Charge Controllers and Clippers => The "Classic" charge controller => Topic started by: openplanet on January 19, 2019, 11:11:46 AM

Title: 2 Follow-Me Classics, Output Current Limit
Post by: openplanet on January 19, 2019, 11:11:46 AM
Two Classics, Follow Me, WbJr.  Is there a way to limit current to the batteries based on WBJr Amps? (I'm aware that this can be done for individual Classics, but it doesn't help for multiples.) Thank you.
Title: Re: 2 Follow-Me Classics, Output Current Limit
Post by: Vic on January 19, 2019, 01:28:45 PM
Hi open..,

At the bottom of the first Post in the following Thread,  there is a White Paper:

http://midniteftp.com/forum/index.php?topic=3796.0

You do not need a WBjr & Shunt on every CC in use,  just on the Classics that could add enough additional battery charge current that would cause this current to exceed the max spec from the battery manufacturer  ... if that makes anu sense.

Vic
Title: Re: 2 Follow-Me Classics, Output Current Limit
Post by: Vic on January 23, 2019, 11:36:25 AM
Also,  this:

http://www.midniteftp.com/support/kb/faq.php?id=37

FWIW,  Vic