Hi,
Setup for wind. Using the MWandS VRD (wish my guy had sold me a clipper)
So I followed MWS directions & nada. Just resting.
Anyone know why? The manual is super vague & I’ve tried every AUX setting
What voltages do you read at the input and outputs ?
can you spin the wind turbine with a motor to see what it produces ?
Try connecting a 100W 120V incandescent bulb to 1 turbine output
Hi,
Sorry for low info... My bad
Its a 12 DC WG (wind generator) from MW&S
I can see the voltage coming from the WG & battery
I think I saw 20 some V at one point coming from WG. Battery reads good
I reset the jumper pins after powering it up & doing the other settings, but it still was in resting.
In the manual it says low light or Aux2 is set wrong. There is nothing connected to Aux2. Aux1 I followed directions & checked to make sure it was correct.
Thank you
Maybe something with the settings being for a AC unit & I have a DC unit.
What voltage does a rectifier make?
You should call the guys you got it from - I looked on their site and they sell their products with Classics so I would think they should know.
Larry
Ya I was just hoping to get lucky. Thanks!
This appears to be a common issue from my research into our call logs. I will reach out to Missouri W&S today and see if we can work on a solution as well as a quick start guide.
Can you tell me what specific turbine you have?
Ryan
Hey Guda,
Call me when you have time, I will help you set-up the Classic for the MO Wind VRD unit.
Todd
MidNite Solar Tech
360.403.7207 x33
M-F, 0800-1700 CST
Hi!
I called you guys & I got hooked up with a working curve! I forwarded that curve to MW&S.
I am producing power as of when I put that 12v curve in.
Much thanks!
Quote from: Guda on January 15, 2020, 08:07:40 PM
Hi!
I called you guys & I got hooked up with a working curve! I forwarded that curve to MW&S.
I am producing power as of when I put that 12v curve in.
Much thanks!
Excellent !
Thank you Todd !!
boB
Quote from: boB on January 16, 2020, 12:00:04 AM
Quote from: Guda on January 15, 2020, 08:07:40 PM
Hi!
I called you guys & I got hooked up with a working curve! I forwarded that curve to MW&S.
I am producing power as of when I put that 12v curve in.
Much thanks!
ANy possibility of someone Posting that 12v Curve here?? Thanks!!
I have same problem with a 12v 1600 Watt Freedom Raptor G4 7 Blade Turbine and Classic 150 w/ VRD.
Thanks!
Excellent !
Thank you Todd !!
boB
Quote from: MidNite in Missouri on January 13, 2020, 09:45:54 AM
Hey Guda,
Call me when you have time, I will help you set-up the Classic for the MO Wind VRD unit.
Todd
MidNite Solar Tech
360.403.7207 x33
M-F, 0800-1700 CST
I have a Pre-Wired VRD unit w/ a MidNite Classic 150 from MO W&S with a 3-phase 12v (AC Wild) 9-Blade 1600watt Freedom PMG wired in (through Rectifiers etc).
My wind average is 10mph. but we get some good Storms up here in Seattle.
It's on a 30ft Pole, and I'm in desperate need of a Wind-Curve Chart for my 12 volt Battery bank (x2 12v Battleborn LiFePo 100ah Batteries in Parallel for 200ah Total).
It's spinning out of control, and all they gave me was a 24 volt Curve, told me to double the amps, cut the volts in half, and GOOD LUCK!!
Ummm, ya, it's not that simple.
Can anyone please help?
Thanks!!