Inverters => Midnite DIY Series => Topic started by: sungrip on June 28, 2024, 10:35:13 PM

Title: MN3548DIY BatOverCurrHW
Post by: sungrip on June 28, 2024, 10:35:13 PM
Getting a persistent flashing red Fault LED and fault code 05 - Battery Overcurrent hardware protection regardless of trying different batteries.
Title: Re: MN3548DIY BatOverCurrHW
Post by: Wizbandit on June 29, 2024, 09:46:55 AM
The internal DC to DC power converter section is busted.  Causes:
Not enough Ah of battery, the DIY3548 needs 300 to 500Ah of battery
Battery cables too small gauge or too long.
Load(s) with motors that have big startup currents, A/C units, water pumps, air compressors...
Title: Re: MN3548DIY BatOverCurrHW
Post by: sungrip on July 01, 2024, 01:40:48 AM
Thanks. 
No load has ever been connected to this inverter.  I'm getting the error with no load. 

Regarding battery cable gauge and length, I'm testing with 4' 4AWG to a fuse and 7' 2AWG to the battery.

The test battery is a 120Ah 48V LFP
Title: Re: MN3548DIY BatOverCurrHW
Post by: Saggys on July 12, 2024, 01:32:03 PM
I also have a 3548 with #2 awg and a 200ah LiFeP04 battery with no issues. I believe the manual states a 100ah minimum.