Charge Controllers and Clippers => The "Classic" charge controller => Topic started by: keithwhare on February 13, 2017, 06:49:38 PM

Title: Replacing an Outback FM60 with a Classic 150, what about ground fault protector?
Post by: keithwhare on February 13, 2017, 06:49:38 PM
In 2010, we installed an Outback FM60 on an Midnite E-Panel. The positive leg from the 1560watts of PV comes through a 63 AMP DC breaker then through a MidNite Solar 63 amp 150 VDC ground fault protector before getting to the FM60.

I am working on replacing the FM60 with a Classic 150 (so we can add a second PV array and a second Classic 150).

The Classic 150 has "Built in DC-GFP and Arc Fault".

Should I keep the existing ground fault protector in the sequence or remove it?

Keith
Title: Re: Replacing an Outback FM60 with a Classic 150, what about ground fault protector?
Post by: Halfcrazy on February 14, 2017, 05:04:30 AM
Remove it, When you add multiple GFP devices you add to the total fault current needed to activate them
Title: Re: Replacing an Outback FM60 with a Classic 150, what about ground fault protector?
Post by: keithwhare on February 14, 2017, 07:45:33 AM
Quote from: Halfcrazy on February 14, 2017, 05:04:30 AM
Remove it, When you add multiple GFP devices you add to the total fault current needed to activate them

Thanks.