Other MidNite Electronics => MidNite SPD (Lightning arrestor) => Topic started by: David on July 19, 2012, 05:33:34 PM

Title: MNSPD300 with Kestrel 110V turbine?
Post by: David on July 19, 2012, 05:33:34 PM
I have a e300i Kestrel turbine.  The maximum voltage is 400VDC from the turbine before the voltage limiter.  The nominal voltage is 135VDC.  I just wanted to verify that the MNSPD300 would be the correct choice?  I assume the 300+VDC from the turbine would happen rarely..
Title: Re: MNSPD300 with Kestrel 110V turbine?
Post by: jhubacka on July 31, 2012, 07:10:17 PM
Hello David, I just logged on to ask the exact same question. Did you get an answer ?

Title: Re: MNSPD300 with Kestrel 110V turbine?
Post by: Halfcrazy on July 31, 2012, 08:12:53 PM
Well the limiter is going to limit the upper voltage so the 300 should be just fine. The Kestrel will never be running without the limiter so life should be good.

Ryan