Is this the right solution for me?

Started by skyking, January 28, 2025, 11:13:34 PM

Previous topic - Next topic

skyking

I have some questions and concerns and want to get it right the first time if at all possible.
This unit will accept up to 15Kw of solar input at up to 600VDC
It will make 10KW of AC with it?
On a peak production day, the surplus 5Kw is only going to charge batteries, other DC loads?
If I have that right, then if I go much above 12Kw of panel I would best be doing some self consuming from the battery bank to take full advantage?
I will eventually be on the grid here with a net metering agreement.
Initially I want to run standalone off the grid with one or two of the PowerFlo 16s.
If I need more PV capacity my plan is to add some microinverter strings to make more capacity for the grid tie action.
This unit will readily handle my backup needs in the event of a power outage. The smart load breakers are handy for that.

ClassicCrazy

 I think that inverter has ability to be able to turn extra loads on and off at whatever you program that for , so to use up extra  pv power you just turn on an AC load of some sort. But I don't have one of those inverters and haven't studied the manual.
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

skyking

Thanks Larry. this new house is big and I suspect that 12~13KW of panels is not going to wipe out my annual power usage. That is why I want to understand it properly.
I don't see a need to run paralell units, just have the means of adding some direct grid tie to fill the gap.