I really like the 100W panels I've been using, they ship for free to my difficult access property unlike larger panels.
If I have a MNPV3 Combiner, how many 100W panels (specs listed below) can I go with if using a Classic 150 or 200W charge controller? I am really having a hard time figuring out the math. Thanks.
Optimum Operating Voltage (Vmp) 18.9V
Optimum Operating Current (Imp) 5.29A
Open - Circuit Voltage (Voc) 22.5V
Short- Circuit Current (Isc) 5.75A
Maximum Series Fuse Rating 15A
Use the MN string calculator, you can play with array size etc...
http://www.midnitesolar.com/sizingTool/displaySizing.php
Some more details about your system would be needed to do the calculations -- for example, what is your battery voltage, and the coldest recorded temperature in your location? Are you limited to only 3 PV combiner slots?
I will likely go with 24V battery bank. Coldest temperature is around 0F. I could go with a larger combiner but would rather not.
With 24 Volts battery and Classic150, you can series connect 5 of the above panels in 3 strings with lots of comfort zone left both in terms of max amp (92A for 150) and max operating voltage (150Volts). You will need to use #4 wire from combiner to classic, and from classic to battery. It is possible to have 6 in series but IMO it's not worth the stress and the unreliability it adds to the system. Code and best practices require overcurrent protection on the combiner output and the classic output -- so I would ause a Midnite mini-DC with 4 breaker slots, or a Disco 6 slot, so you can put a breaker for the output of the combiner in the same box.
laszlo, thank you very much. Ok, I think I will go with a 4x3 configuration. It will produce much more than I need so I will have lots of fudge room.