Hello All--

First time poster here.  I'm building a small, off grid, passive solar house in Maine with a modest 1.2 kw array.  My question concerns the dc load center.

I plan to wire the house for both ac and 24vdc.  Each dual-gang outlet box will have two ac and two dc sockets.  All lighting will be dc.  Given that all dc loads will be low amperage (no circuit above 15 or 20a) I'm wondering why I should go to the expense of using breakers like Midnite's rather than an ATC fuse block such as one might find on a boat or RV.  And, assuming I use fuses, is there a good reason to go with something like Midnite's fuses and fuse holders on a DIN rail rather and ATC fuses?

As an aside, it's puzzling to me why there's relatively little information and discussion about dc load centers on line.  Any thoughts about this?

I greatly appreciate being able to take advantage of the collective wisdom and experience on this forum.

Best to all--

Paul
Title: Re: DC load center for new small house
Post by: Westbranch on June 03, 2013, 12:29:07 AM
FYI Square D "QO"  CB's are rated to 48v DC as are the load centers.
Title: Re: DC load center for new small house
Post by: Robin on June 03, 2013, 03:07:02 AM
I tried to design out DC load circuits about twenty years ago. The DC circuits for a house are not standard. There is no standard for DC sockets. The blade automotive fuses are not listed for use in residential wiring although I do not see why they wouldn't work?
As an engineer who designs systems to meet the NEC it is important to design around standardized parts as much as possible. People do use our little Big Baby and Quad boxes for DC loads all the time. They also use the MNDC15 for more circuits. Quite a few people even use our combiners. Like I said though, I try to not recommend DC circuits other than a light circuit in the equipment room. Today's inverters are efficient enough that people can use regular appliances. Keep in mind that DC circuits in the house may not meet code. I don't know if your house will be inspected or not. The use of automotive fuses will never pass inspection. Another thing to consider is fire insurance. A house that is built to code and has been inspected can have fire insurance. A non code compliant house may not qualify.
Title: Re: DC load center for new small house
Post by: Halfcrazy on June 03, 2013, 05:28:32 AM
To echo Robin. Code compliant is definitely something to think about. Depending on the number of circuits I have used the MNPV6 and MNPV12 with circuit breakers numerous times as DC load centers. I much prefer Breakers as I can open them under load and I can reset them when I do something stupid.

Ryan
Title: Re: DC load center for new small house
Post by: openplanet on June 03, 2013, 09:20:04 PM
Thank you Robin and Ryan.
My main reason for wanting to run DC loads as much as possible is to eliminate the inverter as a failure point.  It seems a pity for a whole RE house to be dead-in-the-water because of an inverter failure.
In any event, I will take your advice and use an MNPV12 with circuit breakers.
Thank you.
--Paul
Title: Re: DC load center for new small house
Post by: dgd on June 03, 2013, 09:43:27 PM
Quote from: openplanet link=topic=1227.msg9583#msg9583
My main reason for wanting to run DC loads as much as possible is to eliminate the inverter as a failure point.  It seems a pity for a whole RE house to be dead-in-the-water because of an inverter failure.

Inverters in general are pretty reliable. A simple insurance is to have a second perhaps smaller inverter for emergency use or spread your ac loads over two medium instead of one large inverter.
I would imagine this would be more economical than dual wiring a house for ac and DC loads.

Dgd
Title: Re: DC load center for new small house
Post by: laszlo on June 03, 2013, 10:07:56 PM
Inverter longevity -- the warranty that most companies in the market provide is more than half the actual MTB of the device. So in general if you have a 5 year warranty on an inverter, which is pretty standard these days, one can expect the inverter to last about 10 years.

A/C power is also considered safer than DC because with alternating current the voltage goes to zero 60 times per second so the breaker has  chance to interrupt it before it starts a fire or causes harm.



Title: Re: DC load center for new small house
Post by: RossW on June 03, 2013, 10:18:47 PM
Quote from: laszlo on June 03, 2013, 10:07:56 PM
with alternating current the voltage goes to zero 60 times per second so the breaker has  chance to interrupt it before it starts a fire or causes harm.

1. The whole world doesn't run at 60Hz.
2. Even if you are on 60Hz, the voltage passes 0V twice per cycle, this 120 times per second
3. Breakers don't wait for a zero crossing to trip

Title: Re: DC load center for new small house
Post by: laszlo on June 04, 2013, 02:16:38 AM
The way I understand  it you can only get an electric shock during the positive half of the cycle, and so that is 60 times per second when the hot goes to 0V.  At any rate, rather than nitpick over this, the key point is that A/C power is much less likely to maintain an arc than DC power since the voltage is attenuated to zero in each cycle. To each his own, but it seems the consensus in this forum is to recommend code compliant AC wiring in the house for the following reasons:

-no DC outlets available
-expense of wiring for DC
-difficulty of obtaining fire insurance for house not wired to code
-DC is more likely to maintain an arc than AC
-you will not find an electrician who will install or service a DC wired house, or an inspector who will pass it





Title: Re: DC load center for new small house
Post by: RossW on June 04, 2013, 03:53:38 AM
Quote from: laszlo on June 04, 2013, 02:16:38 AM
The way I understand  it you can only get an electric shock during the positive half of the cycle

Whoever taught you that is going to get someone killed. Either polarity will send you to your maker without fear or favor!

I wasn't nitpicking for the sake of it - but false information (if repeated often enough) "becomes true!". (Well, it is believed to be true (and repeated by more and more people, thus perpetuating the myth).

No argument that 240V AC is less dangerous than 240V DC to the average punter though! :)
Title: Re: DC load center for new small house
Post by: vtmaps on June 04, 2013, 06:30:57 AM
Quote from: openplanet on June 02, 2013, 08:27:42 PM
I plan to wire the house for both ac and 24vdc.

Stick with AC for the sake of efficiency.  Of course, the inverter represents a loss of efficiency, but running low voltage through your wires also represents a loss of efficiency.   

You will have a much more extensive and inexpensive choice of efficient lighting, fans, etc if you go with AC.  The most efficient exhaust fans you can buy are powered by AC but have DC motors.  Power supplies can be very efficient, so it is usually advantageous to run AC through the house and convert it to low voltage DC at the fan. 

--vtMaps
Title: Re: DC load center for new small house
Post by: openplanet on June 04, 2013, 01:24:53 PM
Thanks everyone for the input.
So...this forum proves its usefulness right out of the starting gate, and I must reconsider my decision about dual-wiring.
I wonder if anyone has done any kind of survey to see what percentage of off-grid systems wire dc-direct to lights and other loads (like a SunDanzer 'fridge).
Title: Re: DC load center for new small house
Post by: Westbranch on June 04, 2013, 02:11:54 PM
Never heard of a survey yet. 

I still have a 1 room cabin that is DC wired but some of the furthest from the Bank get a bit more than 5% loss, no issue with regular quartz halogen but can be a problem with some LED's with tight operating range tolerances.  see avatar...

The new full size place will be 110v AC
Title: Re: DC load center for new small house
Post by: Thirteen on June 23, 2013, 12:01:26 PM
with any system it needs work to keep it running properly. So install a single battery 12v along side of the big bank with a small inverter and 12vdc lights so when things do go wrong you cna have power to wokr on the main bank. If it is during the winter and things go bad you would be able to have a couple of lights to work with. You could always hookup a truck to charge the small battery. Safety first. 13
Title: Re: DC load center for new small house
Post by: zoneblue on June 28, 2013, 08:14:54 PM
There are several of us going the mixed ac/dc route. For me its a no brainer, i have an interest in electronics, we have no kids, live in a tiny place, and live on 3kWh per day.

For most of my loads (at least 90% of the base loads) all the gear is low voltage dc.  Why convert from  24 to 240 then back to 12?

Over the years of living in motorhomes, ive accumulated 24V stuff that is in the upper range of efficiency. We use lots of Dc converters, big and small, which are way more efficient than inverters, in the 95% range.

Our base loads are:

- fridge 24v 70 watts about 40/60 duty cycle
- lighting (about 75 watts of LED). This runs on 24V. Each fitting draws about 800mA at 25volts.
- one custom atom server draws about 15 watts, runs on 19v via a 24-19v converter.
- two laptops run on 12 and 19v , with their own converters, about 12 watts each.
- one desktop with 24" screen. Monitor is 12 Volts, 15 watts via dc converter. CPU has a custom 12-30V power supply board, and runs on 19v converter. Draws 20-40 watts.
- two 2088 waterpumps, one from the stream, one from the tanks. 24v, 30 watts each.
- an electric fence energiser, 12 volts, trivial.
- phone chargers x 2, via 24-5 usb converter
- NiMH, lithium and nicad chargers for various tools, all runs on 12 volts via dc converter.
- cordless phone, still working on that, but its 5.7V using a custom converter.

The only things we turn the inverter on for are power tools, kitchen appliances, and the washing machine.  Personally we like not living in a soup of 50 hz emf hum, although ill grant you all those switch mode power supply probably arent "silent" either, but i tend to put tthem in metal boxes, and use extra capacitance on the input and outputs to try to keep the dc bus clean.

Building Biology says that the earth has several low frequency resonances around the 10 hz range, that are critical to our health and well being. Hence the desire to avoid drowning them out with a much stronger 50hz signal.

As for cabling i run 6 guage from the main dc load  center to 3 sub centers. We got a great deal on the 6awg it was like a dollar something a meter. For branch lines ill use 6mm2, but none of the branchs having fusing over 5amps. So theres no cable loss.

For ac theres only two circuits one to the kitchen and one to the workshop/laundry. Id say about  a quarter of the wiring that we have installed for dc.

But if you really have 20 amp dc loads then yes, maybe you oughta go ac.
Title: Re: DC load center for new small house
Post by: dgd on June 29, 2013, 05:21:52 AM
An interesting post, your years of experience with DC loads, DC to DC converters and conversion efficiences shows just how DC powering can be achieved successfully. 
The only viable alternative is to use an inverter to distribute AC then devices needing low voltage DC convert the distributed AC to DC.
Perhaps thats inefficient but with the ever decreasing costs of PVs to gain extra power the efficiency argument becomes less relevant.

One point you made intrigues me...

Quote from: zoneblue on June 28, 2013, 08:14:54 PM
...
Building Biology says that the earth has several low frequency resonances around the 10 hz range, that are critical to our health and well being. Hence the desire to avoid drowning them out with a much stronger 50hz signal.
...
The last 10Hz resonance (of significant amplitude)  here in New Zealand flattened  a major city with severe loss of life.
Where are these other(?) 10Hz resonances that are somehow critical to our health? published papers on this?

dgd
Title: Re: DC load center for new small house
Post by: phonetic on July 04, 2013, 04:58:02 AM
I have a 24volt DC dist loop wired through the house, using 6 gang wall plates: 2xRG6 coax 2xRJ45 LAN & 2xred/black 30amp Anderson power poles.

All my small gear with wall plugpacks, have been replaced with DC/DC converters all works a treat.
Title: Re: DC load center for new small house
Post by: zoneblue on July 04, 2013, 02:31:23 PM
Quote from: dgd on June 29, 2013, 05:21:52 AM
Where are these other(?) 10Hz resonances that are somehow critical to our health? published papers on this?
dgd

The Building Biology Institute hails from germany, where they can be a bit obsessive about things. The NZ institute has an extensive set of papers. 

See:
http://www.ecoprojects.co.nz/
http://www.hbelc.org/

Building biology is on the eco, slightly fringe end of building practice, ill grant you that, however in general its about getting all the synthetics, pvc, adhesives, composites, fibreboard, foams, acryllic paint etc etc out of the living environment. Sometimes known as SBS or sick building syndrome. Its fairly hard core, they use things like wool, cork and pumice for insulation. They also prefer to minimize the use of metal in roofing, reinforcing, even bracing, (and esp. bedding) to avoid faraday cage effect. Same reason, to allow the earths natural magnetism to percolate undisturbed.

Im certainly no expo\ert, however, and couldnt provide a strong argument for any of this.
Title: Re: DC load center for new small house
Post by: Hialtitude on November 27, 2013, 03:52:53 AM
Quote from: zoneblue on June 28, 2013, 08:14:54 PM


Our base loads are:

- fridge 24v 70 watts about 40/60 duty cycle
- one custom atom server draws about 15 watts, runs on 19v via a 24-19v converter.
- two laptops run on 12 and 19v , with their own converters, about 12 watts each.
-
- NiMH, lithium and nicad chargers for various tools, all runs on 12 volts via dc converter.
- cordless phone, still working on that, but its 5.7V using a custom converter.

Hi, I'm very interested in your post.   Did you build your DC to DC converters as custom or can you buy them.  I can imagine that there's probably 24v to 12v converters, but the 24-19V sounds interesting. 

Also, is there much loss in the conversion, but I'm assuming that it's less than going from DC to AC and then back to DC?   I'd like to use this method for some projects. 

thank you for your time.  GP.
Title: Re: DC load center for new small house
Post by: zoneblue on November 27, 2013, 05:05:57 PM
The first time you put 0.5A into one of those and get 1A out is a real eye opener to how switch mode DC-DC conversion works.

I have quite a collection of them, but have avoided so far the route of large, name brand models such as those made by samlex. For a couple hundred dollars im sure they are good quality, but lack flexibility. I prefer many smaller converters, to match the ridiculous array of voltages used by stuff these days.

- The first ones i got years ago at auction, they had obviously been made custom made in bulk for some kind of business application. They were nominally 24-13.8v (8A), but you could change the voltage divider on the sense end of it easily enough.  I once tried to measure the efficiency under typical load and was astonished to find that with the crappy meters i had it was near 100%. Couldnt tell the loss from the error! Big inductors and caps in them, ill add a pic below later.

- You can find all manner of cheap usb mobile/iphone/etc chargers,  12/24v car adapters, many of which you will find useful and easy enough to hack into off grid life. I also bought a couple of 80W HP car laptop adapters, designed for the corperate market, used off ebay. While designed for laptops, and decent enough quality, i found them to generally have poor thermal design, and lesser efficiency. I think the reason for that is because they have to run off 12 or 24vthey employ auto buck boost. Try to always use a higher input voltage, and buck mode exclusively. This is one big argument against 12v systems.

- You can get relatively cheap fixed voltage converters such as these, with a bit more amps.
http://www.ebay.com/itm/DC-DC-24V-to-19V-10A-190W-Step-DOWN-Waterproof-Power-Voltage-Converter-/321222894255?pt=LH_DefaultDomain_0&hash=item4aca6062af

- Lately i find these just little suckers in particular incredible value for money, $3 ea, and order them in 10 packs.
http://dx.com/p/mini-dc-dc-voltage-stabilizer-regulator-module-red-126106
They seem to have 'upgraded' that model lately to this one. $2!
http://dx.com/p/20083-adjustable-power-supply-voltage-regulating-reducing-module-blue-black-255394 (Has mounting holes)

There is also a version with current limiting, which are good for home brew led arrays.
http://dx.com/p/power-led-driver-constant-current-charger-power-supply-module-cc-cv-156788
(See also my led writeup in sig.)

All those little converters are good for 2 amps continuous, which is enough to run at most a (small) laptop.  These things have been powering our 2 netbooks without issue for the last couple of years, as well all the myriad other dc stuff you tend to have running around the place.

Had none die so far, and the adjustment is fine enough and stable. Set it to 9V, and a year later its still 9V. In a case like my wifi router, which is unhelpfully 7.5V, (which idiot thought that was a good idea), when the AC pack died, it was easier to flick one of those converters on it than try and find a replacement.

I have a couple of better meters now so i should have another go at measuring the efficiency. Like i said being so small they dont have a lot of filtering and i do tend to add capacitors on the input and output sometimes.

I should at this point confess that some of this is at present a real rats nest, but ive ordered some little baby boxes and midnite breakers and whatnot and its a summer project to make it nice and tidy ;)
Title: Re: DC load center for new small house
Post by: ClassicCrazy on December 01, 2013, 11:44:38 AM
zoneblue - are those small DC/DC converters efficient ?  Do they get very warm at 2 amp load ? 
Title: Re: DC load center for new small house
Post by: zoneblue on December 01, 2013, 04:21:19 PM
The regulator chip doesnt really have a heatsink. Theres a bunch of through holes connected to a backplane pcb layer. Thats it. The chip is rated to 3A, but i derate it to 2A for this reason.

The inductor is small, i would say undersized, so there will be some loss there. But being (literally) 1000X  smaller and with variable adjustment makes them so convenient to use.

When say a net book is power up and charging at the same time, there is certainly some warmth there. I will try to measure the efficiency, but to do it accurately requires 4 decent meters, which i dont have. 
Title: Re: DC load center for new small house
Post by: ClassicCrazy on December 02, 2013, 08:23:48 AM
Well the touch test for efficiency  would work for me !  Can't you just take power in and power out ? Why four meters needed , to check the voltage while drawing current ?  I guess that is what those free Harbor Freight meters are for .
Thanks for the info on these - for a couple bucks I am going to get some to have around .

I bought one of the larger type 20 amp ones a few years back off of ebay but didn't think to make sure that the output was variable so it is stuck at 12 volts exactly  which was too low to run the radio I wanted to. I think it may have drawn too much power when not running anything.