Hi all.

Well I took a week off work to give this project the appropriate time and energy.  Please give me your feedback.  Especially what will kill me and/or burn down the house!

Attached is my design for my small off-grid 12 Volt system for my yurt.   Hopefully self-explanatory.  Page 1 of the design is my proposed system, components are already purchased and installed, but just need to be wired together.   My existing 12 Volt system includes the batteries on page 1 and everything on page 2 (did not include existing solar panels which are hard-wired to my batteries w/o charge controller). 

Questions: 

1.  I'm using my combiner box as a DC disconnect box.  Does the PV minus bar also serve as a battery minus bar?  If not, where does the negative feed from the charge controller go? 

2.  Do I integrate my inverter with the disconnect box or just leave it as-is, directly wired to the battery?   Same question for my Genny charger.

3.  I have a lot of connections direct to my battery.  Is that proper?  Seems like a lot of connection stacked on top of each other makes for bad connections.

4.  Do I need a fuse between the inverter and the AC panel?


TIA
Title: Re: System Design Feedback
Post by: pablo on July 07, 2016, 02:14:29 PM
Page 2 of my diagram attached
Title: Re: System Design Feedback
Post by: TomW on July 07, 2016, 02:26:38 PM
Pablo;

I get a blank page for either of those. :(

Tom
Title: Re: System Design Feedback
Post by: pablo on July 07, 2016, 03:15:21 PM
Does this show for you all?

Title: Re: System Design Feedback
Post by: TomW on July 07, 2016, 03:53:26 PM
Quote from: pablo on July 07, 2016, 03:15:21 PM
Does this show for you all?

Now, that one I can see!

Tom
Title: Re: System Design Feedback
Post by: pablo on July 07, 2016, 04:05:28 PM
Great!  Ok, here's page 2 again

Title: Re: System Design Feedback
Post by: dgd on July 07, 2016, 07:40:26 PM
Pablo,

You are correct in that having multiple cables to the battery posts is not a great idea.
Take a look at the MNDC box, it would be ideal for your system and includes a 100/175/250 breaker for power to your inverter and slots for breakers from CCs, turbines etc.
It can also take a shunt so that when you upgrade the CC to a Classic you can monitor real battery current in and out and the Classic can use this to tune charging your battery.
The MNPV3 should really go near the PVs so you can have a breaker on each parallel string, or in your case on each parallel connected single PV. Then run one +ve and -ve from MNPV3 to the CC then then CC to the MNDC.
Good news is if you get an MNDC it comes with a nicely detailed wiring diagram.

dgd
Title: Re: System Design Feedback
Post by: pablo on July 07, 2016, 07:56:45 PM
I forgot to mention my severe financial constraints.  I would like to finish the project with my existing equipment noted in diagrams.  I have enough money left to buy some wire and maybe some circuit breakers.   Of course, if it won't work as shown, it won't work...