I have an MNDC125 enclosure containing an MNEDC 80A breaker which feeds a 24V inverter. Cabling inside enclosure is 2/0, then 2 AWG to the inverter.
This setup has been working fine at 30A for a year or more.
I've recently begun placing higher 70A (~1700W) loads, and notice within a few minutes the 80A breaker is hot to the touch (160F).
Is this expected behavior running so close to the breaker's limit?
I've double-checked that the nuts are all torqued as specified (30 in-lb), and neither the lugs nor the cables seem particularly warm themselves.
Thanks
Adam
What are you running for an inverter? I have seen recirculating currents / Ripple cause this on smaller breakers. The MNEDC1-100A breakers really may be to small for larger inverters you may want to consider the 125 or even 175A breaker depending on the inverter.