Aux 1 (Fan) Doesn't Work - Any Suggestions on What I'm Doing Wrong?

Started by mjp24coho, July 29, 2014, 09:09:31 PM

Previous topic - Next topic

mjp24coho

I'm hoping some of you that have experience with the Classic Aux ports can help me.  I have (2) Classic 200's (Follow Me), and I also have a Zephyr vent fan that I use to vent my battery box (24V battery bank).  I have the fan (12V) wired to Aux 1 on my primary Classic, and the Classic is set to turn the fan on when the batteries are over a certain voltage.  When it gets over that voltage, the Classic displays that Aux 1 is "on", but the problem is, my fan doesn't run.  To make sure the fan itself is good, I wired it directly to a 12V battery, and it works fine.  I tried turning my Classic Aux 1 to "On", but the fan still doesn't kick on. I even ran a separate wire from the Aux 1 ports and hooked that up to a voltmeter (when the Aux 1 was set to "On"), and I get no voltage reading.  At first I was concerned that something was wrong with the Aux port on my Classic, but I tried each of the above steps on my second Classic and got the same results.  Surely there must be something I'm missing here.  Can anyone help?  I'm trying to get this resolved ASAP, as it is set up at my remote cabin and I'm leaving tomorrow.

Thanks,
Mike

dgd

Hi,
Unless I misunderstand it appears you are trying to power the fan from AUX1
This won't work as AUX1 likely cannot provide enough current to drive the fan.
I seem to remember it can provide 12v at about 200ma, thats under 3watts  :D

You need to use AUX1 to control a power relay, eg ssr, that switches power to the fan

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

mjp24coho

I thought I had read that the Classic could power the small Zephyr vent fans.  Regardless, if it could power 3W at 12V, wouldn't I at least get a 12V reading when connecting two wires to Aux 1 when it is on?

dgd

I'm not sure about direct powering zephyr fans, someone from MN would need to confirm this.
The reason you do not see any voltage is because the fan is like a low value resistance and its pulling the voltage down to zero. A higher resistance lower wattage fan such as one of those CPU types would probably work ok.
When you turn on AUX1 use a voltmeter connected to the aux1 outputs to check voltage with nothing else connected to aux1
dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

mjp24coho

Nevermind!  I should have read the manual first.  You can switch Aux 1 between acting as either a relay or 12V output.  I didn't change the jumpers to have it act as a 12V output.  I switched the jumpers, and now it is powering the vent fan just fine.

Halfcrazy

Glad to hear you got it. Those jumpers are the normal culprit. And yes the Classic will power a 12v Zephyr fan great off the Aux direct
Changing the way wind turbines operate one smoke filled box at a time