A Forum run by Enthusiasts of MidNite Solar

Charge Controllers and Clippers => The "Classic" charge controller => Classic and Classic Lite BETA Firmware... => Topic started by: d98ag17 on December 22, 2012, 07:03:25 PM

Title: firmware update failed
Post by: d98ag17 on December 22, 2012, 07:03:25 PM
 >:(when I tried to update the firmware update the black box opened , the the second box opened and said update failed. I can't find a version by any of the methods you mentioned, pushing status or right arrow. I'm not sure how to power down the classic, I have a OUTBACK inverter 8048, classic 150 and classic lite.
Title: Re: firmware update failed
Post by: Vic on December 22, 2012, 07:25:39 PM
Hi d98..,

To power-off the Classic that you are trying to update,  turn off the PV (or what is the input energy source)  In Circuit Breaker,  then power off the Output Circuit Breaker that connects that Classic to the battery  (this is breaker is what powers the Classis Off).

To update the FW,  go through the initial steps,  and when you are asked to power Up the Classic,  turn on only the Battery breaker on the output of the Classic.  When you are successful with the update,  you can then turn on the Input breaker.

Good Luck,  HTH,   Vic