I am currently installing a dual 120VAC outback system on two midnite epanels. Does Midnite supply a wiring diagram for this config?
Title: Re: Dual outback 3648 on two midnite epanels
Post by: Vic on January 28, 2016, 04:18:54 PM
Hi EW,

I am not an expert on e-panels.

MN has great docs.  Here is the Manual on an OB e-panel with the 250 A Inverter breaker,  for example.  The 3648s might be happy with a 175 A breaker,  but look around page 15 for a nice color schematic diagram:
http://www.midnitesolar.com/pdfs/epanelManual.pdf

Just go to midnitesolar >Products >epanel >Outback ...   etc

EDIT:  There are probably a few little details that need to be figured out with Dual e-panels,  like ganged Bypass Breakers,  etc,  and a quick scan of the above manual did not seem to touch on things like this   ...

73,  GL,   Have Fun,   Vic
Title: Re: Dual outback 3648 on two midnite epanels
Post by: EW Zuber on January 28, 2016, 10:12:46 PM
Thanks but I have seen this one. Looks like I will likely have to get bigger breakers for the transfer switch so both inverters can be switched at the same time. Fortunately this is my second two inverter system so I have a decent idea of what is needed because it looks like for the most part I am on my own with this one.
Title: Re: Dual outback 3648 on two midnite epanels
Post by: zoneblue on January 29, 2016, 01:53:13 PM
No hang in there, im sure Ryan will help you out, you wont be the first to have done this im sure.
Title: Re: Dual outback 3648 on two midnite epanels
Post by: Westbranch on January 29, 2016, 03:21:28 PM
I think this is what you are after or at least a part of it


OutBack Dual Stacked

http://www.midnitesolar.com/pdfs/E-PaneWire2_OB.pdf
Title: Re: Dual outback 3648 on two midnite epanels
Post by: Halfcrazy on January 29, 2016, 04:01:44 PM
So it sounds like you want to parallel two 3600 watt 120vac inverters for 7200 watts at 120vac right?

The standard Bypass is good for 50 or 60 amps or around 6-7000 watts. So what you are looking to do is make a 100 amp bypass at 120vac right?

What I would do is use this:
http://www.midnitesolar.com/productPhoto.php?product_ID=397&productCatName=Accessories&productCat_ID=5&sortOrder=24&act=p (http://www.midnitesolar.com/productPhoto.php?product_ID=397&productCatName=Accessories&productCat_ID=5&sortOrder=24&act=p)

but instead of wiring it as 240 simply use one pole for each inverter. That way you have a 100 amp bypass assembly. The bottom two poles are the AC in. So this gives you 2 poles for AC out, 2 poles for AC in and 2 poles for bypass
Title: Re: Dual outback 3648 on two midnite epanels
Post by: Westbranch on January 29, 2016, 04:23:41 PM
Ryan, do you have some pics of the Epanel that bypass is to mount on ... 
I just looked at the file pics and I do not see how it lines up with the standard OB Epanel.. And I don't see how it would fit my OB Epanels

tks.