Other MidNite Electronics => MidNite SPD (Lightning arrestor) => Topic started by: schroew on January 28, 2022, 08:18:31 PM

Title: SPD-300-AC on an Ecogen Generator
Post by: schroew on January 28, 2022, 08:18:31 PM
I am getting an ecogen generator installed in a few weeks and would like to know if it is approved/supported to put a SPD AC on the AC line into my Magnum inverter ?
Title: Re: SPD-300-AC on an Ecogen Generator
Post by: mike90045 on January 29, 2022, 02:18:31 AM
I'd put one on the Gen input and also on the Grid input
Title: Re: SPD-300-AC on an Ecogen Generator
Post by: schroew on January 29, 2022, 09:39:56 AM
No grid for me. Thx for the reply. I’ll pickup a couple this morning.
Title: Re: SPD-300-AC on an Ecogen Generator
Post by: schroew on January 29, 2022, 09:41:12 AM
It was ordered last April and just arrived if anyone was wondering.
Title: Re: SPD-300-AC on an Ecogen Generator
Post by: schroew on May 31, 2022, 10:13:59 PM
This works with 120v ac? I dont have any 240v breakers in my panel and the generator input is 120v..
Title: Re: SPD-300-AC on an Ecogen Generator
Post by: boB on May 31, 2022, 11:51:14 PM
Quote from: schroew on May 31, 2022, 10:13:59 PM
This works with 120v ac? I dont have any 240v breakers in my panel and the generator input is 120v..

Yes, an SPD-300 will work with 120VAC.   120V to GND and Neutral to GND with the two halves.

Oooops...   Bad wording. Fixed  😁
Title: Re: SPD-300-AC on an Ecogen Generator
Post by: schroew on June 01, 2022, 12:01:06 AM
Thank you!!