Title: what type of wires to use?
Post by: kauaisolarman on December 06, 2016, 04:06:58 AM
So i just finished wiring up my new system together.  it consist of 2 midnite CC 150SL & 200classic.  ran through a wire gutter for clean look.

after all day of wiring i got it done.  sadly as i was browsing the forums i realized i may have use the wrong wires   :o

i am using welding cable for all my wiring but it is not UL approved.  just realized this.  this is mainly the type of wire i used for my setup  ranging from 10-2 awg.
https://www.amazon.com/gp/product/B01JMNMM8S/ref=oh_aui_detailpage_o06_s00?ie=UTF8&psc=1

or

https://www.amazon.com/gp/product/B0167K7GO4/ref=oh_aui_detailpage_o07_s00?ie=UTF8&psc=1

are these wires sufficient or do i need to re do everything and switch to UL approved wires?

i also purchased a set of these which have (UL) rated on them but do not have the NEC wire type designation listed on them.  would these still be NEC compliant or do the NEED to have the (UL) and a NEC wire type designation (thwn,thhn,thw,etc.)?

https://www.amazon.com/gp/product/B00TANRTSO/ref=oh_aui_detailpage_o09_s00?ie=UTF8&psc=1


this article says it needs to have both to be NEC compliant can someone verify?  thanks
http://www.homepower.com/articles/solar-electricity/design-installation/inverter-battery-cables


just want it to be safe. i know NEC guidelines promote safety but is it not safe to use the wires i used above?  i used ferrules/cable lugs for all connections with these wires.

thanks again for any input
Title: Re: what type of wires to use?
Post by: ClassicCrazy on December 06, 2016, 11:06:26 AM
The insulation is different on the approved type wiring. It is rated for different temperatures as well as being very rugged. I think the heating standards especially apply when you put multiple conductors in conduit and run rated amperage's through them. You should do some research and maybe check with an electrician.

I don't have any direct experience with using those welding cables. Big question is do you need it to meet some kind of code inspection ? Probably not or you would have not been asking this question. If you don't have code it all depends on which level of risk you wish to take with your system and safety.

I think I have heard  there can be issues with trying to properly compress all those fine wires in compression terminal blocks.

I know a lot of people have used welding cable for the short runs from inverter to batteries because it costs less for 4/0 welding cable wire.  When I did my system I spent the extra money and got marine grade wire for my inverter partially because I found a place that would make them up with the length and lugs that I specified. They are super rugged and they really know how to crimp terminals on and used the special heat shrink that makes it water tight. Cost was higher than welding cable but I think it was a good investment in the long run because those are not going to ever have any problems. I would have to go look at them to see what marine wire standards they have.

Larry
Title: Re: what type of wires to use?
Post by: ClassicCrazy on December 06, 2016, 11:15:20 AM
I just looked up EWCS Branded  - that is a company trademark and name . It is not any electrical standard.

http://ewcswire.com/blog/

Northern Arizona Wind Sun has a good forum and the question you asked has probably already been asked and answered there

http://forum.solar-electric.com/
Title: Re: what type of wires to use?
Post by: Vic on December 06, 2016, 02:25:00 PM
Hi kauaisolarman,

You  did say,   "   ...   after all day of wiring i got it done.  sadly as i was browsing the forums i realized i may have use the wrong wires   :o

i am using welding cable for all my wiring but it is not UL approved.  just realized this.  this is mainly the type of wire i used for my setup  ranging from 10-2 awg.
https://www.amazon.com/gp/product/B01JMNMM8S/ref=oh_aui_detailpage_o06_s00?ie=UTF8&psc=1

   ...   "

It IS true that screw-type terminals are not designed to accept fine-stranded cable,  and the welding cable that I have seen IS fine strand.

Cables,  crimped with the correct lugs  --  made specifically for fine strand cable should be OK, when correctly crimped.    Crimped lugs will not be a solution for smaller breakers,  busbars,  etc,  with screw connections.  And,  there can still be issues,  if the system will be Inspected for Code compliance (as CC Larry mentioned).

There are provisions in the NEC for cables,   like the VW-1 fire provisions that welding cable may not meet,  etc.  This applies for cables that are inside inhabited structures,  IIRC.

Building wire  with THHN  ratings are easy to use in smaller diameters,  and  this is the type of cable that screw terminals on breakers,  busbars,  etc are designed to accommodate,  and  this building wire is inexpensive.

At the big box retailers,  the reference cable that I use for monitoring the relative price change of building wire (500' #10 THHN stranded) is now about 60% of the price that it was about two years ago  ...   seemingly inexpensive.

It is very important,  IMO,   that the lugs used on fine strand cable,  be intended and designed for that use.    One does not loose connections on any cable,  especially those carrying large currents.

FWIW,   Good luck with the new system.     Vic
Title: Re: what type of wires to use?
Post by: kauaisolarman on December 06, 2016, 03:51:09 PM
thanks for the replies.

I did use lugs or ferrules on all wires that were going into screw terminals/bus bars and also used ferrules on all the circuit breakers so that the stranded wire stays together.

used marine grade anchors
https://www.amazon.com/gp/product/B000NHZYRY/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1

made really good connections for all wires going to a terminal or bus bar with the ferrules.  no lose connections.  all lugs were installed with hammer type crimper and waterproof heat shrink with adhesive lining was used to seal it together.

I read through some earlier posts on the forum and seen people try to tin these stranded wires but the consensus seems to be no solder or tinning, so I purchased a bunch of ferrules and ferrule crimper and went to work.

i am never sending full current rating through any wires.  for example my 2 awg will see 80A max.

Just more worried about the heat resistance and durability of the wire jacket.  don't have to pass any inspections but i tend to be very anal and want to be able to get a good night sleep not worrying about evacuating my house because of you know what

I also purchased a few of these wires that say they are UL rated but they have no NEC ratings on them.  any input on using these wires or should i just purchase all new and look for UL and NEC ratings printed on the jacket.
https://www.amazon.com/gp/product/B00TANRJNO/ref=oh_aui_detailpage_o00_s01?ie=UTF8&psc=1

thanks again people  very helpful
Title: Re: what type of wires to use?
Post by: kauaisolarman on December 06, 2016, 05:06:43 PM
does marine wire have the same NEC ratings as non marine?

was looking at the Vertex wire website and it says all their wire is UL Standard 1426 BC-5W2 (Electric Cable for Boat) compliant.  didn't see anywhere specifying NEC ratings anywhere.

is it OK to use marine cable that has the UL listing but does not have any NEC ratings?

http://www.vertex-marine.com/ul-1426-boat-cable-bc-5w2/battery-cable/8-awg-wire/
Title: Re: what type of wires to use?
Post by: Vic on December 06, 2016, 06:39:05 PM
Hi Kauai..,

1.  Will your system be Inspected by some Building Inspector?

2.  On the Vertex site,  it looks like most of their Boat cable products are Fine-Stranded,   as was your Link to #8 AWG cable.   If you are using ANY fine-stranded cable on screw type terminals on breakers and busbars,  and any other connection that uses a screw to compress a cable or a "shoe" that presses on the cable,   IMO,  this would NOT be OK.   It is possible to use a crimped ferrule on fine strand cables to help reduce the risk of cold flow,  although this might not pass muster of careful inspection.   Personally would not use fine strand cable that is a smaller gauge (smaller diameter) than about #1 AWG,  and then only with proper lugs and crimping.  Would not use ferrules,  either,  as this is one additional point of some resistance in the circuit.

3.  Fine strand cables that have a properly crimped lug,  designed for use on fine strand cable,  and  attaches to a terminal,  using a bolt,  or nut would probably not be considered dangerous.

4. I am not a Code expert,   so the suitability of Boat cable for your system,  verses building wire  (THHN ...),  is something that I cannot comment on,  but,  if your system will need an Inspection,  you should probably speak with the Building Department officials that have specified just what they require in the way of cables,  and also ask what Code Revision that will need to be met.

To me,  the largest issue for any system would be that cables are sized correctly for the Overcurrent Protective Devices (circuit breaker or fuse) that are protecting those cables.   And,  that no fine strand cable is connected to a circuit using a compression type screw terminal.   Also,  meeting Ampacity Derating for ambient temperature,  and number of current-carrying conductors in conduit,  raceway,  etc,  as well as not filling any conduit with an excessive number of conductors.

...   and so on.   Some of the above are probably nits;
If the system will be inspected,  then follow the standards noted by the Authority responsible for the inspection.

Eliminate any fine strand cable terminated by a compression type screw terminal.

Realize that you are in HI,  and sourcing some of the specific parts for a compliant solar installation,  may not be at your finger tips.

Then relax and enjoy the fruits of all of your labor,  after any required inspection.

Just my opinions,   and,  getting a self-installed system on line,  is a real accomplishment,  so congratulations are in order,  even if a few things might need a bit of tweaking.   Vic
Title: Re: what type of wires to use?
Post by: ClassicCrazy on December 06, 2016, 09:51:44 PM
I don't know what a hammer crimper is like but Harbor Frieght tools has an inexpensive hydraulic crimper that works great. You can also find the same type on ebay for low prices.
http://www.harborfreight.com/catalogsearch/result?q=hydraulic+crimper

I have one and it will squash crimps very tight so no air is in them or going to get in there .  It is a good tool to have for all size wires. I did use it to crimp some lugs that were bigger than the biggest die that came with it - but I was able to drill out one of the smaller ones . I usually use one die , then use  to the next smaller die to ensure it is squashed good.

Larry

Title: Re: what type of wires to use?
Post by: kauaisolarman on December 07, 2016, 01:49:03 AM
thanks everyone for the input.

my system will not need to be inspected as it is a home off grid setup.  just trying to be as safe as possible.

guess i am going to switch everything out to UL rated wires with the NEC building wire ratings on them. I have 1 source of marine stranded wire that has both the UL rating and (THW) NEC spec printed on the jacket.  will double check with a local inspector to see if that would be up to standard with the use of the ferrules and if I get the green light i'm going the stranded ferrule route (just because i think its easier to work with)

anyway heres some pics of the progress so far, just sad that i have to start over.

(http://i1068.photobucket.com/albums/u447/rustansouza/solar/IMG_0085_zpsrqgkjiqx.jpg)

(http://i1068.photobucket.com/albums/u447/rustansouza/solar/IMG_0088_zpsngfuetom.jpg)

all sealed up

(http://i1068.photobucket.com/albums/u447/rustansouza/solar/0bc731bc-2881-434a-bbe1-1b294ef4d34e_zpsxa7l0enb.jpg)

I would think that the marine UL stuff would be better thank the regular building stuff as it sees a much harsher environment and conditions with the salt air and all.

I figured being out here in the middle of the ocean using all marine grade stuff would be better/safer than using regular building stuff.

none of the wires that i am using will see anything even close to their ampacity ratings and the breakers are all well below the ampacity rating for the wires.  for example the 6awg will see 40A at max and also has a 40A breaker used with that wire.  only thing in my system that comes close to ampacity rating is the 4AWG that is comming out of CC 1 to the battery and even that will only see 80A max and also has a 80A breaker on it.  all my wires should be adequately protected from overcurrent but i'm not sure if that will protect me from a fire.
Title: Re: what type of wires to use?
Post by: ClassicCrazy on December 07, 2016, 01:39:44 PM
 Looks nice. I don't know about those ferrules on the ends of the wires though. When you crank it up get it too full capacity and use a thermal imaging camera and look at all those connections and see if they get warm. Then you know you don't have good connections.

I don't get what is wired up to your shunt . One side should go to the battery and nothing else. 

Larry

Title: Re: what type of wires to use?
Post by: Vic on December 07, 2016, 04:45:58 PM
Hi Kauai..,

YES,  that installation looks very neat,  indeed.

The busbar on the top of the Shunt should be fine.  It is a bit difficult to see clearly,  but guess that the cable from the other side of the Shunt  --  the bottom in the photo goes under the busbar on the top of the shunt (and does NOT connect to that bar),  and proceeds directly to the battery negative.   That end of the Shunt should only connect to that end of the Shunt,  and the battery negative,  and nowhere else.

Am not a fan of ferrules,  as mentioned before,  but,  if there is no noticeable heating when the charging is maxed out,  or the inverter loads are maxed out,  then things are probably OK.

An inexpensive IR non-contact gun-type thermometer should be able to measure the temperatures of busses,  ferrules,  etc.

Vic
Title: Re: what type of wires to use?
Post by: kauaisolarman on December 07, 2016, 05:08:33 PM
thanks guys

as far as the shunt goes  it is wired to the part of the box that says "connect battery negative here".  i was planning to connect battery negative there and just run that small jumper from there to the battery side of the shunt.

i was unsure about if i connect the battery ground to the stud on the box it will be bonded through the box to the earth ground that is also connected to the box.

should i just remove the jumper, not use the battery negative connection on the box and just run the battery negative straight to the shunt?

that was going to be my next question.

if not using ferrules then what would i use? even the Thhn building wire is "B" stranded and i was under the impression that no stranded wire can go under the screw type cinnections that are on the busbars?  if using building thhn "A-B" stranded how would they terminate into the busbar?

thanks again for input
Title: Re: what type of wires to use?
Post by: Vic on December 07, 2016, 06:04:35 PM
Hi kauaisolarman,

First,  all of the busbars,  circuit breakers,  etc,  that use a screw as the connection method are designed to use THHN stranded cable.

Most THHN cable is 19 strand cable.  Small diameter and large diameter THHN cables might have 31 strands.   These cables are NOT Fine Strand types.   So,  NO ferrules would be required,  or desirable.

Am not certain just what panel you are using,  so,  should not comment of just where the connection to your ground rod/system should be made.

Regarding the Shunt,   Is there a piece of cable that is across the Shunt,  thus shorting it ?? ?

If there is this short across the Shunt,  it is not necessary,  as with a huge current flowing through it --  500 Amps  --  it drops only 50 millivolts,  which if  0.05 volts.  At 50 Amps of current the drop is 0.005 volts.

It is not clear in the photo if that cable from the lower bolt on the Shunt connects to the busbar mounted on the top of the Shunt.

FWIW.   Thanks for any clarification.   Vic
Title: Re: what type of wires to use?
Post by: kauaisolarman on December 07, 2016, 08:37:51 PM
thanks vic.  the cable on the "battery" side of the shunt is NOT connected to the busbar on the other side of the shunt.  it is connected to the stud that comes attached to the BOX where i would also connect my battery negative cable directly to. 

basically battery negative going to stud on box and another wire going from the stud to the "battery negative" side of the shunt.

only battery negative is connected to the side of the shunt that WbJr is sticking out past.

thanks for the clear up with the building thhn.   may just switch everything to that thhn and not do any ferrules.
Title: Re: what type of wires to use?
Post by: ClassicCrazy on December 08, 2016, 09:54:53 AM
If it was me I would run a cable - just one connector on the battery side of the shunt directly to the battery negative and not go to any buss bars. That makes just one solid connection and every other negative in the system would go to the other side of the shunt via bus bar or directly on that other side of the shunt bolt.

I wasn't sure from what you said - but the wiring from the battery side of the shunt has to be sized to take every load of the whole system including the inverter and associated surge ratings of the inverter.

Larry
Title: Re: what type of wires to use?
Post by: Vic on December 08, 2016, 05:15:42 PM
Hi Kauai..,

Thanks for the info on the wiring of the Shunt,  to the battery negative.   That sounds fine to me,  although,  it does look like this cable does step-down to a considerably smaller cable,  which could be an issue ...  believe that this is what Larry was mentioning.

Think that you may have a Magnasine inverter ...   cannot see your Signature now,   but the inverter cables (including those going to the 3/8" bolts on the Shunt),  and battery interconnects DO need to be sized for the current rating of the Main DC breaker that feeds the Inverter.   What is the size of this breaker?

Your ferrules may be OK,  at least most of them.   I do not want my personal opinions to discourage you,  to the point of you feeling that you need to tear out much of that cable.  You have done a very nice,  neat and clean install.

If you could check the torque on each screw that has a ferrule connection,  load the system heavily (on the inverter),  in bright sun,  with the battery being charged in Bulk,  and measure the temperature of each connection with an IR thermometer,  you may find that the crimps,  ferrules,  screws and bolts show very little temperature rise.  If so,  you should be fine.

More later,   Thanks for the info,   Vic

Title: Re: what type of wires to use?
Post by: kauaisolarman on December 08, 2016, 08:55:00 PM
Quote from: Vic on December 08, 2016, 05:15:42 PM
Hi Kauai..,

Think that you may have a Magnasine inverter ...   cannot see your Signature now,   but the inverter cables (including those going to the 3/8" bolts on the Shunt),  and battery interconnects DO need to be sized for the current rating of the Main DC breaker that feeds the Inverter.   What is the size of this breaker?


thanks for the response.

cables from battery all the way through to inverter is 2AWG.  80A breaket will be used between the battery and the main power busbar, then 60A breaker between main bus bar and inverter.  all running 2awg wire.

this 48V system is only intended to run an air conditioner (6000btu 500watts max draw) and refridgerator (another 600w max).  inverter is a cotex 2000watt so max amps it would see is 42@48V..

the aquion batteries that this system will charge has absorb 59V and float 55V.  when batteries are reading 48V the are at 90% dod.   full charge reading is 55V.

i am also running the tristar pwm controller off the battery bank and hopefully using it as a diversion controller to heat a 48V 2000W heating element to utilize the excess power from my array.

total load off the battery bank with the inverter and dump load would be about 3800 watts maximum or about 73A assuming 52V battery state (never see more than this much load).

so
80A breaker for battery 2 awg (between battery bank and main positive bus bar)
60A breaker for inverter 2 awg (between main positive bus bar and inverter)
40A breaker for tristar PWM 8awg in/6awg to load (40A for tristar and 40A for load)
80A breaker for CC#1 with PV 3850watts 4AWG (between CC 1 and main positive bus bar)
50A breaker for CC#2 6awg (power source undetermined but 2000W max power input) (between CC 2 and main positive bus bar)
Title: Re: what type of wires to use?
Post by: CDN-VT on December 08, 2016, 10:57:23 PM
I would move the Shunt to the LEFT mounting holes & give more room so the pos cables are NOT close !

(http://i1068.photobucket.com/albums/u447/rustansouza/solar/IMG_0088_zpsngfuetom.jpg)
Title: Re: what type of wires to use?
Post by: kauaisolarman on December 09, 2016, 06:36:08 PM
will do.

decided to change all wires to UL approved stuff.

going to stick with marine fine stranded 2 awg for the battery to inverter cables.

i need help finding a good source for 2awg lugs (1/4, 5/16, 3/8) that are rated for fine stranded marine grade UL rated wire.

the lugs that i am currently using are UL rated from ANCHORbut i cant tell if they are for fine stranded cable or not.  can anyone tell me for sure how to determine if the UL approval is for the Fine stranded wire type.

the data sheet that is with the advertisement on amazon says that fine stranded wires will improve a crimped joints performance.  does that mean i can use these anchor lugs with my fine stranded tinned marine grade UL listed 2awg wire?
https://www.amazon.com/gp/product/B000NI5CS4/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1

thanks for any input.  other than the NEC requiring lugs that are specifically designed for fine stranded wire i cannot find information on how to determine this information.  all seems to be UL486A approved?
Title: Re: what type of wires to use?
Post by: Vic on December 09, 2016, 08:30:33 PM
Hi Kauai..,

Just looked at the Wind-Sun online store,  but could not find relatively large crimp lugs of any kind,  and could not find them on the Colorado Solar (SPS) site either.

But searching for "  fine strand crimp lugs   " should yield some results.

As an aside,  here is a Tech Note on this topic:
https://www.nema.org/Technical/Documents/Bull_105_Fine-Stranded%20Connections.pdf

Sorry to have been raining on your parade.

Will look further for appropriate lugs.   Good Luck,   Vic
Title: Re: what type of wires to use?
Post by: Resthome on December 09, 2016, 11:35:32 PM
Quote from: kauaisolarman on December 09, 2016, 06:36:08 PM
will do.

decided to change all wires to UL approved stuff.

going to stick with marine fine stranded 2 awg for the battery to inverter cables.

i need help finding a good source for 2awg lugs (1/4, 5/16, 3/8) that are rated for fine stranded marine grade UL rated wire.

the lugs that i am currently using are UL rated from ANCHORbut i cant tell if they are for fine stranded cable or not.  can anyone tell me for sure how to determine if the UL approval is for the Fine stranded wire type.

the data sheet that is with the advertisement on amazon says that fine stranded wires will improve a crimped joints performance.  does that mean i can use these anchor lugs with my fine stranded tinned marine grade UL listed 2awg wire?
https://www.amazon.com/gp/product/B000NI5CS4/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1

thanks for any input.  other than the NEC requiring lugs that are specifically designed for fine stranded wire i cannot find information on how to determine this information.  all seems to be UL486A approved?

Ultra flexible (Type 3) stranding is used in Ancor Marine Grade wire. The Ancor HD lugs are made for this type of flexible Marine grade wire. All my lugs and Ancor boxes from West Marine are on the boat 120 miles from here so I do not know what marking are on the lugs or Ancor boxes they where sold in. Ancor makes a crimper for insulated lugs up to 10awg. This is a double crimping tool. Not sure what they recommend for their uninsulated HD lugs. Might be worth it to call them to verify as they meet the Marine boating code but not sure about NEC codes. I would like to see MidNite eliminate these screw terminal and provide for lug connections for the Classic CC.  Boat owners have no choice but to use Marine Grade flexible wire or fail Marine surveys for insurance required by most marinas.
Just my $.02
Title: Re: what type of wires to use?
Post by: kauaisolarman on December 10, 2016, 02:00:29 AM
thank you.

i just wanted to make sure that the Lugs im using are designed to be used with the fine stranded marine wire.

I dont have to worry about any inspections so i am just going to make sure that all the wires/components that i am using are at least UL rated.



 
Title: Re: what type of wires to use?
Post by: sigp2101 on December 15, 2016, 10:58:51 AM
Quote

cables from battery all the way through to inverter is 2AWG.  80A breaket will be used between the battery and the main power busbar, then 60A breaker between main bus bar and inverter.  all running 2awg wire.

this 48V system is only intended to run an air conditioner (6000btu 500watts max draw) and refridgerator (another 600w max).  inverter is a cotex 2000watt so max amps it would see is 42@48V..


Out of curiosity, your inverter will never be able to pull more than 41.6 A from your batt bank. Why are you using higher rating breaker than that? (60 A) I would use way less than max inverter Amps rating on both sides of input-output. To protect wiring and equipment you have to create bottlenecks aka breakers. For example if your inverter is capable of 18A on output side you will limit that to 10-15 amps so it will never work at max for prolonged period of time.
To stay safe you always oversize wire and under size breakers. This will prevent melting wires and fire hazard in equipment.
Title: Re: what type of wires to use?
Post by: Powerplay on December 15, 2016, 03:59:43 PM
QuoteTo stay safe you always oversize wire and under size breakers.

Or size the breaker correctly to the wire it protects.
Title: Re: what type of wires to use?
Post by: CDN-VT on December 18, 2016, 12:25:42 AM
Some ONE have the controls,, to have a like , thumbs up etc.


IS there an EASY wat to have a vote / thumbs up  area on this forum
VT
Title: Re: what type of wires to use?
Post by: TomW on December 18, 2016, 07:51:48 AM
Quote from: CDN-VT on December 18, 2016, 12:25:42 AM
Some ONE have the controls,, to have a like , thumbs up etc.
Were a small bit behind ,, BUT dot test B4
Wind sun suck &
12 YO kids do NOT KNOW !!! LEARN & CHEAK
VT


CDN-VT;


Can an old fart get that translated to American English?

I just don't understand the abbreviations and slang these days. I got the 12 year old kid bit but the rest blew by like a 10 year old on a dirt bike. I "think" it has to do with online "experts", which I ain't.

Tom
Title: Re: what type of wires to use?
Post by: ClassicCrazy on December 18, 2016, 12:28:34 PM
Quote from: Resthome on December 09, 2016, 11:35:32 PM



Ultra flexible (Type 3) stranding is used in Ancor Marine Grade wire. The Ancor HD lugs are made for this type of flexible Marine grade wire. All my lugs and Ancor boxes from West Marine are on the boat 120 miles from here so I do not know what marking are on the lugs or Ancor boxes they where sold in. Ancor makes a crimper for insulated lugs up to 10awg. This is a double crimping tool. Not sure what they recommend for their uninsulated HD lugs. Might be worth it to call them to verify as they meet the Marine boating code but not sure about NEC codes. I would like to see MidNite eliminate these screw terminal and provide for lug connections for the Classic CC.  Boat owners have no choice but to use Marine Grade flexible wire or fail Marine surveys for insurance required by most marinas.
Just my $.02

John - I am curious why on marine their code always wants that fine stranded wire ? Is there some logical reason like it handles bouncing around in ocean swells better ?

Larry
Title: Re: what type of wires to use?
Post by: Resthome on December 18, 2016, 02:36:18 PM
Quote from: ClassicCrazy on December 18, 2016, 12:28:34 PM
Quote from: Resthome on December 09, 2016, 11:35:32 PM



Ultra flexible (Type 3) stranding is used in Ancor Marine Grade wire. The Ancor HD lugs are made for this type of flexible Marine grade wire. All my lugs and Ancor boxes from West Marine are on the boat 120 miles from here so I do not know what marking are on the lugs or Ancor boxes they where sold in. Ancor makes a crimper for insulated lugs up to 10awg. This is a double crimping tool. Not sure what they recommend for their uninsulated HD lugs. Might be worth it to call them to verify as they meet the Marine boating code but not sure about NEC codes. I would like to see MidNite eliminate these screw terminal and provide for lug connections for the Classic CC.  Boat owners have no choice but to use Marine Grade flexible wire or fail Marine surveys for insurance required by most marinas.
Just my $.02

John - I am curious why on marine their code always wants that fine stranded wire ? Is there some logical reason like it handles bouncing around in ocean swells better ?

Larry

Larry

A wire could hardly find a more hostile environment than aboard a boat. On-board wiring is salted and doused, shaken and whipped, crushed and abraded, exposed to sunlight, subjected to heat, and coated with petroleum.  House wiring will long endure these conditions.

Never use solid wire on a boat. Wave or motor induced oscillations eventually fracture solid wire. Boat wiring must have the flexibility stranding provides. Boat owners should use only the most flexible wire, called Type 3. I believe most marine wire is Class K (Type 3) 30 AWG copper tinned strands which is very flexible.

The wire must be copper, but even copper corrodes in the marine environment, and corrosion is the primary cause of electrical failures on a boat. Plating each strand of the wire with a thin coat of tin â€" called tinning â€" dramatically improves corrosion resistance. The additional cost of tinned wire is nominal, the benefits substantial.

Title: Re: what type of wires to use?
Post by: ClassicCrazy on December 19, 2016, 12:36:43 AM
I thought there must be a good reason - thanks for the explanation John. But if it is good enough for boats you would think it would be good enough for home use too.
Title: Re: what type of wires to use?
Post by: Resthome on December 19, 2016, 01:46:35 PM
Quote from: ClassicCrazy on December 19, 2016, 12:36:43 AM
I thought there must be a good reason - thanks for the explanation John. But if it is good enough for boats you would think it would be good enough for home use too.

Oh I think it's good enough for home, just more expensive in most cases. The draw back is the terminal block and bus bars that use a screw to tighten down on the small stranded wires may come loose after time.
Title: Re: what type of wires to use?
Post by: grgdgreek on December 19, 2016, 03:07:37 PM
Just put ferrules on em' and you're all set

George
Title: Re: what type of wires to use?
Post by: Resthome on December 19, 2016, 03:46:28 PM
Quote from: grgdgreek on December 19, 2016, 03:07:37 PM
Just put ferrules on em' and you're all set

George

Exactly.  Now get it to fit in that terminal block   :-\
Title: Re: what type of wires to use?
Post by: grgdgreek on December 19, 2016, 04:04:22 PM
Yeah, I had a hell of a time getting them to fit...
Still trying to wrap my head around the small terminal block

George
Title: Re: what type of wires to use?
Post by: Vic on December 19, 2016, 05:17:25 PM
Just to beat this topic to death,  a bit more;

Anyone who believes that one "just" needs to use some ferrules,  and one is all set,   PLEASE read this Article,  it is only a couple of pages:

https://www.nema.org/Technical/Documents/Bull_105_Fine-Stranded%20Connections.pdf

This was referenced in this Thread  previously,  but there are ferrules,  and there are ferrules.   And,  there are many,  many different crimpers,   dies,  and cable stranding classes.

Any ferrule must be marked and listed for use with a specific class of stranding in a cable,  AND a crimper that is appropriate to the cable and ferrule MUST be used.

This is in the Code.   Even for systems that will not be inspected,  using proper cable connections is an important safety matter.

Ferrules will add one,  or two additional  resistance points per cable.

I would guess that Anchor fine strand cable would be compatible with Anchor Lugs.   But  this should be confirmed by Anchor,  by asking for a compatibility table,  or similar,  that states which Lug part number is compatible with each cable part number,  of interest.

Anchor should state which Crimper/Die is to be used for each size of cable and lug that is going to be used.

Am not a real Code guru.  And some parts of the more recent NEC really do seem to be a bit excessive.   But,  sizing cable,  breakers,  and doing proper terminations is one of the most important,  basic things that need to be done to make a system as safe as possible.  An electrical fire,  in  a power generating system is an ugly thing.

Not to put too fine a point on it ...   IMO,   Vic

Title: Re: what type of wires to use?
Post by: TomW on December 20, 2016, 07:56:55 AM
Vic;

Agree on your beating it to death comments. Especially where code compliance or possible future insurance coverage may matter.

This cable and ferrules confusion is exactly why giving online advice to folks with unknown skills / knowledge could possibly lead to problems.

Lots of little gotchas hidden in a simple statement like "just use ferrules". Improper application of this advice can add more points of failure if done incorrectly due to inexperience.

Just because I think it matters.

Tom
Title: Re: what type of wires to use?
Post by: grgdgreek on December 20, 2016, 12:11:32 PM
Ouch



G
Title: Re: what type of wires to use?
Post by: Vic on December 20, 2016, 01:03:55 PM
Hi George,

I did not mean for my comments to be an attack on you.

I should have tried to make my recent comments more generic,  and less specific.

EDIT:
Your comments were strongly implied by others.

I was just trying to be emphatic,  that without some specifications and control of the connection ends,  and the tools to crimp them,  the outcome is not controlled.

Charging batteries often takes a number of hours,  at relatively high currents,  so even small connection resistance can cause significant heating,  over a fairly long period of time.

Also,  thermal-cycling induces additional cold-flow,  and loosening of many fasteners,  which can cause a  rise in connection resistance.

Sorry,   Vic
Title: Re: what type of wires to use?
Post by: grgdgreek on December 20, 2016, 01:11:15 PM
No problem Vic!
I love this forum + everyone is just offering their opinions and knowledge. :-)

George
Title: Re: what type of wires to use?
Post by: sigp2101 on December 20, 2016, 02:07:27 PM
DIY-ers should always go above and beyond minimum code requirements. Because that is what the code is. Lack of additional knowledge training and expertise is what creates problems if you just adhere to code as a novice. People often think that using a minimum will give them desired outcome. Most of the time minimum is not enough.
Marine grade wire is excellent choice only if termination of those ends are also per specs. Strip - flux - solder by dipping into molten solder. Do not use soldering iron on thick wire. You are after wet look of the soldered end. Not frosty look or cracked look but shiny and wet look. Put end into the block tighten per spec and after one hour tighten each screw again. Revisit tomorrow and retighten again if needed. This way you will have solid contact that will last.