If the absorb minutes were set an 1 minute and the max was 2 hours, and end amps was 6 amps...
Where would float start? At the end of 2 hours or when the amps got to 6 amps??
Is the logic setup for "Which ever happens first"?
Paul
Quote from: plongson on May 22, 2012, 06:13:13 PM
If the absorb minutes were set an 1 minute and the max was 2 hours, and end amps was 6 amps...
Where would float start? At the end of 2 hours or when the amps got to 6 amps??
Is the logic setup for "Which ever happens first"?
Paul
Yes, whatever condition happens first.
boB
Thanks boB.
Hi bob any news on the update that will make end amps work? Cheers!
Heck, mine is working with the last firmware release.
Quote from: offgrid on May 23, 2012, 05:00:21 PM
Hi bob any news on the update that will make end amps work? Cheers!
It is fixed and will be released just as soon as we test this newest code we are working on.
I'm not sure but plongson may be referring to the placebo ending amps mode which has been in every
version of firmware. Unless maybe he got a version to test ?
Either way, the fix should be coming within a week I would think.
boB