Post by: Tobit on July 04, 2016, 11:43:02 AM
Is there a way I can get two 275W panels and a 12V bank to play?  Voc = 39.4V. The calculator says 1.4 kids are needed for a 12V bank, so I am right on the edge.  What risks do I run if I try this configuration?
Title: Re: Two 275W Panels
Post by: BobWhite on July 04, 2016, 12:50:18 PM
Hi Tobit,

What are the panels and specs you are planing on using?
Title: Re: Two 275W Panels
Post by: Tobit on July 04, 2016, 02:25:05 PM
SolarWorld SW275's

Voc 39.4v
Vmp 31.0v
Isc 9.58a
Imp 8.94a
Title: Re: Two 275W Panels
Post by: Halfcrazy on July 04, 2016, 06:10:48 PM
Run the 2 in parallel. All that is going to happen is the Kid will current limit and leave some energy on the table
Title: Re: Two 275W Panels
Post by: Tobit on July 07, 2016, 07:01:59 AM
Quote from: Halfcrazy on July 04, 2016, 06:10:48 PM
Run the 2 in parallel. All that is going to happen is the Kid will current limit and leave some energy on the table