What's the recommended wire size for the panel mount 100A breaker? The epanel manual suggests using #6 for the 63A DIN mounts, #4 for the 80A breakers, but doesn't mention the 100A units.
Thanks!
100 amp should be #2 or #1/0 cable
Mike
It depends on where it is going. If it is in an E-Panel and going out to a Classic then #4 is what you want to use.
Ryan
Thanks, Mike & Ryan. The connection in question IS running between an epanel and a Classic, so #4 it is. Having looked at some ampacity tables, some have noted higher rattings for THHN/USE-2 and the like. Should it be THHN etc. in my case or does it matter?
Mike
Quote from: mofawayesu on May 13, 2013, 05:02:24 PM
Thanks, Mike & Ryan. The connection in question IS running between an epanel and a Classic, so #4 it is. Having looked at some ampacity tables, some have noted higher rattings for THHN/USE-2 and the like. Should it be THHN etc. in my case or does it matter?
Mike
Just be careful of stiff cable like THHN so that it doesn't break the posts off the breaker.
Routing it carefully should take care of that.
boB