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:19:28	UPS: Switched to battery backup power.
05/29/2016	05:19:24	UPS: Returned from AVR Trim.
05/29/2016	05:19:19	UPS: Returned from battery backup power.
05/29/2016	05:19:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:19:15	UPS: Switched to battery backup power.
05/29/2016	05:19:11	UPS: Returned from AVR Trim.
05/29/2016	05:19:06	UPS: Returned from battery backup power.
05/29/2016	05:19:06	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:19:02	UPS: Switched to battery backup power.
05/29/2016	05:18:58	UPS: Returned from AVR Trim.
05/29/2016	05:18:53	UPS: Returned from battery backup power.
05/29/2016	05:18:53	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:18:49	UPS: Switched to battery backup power.
05/29/2016	05:18:45	UPS: Returned from AVR Trim.
05/29/2016	05:18:40	UPS: Returned from battery backup power.
05/29/2016	05:18:40	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:18:36	UPS: Switched to battery backup power.
05/29/2016	05:18:32	UPS: Returned from AVR Trim.
05/29/2016	05:18:27	UPS: Returned from battery backup power.
05/29/2016	05:18:27	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:18:23	UPS: Switched to battery backup power.
05/29/2016	05:18:19	UPS: Returned from AVR Trim.
05/29/2016	05:18:14	UPS: Returned from battery backup power.
05/29/2016	05:18:14	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:18:10	UPS: Switched to battery backup power.
05/29/2016	05:18:06	UPS: Returned from AVR Trim.
05/29/2016	05:18:01	UPS: Returned from battery backup power.
05/29/2016	05:18:01	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:17:57	UPS: Switched to battery backup power.
05/29/2016	05:17:53	UPS: Returned from AVR Trim.
05/29/2016	05:17:48	UPS: Returned from battery backup power.
05/29/2016	05:17:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:17:44	UPS: Switched to battery backup power.
05/29/2016	05:17:41	UPS: Returned from AVR Trim.
05/29/2016	05:17:36	UPS: Returned from battery backup power.
05/29/2016	05:17:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:17:32	UPS: Switched to battery backup power.
05/29/2016	05:17:28	UPS: Returned from AVR Trim.
05/29/2016	05:17:23	UPS: Returned from battery backup power.
05/29/2016	05:17:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:17:14	UPS: Switched to battery backup power.
05/29/2016	05:17:10	UPS: Returned from AVR Trim.
05/29/2016	05:17:05	UPS: Returned from battery backup power.
05/29/2016	05:17:05	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:16:56	UPS: Switched to battery backup power.
05/29/2016	05:16:52	UPS: Returned from AVR Trim.
05/29/2016	05:16:47	UPS: Returned from battery backup power.
05/29/2016	05:16:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:16:37	UPS: Switched to battery backup power.
05/29/2016	05:16:34	UPS: Returned from AVR Trim.
05/29/2016	05:16:29	UPS: Returned from battery backup power.
05/29/2016	05:16:29	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:16:20	UPS: Switched to battery backup power.
05/29/2016	05:16:16	UPS: Returned from AVR Trim.
05/29/2016	05:16:11	UPS: Returned from battery backup power.
05/29/2016	05:16:11	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:16:01	UPS: Switched to battery backup power.
05/29/2016	05:15:58	UPS: Returned from AVR Trim.
05/29/2016	05:15:53	UPS: Returned from battery backup power.
05/29/2016	05:15:53	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:15:44	UPS: Switched to battery backup power.
05/29/2016	05:15:40	UPS: Returned from AVR Trim.
05/29/2016	05:15:35	UPS: Returned from battery backup power.
05/29/2016	05:15:35	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:15:25	UPS: Switched to battery backup power.
05/29/2016	05:15:22	UPS: Returned from AVR Trim.
05/29/2016	05:15:17	UPS: Returned from battery backup power.
05/29/2016	05:15:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:15:07	UPS: Switched to battery backup power.
05/29/2016	05:15:04	UPS: Returned from AVR Trim.
05/29/2016	05:14:59	UPS: Returned from battery backup power.
05/29/2016	05:14:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:14:50	UPS: Switched to battery backup power.
05/29/2016	05:14:47	UPS: Returned from AVR Trim.
05/29/2016	05:14:42	UPS: Returned from battery backup power.
05/29/2016	05:14:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:14:32	UPS: Switched to battery backup power.
05/29/2016	05:14:29	UPS: Returned from AVR Trim.
05/29/2016	05:14:24	UPS: Returned from battery backup power.
05/29/2016	05:14:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:14:16	UPS: Switched to battery backup power.
05/29/2016	05:14:12	UPS: Returned from AVR Trim.
05/29/2016	05:14:07	UPS: Returned from battery backup power.
05/29/2016	05:14:07	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:13:58	UPS: Switched to battery backup power.
05/29/2016	05:13:54	UPS: Returned from AVR Trim.
05/29/2016	05:13:50	UPS: Returned from battery backup power.
05/29/2016	05:13:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:13:41	UPS: Switched to battery backup power.
05/29/2016	05:13:37	UPS: Returned from AVR Trim.
05/29/2016	05:13:32	UPS: Returned from battery backup power.
05/29/2016	05:13:32	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:13:24	UPS: Switched to battery backup power.
05/29/2016	05:13:20	UPS: Returned from AVR Trim.
05/29/2016	05:13:15	UPS: Returned from battery backup power.
05/29/2016	05:13:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:13:07	UPS: Switched to battery backup power.
05/29/2016	05:13:03	UPS: Returned from AVR Trim.
05/29/2016	05:12:58	UPS: Returned from battery backup power.
05/29/2016	05:12:58	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:12:50	UPS: Switched to battery backup power.
05/29/2016	05:12:46	UPS: Returned from AVR Trim.
05/29/2016	05:12:41	UPS: Returned from battery backup power.
05/29/2016	05:12:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:12:33	UPS: Switched to battery backup power.
05/29/2016	05:12:29	UPS: Returned from AVR Trim.
05/29/2016	05:12:24	UPS: Returned from battery backup power.
05/29/2016	05:12:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:12:16	UPS: Switched to battery backup power.
05/29/2016	05:12:12	UPS: Returned from AVR Trim.
05/29/2016	05:12:08	UPS: Returned from battery backup power.
05/29/2016	05:12:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:11:59	UPS: Switched to battery backup power.
05/29/2016	05:11:56	UPS: Returned from AVR Trim.
05/29/2016	05:11:51	UPS: Returned from battery backup power.
05/29/2016	05:11:51	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:11:43	UPS: Switched to battery backup power.
05/29/2016	05:11:39	UPS: Returned from AVR Trim.
05/29/2016	05:11:34	UPS: Returned from battery backup power.
05/29/2016	05:11:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:11:26	UPS: Switched to battery backup power.
05/29/2016	05:11:22	UPS: Returned from AVR Trim.
05/29/2016	05:11:17	UPS: Returned from battery backup power.
05/29/2016	05:11:17	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:11:08	UPS: Switched to battery backup power.
05/29/2016	05:11:04	UPS: Returned from AVR Trim.
05/29/2016	05:11:00	UPS: Returned from battery backup power.
05/29/2016	05:10:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:10:51	UPS: Switched to battery backup power.
05/29/2016	05:10:47	UPS: Returned from AVR Trim.
05/29/2016	05:10:43	UPS: Returned from battery backup power.
05/29/2016	05:10:42	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:10:35	UPS: Switched to battery backup power.
05/29/2016	05:10:31	UPS: Returned from AVR Trim.
05/29/2016	05:10:25	UPS: Returned from battery backup power.
05/29/2016	05:10:25	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:10:17	UPS: Switched to battery backup power.
05/29/2016	05:10:13	UPS: Returned from AVR Trim.
05/29/2016	05:10:08	UPS: Returned from battery backup power.
05/29/2016	05:10:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:10:00	UPS: Switched to battery backup power.
05/29/2016	05:09:56	UPS: Returned from AVR Trim.
05/29/2016	05:09:51	UPS: Returned from battery backup power.
05/29/2016	05:09:51	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:09:44	UPS: Switched to battery backup power.
05/29/2016	05:09:40	UPS: Returned from AVR Trim.
05/29/2016	05:09:35	UPS: Returned from battery backup power.
05/29/2016	05:09:35	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:09:27	UPS: Switched to battery backup power.
05/29/2016	05:09:23	UPS: Returned from AVR Trim.
05/29/2016	05:09:18	UPS: Returned from battery backup power.
05/29/2016	05:09:18	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:09:11	UPS: Switched to battery backup power.
05/29/2016	05:09:07	UPS: Returned from AVR Trim.
05/29/2016	05:09:02	UPS: Returned from battery backup power.
05/29/2016	05:09:02	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:08:54	UPS: Switched to battery backup power.
05/29/2016	05:08:50	UPS: Returned from AVR Trim.
05/29/2016	05:08:46	UPS: Returned from battery backup power.
05/29/2016	05:08:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:08:37	UPS: Switched to battery backup power.
05/29/2016	05:08:33	UPS: Returned from AVR Trim.
05/29/2016	05:08:28	UPS: Returned from battery backup power.
05/29/2016	05:08:28	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:08:21	UPS: Switched to battery backup power.
05/29/2016	05:08:17	UPS: Returned from AVR Trim.
05/29/2016	05:08:12	UPS: Returned from battery backup power.
05/29/2016	05:08:12	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:08:06	UPS: Switched to battery backup power.
05/29/2016	05:08:01	UPS: Returned from AVR Trim.
05/29/2016	05:07:57	UPS: Returned from battery backup power.
05/29/2016	05:07:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:07:49	UPS: Switched to battery backup power.
05/29/2016	05:07:45	UPS: Returned from AVR Trim.
05/29/2016	05:07:41	UPS: Returned from battery backup power.
05/29/2016	05:07:41	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:07:33	UPS: Switched to battery backup power.
05/29/2016	05:07:29	UPS: Returned from AVR Trim.
05/29/2016	05:07:24	UPS: Returned from battery backup power.
05/29/2016	05:07:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:07:16	UPS: Switched to battery backup power.
05/29/2016	05:07:12	UPS: Returned from AVR Trim.
05/29/2016	05:07:08	UPS: Returned from battery backup power.
05/29/2016	05:07:08	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:07:00	UPS: Switched to battery backup power.
05/29/2016	05:06:56	UPS: Returned from AVR Trim.
05/29/2016	05:06:51	UPS: Returned from battery backup power.
05/29/2016	05:06:51	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:06:43	UPS: Switched to battery backup power.
05/29/2016	05:06:40	UPS: Returned from AVR Trim.
05/29/2016	05:06:35	UPS: Returned from battery backup power.
05/29/2016	05:06:35	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:06:27	UPS: Switched to battery backup power.
05/29/2016	05:06:24	UPS: Returned from AVR Trim.
05/29/2016	05:06:19	UPS: Returned from battery backup power.
05/29/2016	05:06:19	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:06:11	UPS: Switched to battery backup power.
05/29/2016	05:06:08	UPS: Returned from AVR Trim.
05/29/2016	05:06:03	UPS: Returned from battery backup power.
05/29/2016	05:06:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:05:55	UPS: Switched to battery backup power.
05/29/2016	05:05:51	UPS: Returned from AVR Trim.
05/29/2016	05:05:47	UPS: Returned from battery backup power.
05/29/2016	05:05:46	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:05:39	UPS: Switched to battery backup power.
05/29/2016	05:05:35	UPS: Returned from AVR Trim.
05/29/2016	05:05:30	UPS: Returned from battery backup power.
05/29/2016	05:05:30	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:05:24	UPS: Switched to battery backup power.
05/29/2016	05:05:20	UPS: Returned from AVR Trim.
05/29/2016	05:05:15	UPS: Returned from battery backup power.
05/29/2016	05:05:15	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:05:07	UPS: Switched to battery backup power.
05/29/2016	05:05:04	UPS: Returned from AVR Trim.
05/29/2016	05:04:59	UPS: Returned from battery backup power.
05/29/2016	05:04:59	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:04:51	UPS: Switched to battery backup power.
05/29/2016	05:04:48	UPS: Returned from AVR Trim.
05/29/2016	05:04:43	UPS: Returned from battery backup power.
05/29/2016	05:04:43	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:04:35	UPS: Switched to battery backup power.
05/29/2016	05:04:31	UPS: Returned from AVR Trim.
05/29/2016	05:04:26	UPS: Returned from battery backup power.
05/29/2016	05:04:26	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:04:19	UPS: Switched to battery backup power.
05/29/2016	05:04:15	UPS: Returned from AVR Trim.
05/29/2016	05:04:10	UPS: Returned from battery backup power.
05/29/2016	05:04:10	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:04:04	UPS: Switched to battery backup power.
05/29/2016	05:04:00	UPS: Returned from AVR Trim.
05/29/2016	05:03:55	UPS: Returned from battery backup power.
05/29/2016	05:03:55	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:03:48	UPS: Switched to battery backup power.
05/29/2016	05:03:44	UPS: Returned from AVR Trim.
05/29/2016	05:03:39	UPS: Returned from battery backup power.
05/29/2016	05:03:39	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:03:33	UPS: Switched to battery backup power.
05/29/2016	05:03:29	UPS: Returned from AVR Trim.
05/29/2016	05:03:24	UPS: Returned from battery backup power.
05/29/2016	05:03:24	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:03:18	UPS: Switched to battery backup power.
05/29/2016	05:03:14	UPS: Returned from AVR Trim.
05/29/2016	05:03:09	UPS: Returned from battery backup power.
05/29/2016	05:03:09	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:03:02	UPS: Switched to battery backup power.
05/29/2016	05:02:58	UPS: Returned from AVR Trim.
05/29/2016	05:02:53	UPS: Returned from battery backup power.
05/29/2016	05:02:53	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:02:46	UPS: Switched to battery backup power.
05/29/2016	05:02:42	UPS: Returned from AVR Trim.
05/29/2016	05:02:37	UPS: Returned from battery backup power.
05/29/2016	05:02:37	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:02:30	UPS: Switched to battery backup power.
05/29/2016	05:02:26	UPS: Returned from AVR Trim.
05/29/2016	05:02:21	UPS: Returned from battery backup power.
05/29/2016	05:02:21	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:02:14	UPS: Switched to battery backup power.
05/29/2016	05:02:10	UPS: Returned from AVR Trim.
05/29/2016	05:02:06	UPS: Returned from battery backup power.
05/29/2016	05:02:06	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:01:59	UPS: Switched to battery backup power.
05/29/2016	05:01:55	UPS: Returned from AVR Trim.
05/29/2016	05:01:50	UPS: Returned from battery backup power.
05/29/2016	05:01:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:01:43	UPS: Switched to battery backup power.
05/29/2016	05:01:40	UPS: Returned from AVR Trim.
05/29/2016	05:01:35	UPS: Returned from battery backup power.
05/29/2016	05:01:35	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:01:28	UPS: Switched to battery backup power.
05/29/2016	05:01:24	UPS: Returned from AVR Trim.
05/29/2016	05:01:20	UPS: Returned from battery backup power.
05/29/2016	05:01:20	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:01:13	UPS: Switched to battery backup power.
05/29/2016	05:01:09	UPS: Returned from AVR Trim.
05/29/2016	05:01:04	UPS: Returned from battery backup power.
05/29/2016	05:01:04	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:00:57	UPS: Switched to battery backup power.
05/29/2016	05:00:53	UPS: Returned from AVR Trim.
05/29/2016	05:00:49	UPS: Returned from battery backup power.
05/29/2016	05:00:48	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:00:42	UPS: Switched to battery backup power.
05/29/2016	05:00:38	UPS: Returned from AVR Trim.
05/29/2016	05:00:34	UPS: Returned from battery backup power.
05/29/2016	05:00:34	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:00:27	UPS: Switched to battery backup power.
05/29/2016	05:00:23	UPS: Returned from AVR Trim.
05/29/2016	05:00:19	UPS: Returned from battery backup power.
05/29/2016	05:00:18	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	05:00:12	UPS: Switched to battery backup power.
05/29/2016	05:00:08	UPS: Returned from AVR Trim.
05/29/2016	05:00:03	UPS: Returned from battery backup power.
05/29/2016	05:00:03	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	04:59:59	UPS: Switched to battery backup power.
05/29/2016	04:59:55	UPS: Returned from AVR Trim.
05/29/2016	04:59:50	UPS: Returned from battery backup power.
05/29/2016	04:59:50	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	04:59:45	UPS: Switched to battery backup power.
05/29/2016	04:59:41	UPS: Returned from AVR Trim.
05/29/2016	04:59:36	UPS: Returned from battery backup power.
05/29/2016	04:59:36	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	04:59:32	UPS: Switched to battery backup power.
05/29/2016	04:59:28	UPS: Returned from AVR Trim.
05/29/2016	04:59:23	UPS: Returned from battery backup power.
05/29/2016	04:59:23	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	04:59:19	UPS: Switched to battery backup power.
05/29/2016	04:59:15	UPS: Returned from AVR Trim.
05/29/2016	04:59:10	UPS: Returned from battery backup power.
05/29/2016	04:59:10	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	04:59:06	UPS: Switched to battery backup power.
05/29/2016	04:59:02	UPS: Returned from AVR Trim.
05/29/2016	04:58:57	UPS: Returned from battery backup power.
05/29/2016	04:58:57	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	04:58:54	UPS: Switched to battery backup power.
05/29/2016	04:58:50	UPS: Returned from AVR Trim.
05/29/2016	04:58:45	UPS: Returned from battery backup power.
05/29/2016	04:58:45	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	03:35:50	System: Web user 'apc' logged out from 192.168.1.60.
05/29/2016	03:23:00	UPS: Switched to battery backup power.
05/29/2016	03:22:56	UPS: Returned from AVR Trim.
05/29/2016	03:21:43	System: Web user 'apc' logged in from 192.168.1.60.
05/29/2016	01:36:47	UPS: Returned from battery backup power.
05/29/2016	01:36:47	UPS: Enabled AVR Trim; high incoming line voltage.
05/29/2016	01:36:44	Environment: Integrated relay output fault cleared.
05/29/2016	01:36:44	UPS: Returned from a Low-Battery condition.
05/29/2016	01:36:40	Environment: Integrated relay output 1, Relay 1, has faulted due to UPS - Low Battery.
05/29/2016	01:36:40	UPS: Battery power is low and will soon be exhausted.