Inverters => The Rosie => Topic started by: umtiwdfn on November 03, 2024, 07:37:57 PM

Title: Rosie Missing Specs
Post by: umtiwdfn on November 03, 2024, 07:37:57 PM
I'm trying to find some Rosie information that does not seem to be in the manual:
Title: Re: Rosie Missing Specs
Post by: FNG on November 05, 2024, 05:54:41 AM
Rosie has a max passthrough current of 60 amps at 240VAC in passthrough and a max DC charge current of 120 amps
Title: Re: Rosie Missing Specs
Post by: umtiwdfn on November 05, 2024, 10:21:58 AM
So if I have 50 amps worth of load and a significantly depleted battery when grid AC becomes available, does the breaker just pop or does the rosie back off on charging until the load drops?
Title: Re: Rosie Missing Specs
Post by: FNG on November 05, 2024, 12:44:31 PM
In your example (Assuming you are feeding it with a 60A breaker) what would happen is 50A would go to the load and 10AAC would go towards charging. In other words, Yes the Rosie will bck its charger down to obey the AC input breaker size to prevent it from tripping