General Category => General Discussion => Topic started by: cindy on September 23, 2020, 06:07:08 PM

Title: neutral ground bond
Post by: cindy on September 23, 2020, 06:07:08 PM
I have an off grid 24vdc system that was installed in March 2009. The system includes:
•   Midnite Epanel MNE250AL+
•   Outback VFX3524, FM60, mate 2
•   3 Rolls Surrette 8CS25P
•   6 sharp 216 panels
I am now adding a Kohler 8.5 KW generator to the system. Questions:
•   I’ve read there should be only one neutral-ground bond. Is this correct? I have a neutral ground bond in the epanel. The Kohler generator comes pre-wired with a neutral ground bond but this can be disconnected.
•   What else should I be thinking about? It has been 10+ years since my system was installed.
Thank you!
-cindy
Title: Re: neutral ground bond
Post by: ClassicCrazy on September 23, 2020, 08:13:49 PM
If you asking about what is code you probably want to consult with a local electrician.  They probably know what local inspectors want to see in your area.
As far as neutral and ground being bonded - in a conventional house it is usually at the first place where the electric comes down from the service.   But I am no electrician.
The idea I believe is so that if anywhere else on the system a hot touches either the neutral or the ground it will trip the breaker.  You don't want current ever to potentially running through the ground.  Someone else can correct me if I have that theory wrong.
But as far as adding generator to the mix I have no idea the right way it is supposed to be done.
Maybe someone else does.

Larry
Title: Re: neutral ground bond
Post by: Kent0 on September 24, 2020, 10:08:29 PM
Portable generators with outlets shouldn't have the neutral/ground bond removed. Many of those have GFCI breakers or outlets and create problems when attempts are made to connect them to a house. A fixed-in-place generator that is permanently wired to the house power system should have the neutral/ground connection removed unless it is being wired to a transfer switch that also switches the neutral.
Title: Re: neutral ground bond
Post by: cindy on September 25, 2020, 03:05:26 PM
Thank you. The Kohler 8.5kw gen is a stationary unit. Will run permanent connection from gen to small breaker box in house (no neutral ground bond) then a 110 leg to Midnite Epanel. The Midnite epanel contains a neutral-ground bond.

This is the plan. Feedback appreciated.

Would like to hire an electrician for this but live in a rural unincorporated area 5 miles outside a village with population 132. Not a lot of electricians 🤣. Even fewer willing to work on PV.
Title: Re: neutral ground bond
Post by: cindy on September 29, 2020, 08:29:35 AM
Two additional notes in relation to my last post.

1. Since posting, I've read there may be load imbalance issues from using only one leg of a 240v line?

Xantrex and Outback make 240v to 120v step down transformers for $450 to $600. I would be interested in hearing thoughts on this.

2. I found a more recent Outback Off-Grid Epanel wiring diagram than the 6-30-2007 version I used 10+ years ago when installing my system. The newer version does not show a neutral-ground bond in the epanel. https://www.midnitesolar.com/pdfs/classic_simple_flow_diagram.pdf (https://www.midnitesolar.com/pdfs/classic_simple_flow_diagram.pdf)

Is Midnite now recommending NO neutral ground bond in the epanel?
Title: Re: neutral ground bond
Post by: ClassicCrazy on September 29, 2020, 12:12:09 PM
Maybe you can get a design consult with one of the bigger suppliers of equipment like Northern Arizona Windsun or AltE .
Might be worth a few bucks for them to take the time to evaluate your system and make recommendations.

Larry
Title: Re: neutral ground bond
Post by: cindy on September 29, 2020, 12:46:20 PM
Thanks Larry. Didn't know that was an option.
Title: Re: neutral ground bond
Post by: Kent0 on September 30, 2020, 12:06:57 AM
The questions as to where the best location for the neutral ground bond connection depends on situation specific factors: inverter type, off-grid, grid connected, mobile? With no one answer applying for all, it makes sense that the E-panel wiring diagram doesn't include it. Haven't looked at the manual, but it seems like the sort of issue that should be addressed there. For off-grid, making the neutral ground bond in the E-panel is probably the best choice, but doing it in a load center instead is an alternative.
Title: Re: neutral ground bond
Post by: cindy on September 30, 2020, 07:41:45 AM
Thank you Kent0. Your explanation makes complete sense. I found the most recent version of my Epanel manual on the website and you are correct, the topic of neutral-ground bond is covered in more detail there.