Hi,
I'm using skip days this summer to be able to discharge my bank a bit deeper. Actually, with skip day set to 1 the Classic tries to charge  from bulk every two days and will stay in float voltage no matter if the first day was cloudly and that it wasn't able to fully absorb the bank. Wouldn't it be better to change this logic and to force a new bulk charge if the previous bulk/absorb charge wasn't complete for any reasons?
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

boB


Erik, could you maybe use the Re-Bulk voltage to accomplish something similar ?

Sometime not too long ago we changed the software so that Re-Bulk would happen
weather or not the Classic was below Float voltage or not for at least 90 seconds.

boB