Hi, I wonder if someone can tell me if I have a Classic feeding a 24 volt battery bank for a PV array that can be up to a much higher voltage say 90 volts, when using the diversion feature what voltage will be supplied to the diversion load? Can the diversion load be supplied somehow from the Classic so that it is the same as battery voltage?
Thanks,
The Classic does not feed a voltage (or power) to a diversion load. It will, however, provide an AUX signal that can be used to control a solid state relay that switches in the load to the battery.
This AUX signal could also be used to directly switch the load into the PV output.
There are many posts in this forum concerning both methods, some searching is the way to go...
dgd