Post by: Saggys on May 05, 2024, 07:39:19 PM
I am hoping I can use a MNEPV-300 20A breaker as a 125vdc 2 pole PV input breaker. It is polarized and the one side is jumpered + to - with a copper bar jumper.

I am thinking remove the jumper and install the PV in to the breaker and the load side to the AIO PV input.
The breaker polarity should remain correct. The breaker has a copper jumper for a series connection I believe for the 300 volt rating, the two tabs are ganged together.

Will this work? I already have it and it would save me money.
Title: Re: MNEPV-300 20A used as 2-pole?
Post by: FNG on May 08, 2024, 08:08:10 AM
That should work yes. We typically take the 2 pole 600V breaker and remove the jumper and use it to break PV+ and - of 600V as it is all one circuit this works well
Title: Re: MNEPV-300 20A used as 2-pole?
Post by: Saggys on May 08, 2024, 07:39:38 PM
Thank you for clarifying FNG. 8)