Auto EQ day counter stuck at 0

Started by SolarMusher, April 09, 2016, 09:43:07 AM

Previous topic - Next topic

SolarMusher

Hi all,
Second auto EQ here on Classic:
First one was set to retry for 3 days and was still EQ'ing on the fourth day.
Yesterday, for test purpose, Classic auto was set to EQ for just one day and is still Eq'ing today with day counter stuck at 0 day.
In both cases, it has never reached EQ voltage because it was too cloudly.
Is there something that I don't understand with auto EQ or it just doesn't work as it should?
Thanks,
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

ClassicCrazy

Which firmware version do you have  ?

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

SolarMusher

#2
I'm on the last one, FW2079.
Is it working for you? Does your classic stop eq'ing after the number of days you've set?
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

ClassicCrazy

I know there were bugs in the past for Equalizing but they were fixed in firmware updates.
So you are saying that on your system it seems like the Retry days is being ignored  if it doesn't reach the EQ setpoint for the EQ hours timer ?  Have you tested to see if  it comes out of Equalize if it reaches the EQ setpoint and hours  ?

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

SolarMusher

Quote from: ClassicCrazy on April 09, 2016, 06:34:34 PM
I know there were bugs in the past for Equalizing but they were fixed in firmware updates.
So you are saying that on your system it seems like the Retry days is being ignored  if it doesn't reach the EQ setpoint for the EQ hours timer ?  Have you tested to see if  it comes out of Equalize if it reaches the EQ setpoint and hours  ?

Larry
Ok so I'm not lucky, on mine Retry days seems to be ignored each time that it starts and can't reach the EQ voltage when cloudly.
I will check it next time as I would like to be sure that it really stops after voltage and time has been reached.
But you confirm that it works for you?
Thanks Larry
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

ClassicCrazy

Yes - I believe my auto equalization has been working. I did a new firmware update recently and not sure if that starts the counter over again so might be 30 days before I can check it again. But looking back on MyMidnite history online it looked like the last equalization was all okay and normal.

Larry