Battery AH menu missing?

Started by BAndrews, September 17, 2016, 04:41:52 PM

Previous topic - Next topic

BAndrews

At one time I was going thru the menus of the classic 150 and found an adjustable entry for battery AH size and efficiency.  Around a month or so ago, I upgraded the Classic bios.  Now, I can't seem to locate the Battery AH menu item.

I cracked open the 2056 manual and have not found these menu entries (page 85) although the manual does touch on setting the battery pack AH and efficiency on page 76.  The vulcan-mind-meld was employed and I was not able to locate the fugitive menu items. 

Any ideas where I can find these settings??


4 Star Solar power center w/4KW Magnum inverter, (2) Midnite Solar Classic 150,  3.5 KW PV [(eight) Solarworld 265W, (4) Solarword 345W],  S550 (24 volt) Rolls Surrette battery bank.

Westbranch

when doing an upgrade you have to wait for the computer to close the "DOS Command window'',  What Version of WinDoze are you using?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

BAndrews

I used Win 7.

I don't recall any problems with the upgrade and everything appears present except for these two menu items.  Where should these items be?
4 Star Solar power center w/4KW Magnum inverter, (2) Midnite Solar Classic 150,  3.5 KW PV [(eight) Solarworld 265W, (4) Solarword 345W],  S550 (24 volt) Rolls Surrette battery bank.

Westbranch

In the local App they are in CONFIGURE / ADVANCED part way down the page after Temp Compensation.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

BAndrews

These entries don't show up anywhere in the MNGP?
4 Star Solar power center w/4KW Magnum inverter, (2) Midnite Solar Classic 150,  3.5 KW PV [(eight) Solarworld 265W, (4) Solarword 345W],  S550 (24 volt) Rolls Surrette battery bank.

Vic

Hello BAndrews,

Here is a Link to the WBjr installation & Setup Manual:
http://www.midnitesolar.com/documents.php?productCat_ID=43&productCatName=Charge+Controllers+-+KID&model=MNWBJR&product_ID=519&act=

Click on the first Link,  unless you need the German version.

Be certain that you have selected the WBjr in the Aux 2 Setup.

From the Main Status page on the MNGP,  press the Status page navigation button three times,  on the lower right of this page,  press the right Soft Button,  for "  Setup  ",  this should allow the Ah Capacity of your battery to be set.

Aux 2 = WBjr may be the thing that enables additional WBjr setup ...  dunno,  have not tried setting up a WBjr without a WB,  or without first setting Aux 2 = WBjr.

FWIW,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

BAndrews

Quote from: Vic on September 17, 2016, 07:20:56 PM
Hello BAndrews,

Here is a Link to the WBjr installation & Setup Manual:
http://www.midnitesolar.com/documents.php?productCat_ID=43&productCatName=Charge+Controllers+-+KID&model=MNWBJR&product_ID=519&act=

Click on the first Link,  unless you need the German version.

Be certain that you have selected the WBjr in the Aux 2 Setup.

From the Main Status page on the MNGP,  press the Status page navigation button three times,  on the lower right of this page,  press the right Soft Button,  for "  Setup  ",  this should allow the Ah Capacity of your battery to be set.

Aux 2 = WBjr may be the thing that enables additional WBjr setup ...  dunno,  have not tried setting up a WBjr without a WB,  or without first setting Aux 2 = WBjr.

FWIW,   Vic



Thanks Vic -- I'll check tomorrow when I make my daily journey to the solar shack.  I just installed a WBJr a few weeks ago ......


4 Star Solar power center w/4KW Magnum inverter, (2) Midnite Solar Classic 150,  3.5 KW PV [(eight) Solarworld 265W, (4) Solarword 345W],  S550 (24 volt) Rolls Surrette battery bank.

Westbranch

B Andrews, were you getting WBjr data before, or was the FW version too old to work with the WBjr?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

ClassicCrazy

Easy way to fill out all the setpoints - including the Whizbang ones you are looking for is with the Local Status App. You can also save them with that and easily restore them after a firmware update.

I just was looking for them on MNGP - took me awhile but I remembered where they are now
Make sure Whizbang is setup on AUX2 and using shunt
Then use Status button to scroll through until you get to
Whizbang Junior Shunt
press right arrow under SETUP
You will see the things you are looking for to set up there

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

BAndrews

Quote from: Vic on September 17, 2016, 07:20:56 PM
Hello BAndrews,

Here is a Link to the WBjr installation & Setup Manual:


That did it.  got into the WBJr menu and reset from 400 AH to 856 AH.
4 Star Solar power center w/4KW Magnum inverter, (2) Midnite Solar Classic 150,  3.5 KW PV [(eight) Solarworld 265W, (4) Solarword 345W],  S550 (24 volt) Rolls Surrette battery bank.

BAndrews

Quote from: Westbranch on September 17, 2016, 07:56:26 PM
B Andrews, were you getting WBjr data before, or was the FW version too old to work with the WBjr?


I upgraded the eprom so I could use the graphical software.   I installed a WBJr a few weeks later IIRC.  After the WBJr install, I was getting SOC readings on the MNGP (lower right hand).  I thought I had seen the amp-hour settings in the normal menu prior to installing the WBJr.


4 Star Solar power center w/4KW Magnum inverter, (2) Midnite Solar Classic 150,  3.5 KW PV [(eight) Solarworld 265W, (4) Solarword 345W],  S550 (24 volt) Rolls Surrette battery bank.

BAndrews

Quote from: ClassicCrazy on September 17, 2016, 09:18:44 PM
Easy way to fill out all the setpoints - including the Whizbang ones you are looking for is with the Local Status App. You can also save them with that and easily restore them after a firmware update.

I just was looking for them on MNGP - took me awhile but I remembered where they are now
Make sure Whizbang is setup on AUX2 and using shunt
Then use Status button to scroll through until you get to
Whizbang Junior Shunt
press right arrow under SETUP
You will see the things you are looking for to set up there

Larry


Thanks Larry. 
4 Star Solar power center w/4KW Magnum inverter, (2) Midnite Solar Classic 150,  3.5 KW PV [(eight) Solarworld 265W, (4) Solarword 345W],  S550 (24 volt) Rolls Surrette battery bank.