Best practice

Started by Dgrblu, April 11, 2024, 09:55:36 AM

Previous topic - Next topic

Dgrblu

Greetings all,

This forum is full of people that are a whole lot smarter than I so I'm here for guidance.

The system. Off grid. Two 48v battery banks of eight 6v agm, 424ah in series with the banks wired in parallel. Two classic 150's, both with wizbang's. Two, Magnum ms4448pae operating in master/slave configuration with one BMS.

I have purchased a Generac 20k HSB propane fired generator and am wondering how others or the best practice would be to configure the auto start/Stop of the generator.

 I was thinking that I could use the SOC of the Classic 150 through the aux 1 contact to initiate the transfer switch at a SOC of 60%. To terminate the generator,  I was thinking of using the Magnum Absorb time termination,  2.5 hrs to switch back to solar charging.

Wondering if this doable. Will I need a piece of Magnum hardware or other piece of hardware to accomplish my task? How are others doing this? I'm wanting to have a KISS approach for this function of the system.

TIA,
Bruce

4.4 Kw Off Grid system
6 strings of 3 panels (825w/string)
Midnite combiner
Classic 150
Magnum PAE sine inverter
Magnum distribution panel, expandable.

boB

Hi Bruce.

As long as the Classic's aux output turns on and off according to the minimum and maximum SOC%, it should be able to start and stop the generator.  It is only one wire though.  On or Off.  It can also turn its aux off and on by battery voltage. 

Are you using lithium or lead acid batteries ?

I don't know about that Generac but I would think it works like you want.  Maybe it even has some warm up and cool down smarts built in ?

Best practices should say there is a warm up period for the generator and a cool down time for the generator.  There will be some amount of warm up time (seconds ?) before the Magnum starts to charge.

Someone else here may have some more insight and experience with this particular setup.

boB
K7IQ 🌛  He/She/Me

LilMT

Personally, I use the Magnum AGS along with their BMK.  You can then program the AGS very easily to perform a gen warmup run a programmed cycle, gen cooldown, and shut off.  You can program it easily and it is pretty intuitive.  Lots of option for basic start run stop based on SOC, or Bat voltage, quiet hours, run exercise cycles etc.

I have mine set to start at a specific voltage - runs it cycle until float, float for a bit and then shutdown.

I also have a safety on cycle programmed so that it will auto start and run a cycle if my SOC gets below 60%

I use that for when I am getting enough sun that I am getting a higher bat voltage but my SOC is still dropping.

Just one way of doing it, but I would recommend some kind of setup that allows for warmup and cooldown.

Slamming dirty startup gen voltage into the inverter is not real good.  And neither is power off a gen while under load.

Of course, all of that is my humble opinion.  :)

Hope you get it figured out and let us know what you came up with.  If you have any questions, let us know.
Thanks,
LilMT

Classic 250, 3s2p Trina Solar 405watt, 8 Renogy 200ah for 48V 400ah, Magnasine 4448 inverter.

boB


Thank you LilMT.  I was going to suggest the Magnum AGS but I did not know if it was still available.

There are other third party AGS management systems available or at least there used to be.

Here is the Magnum one.  Gary, who works with us now designed this many years ago and is proven to work great.

https://www.amazon.com/Magnum-Energy-Automatic-Network-ME-AGS-N/dp/B00A6XGLKO

But The aux output should work temporarily at least until a better method is chosen.

boB

K7IQ 🌛  He/She/Me

Rob Linschoten

The Magnum AGS is still available and we use one all winter. One useful aspect to that AGS is the ability to add external on/off control to it to overrride the auto programming.

In our case we have added a WiFi controlled override switch to start stop with a phone app when away from home. It triggers the Magnum's warmup and cooldown cycle as per normal. Graham's Android app keeps us informed.

In absolute repudiation of the KISS principle I tried to include the aux output of my master CC so that when I reached 98% SOC (using the WBjr)it would initiate a shutdown in series with the on/off overide.  It does do that but I have not figured out how to keep it from restarting when the SOC drops...trying not to buy the Magnum BMK.
7.8kW PV
3 Classic150, 1 WBjR shunt, 1 Classic200, 1 Classic250 for hydro
1 Outback FX3524 for domestic power (240VAC via transformer)
1 Magnum 4024PAE for shop power with phone/auto gen start
8 Switch SWE6-420 (4S-2P) for 840AH@20H-Lead Carbon

Rob Linschoten

And the correct answer is:

Remember to set the low SOC setting well below any normal usage situation, like 30%.
So it is now 99% SOC off (can't set it to to 100%) and 30% SOC on, with remote Ewelink phone app/WiFi switch override.

On to the next conundrum....
7.8kW PV
3 Classic150, 1 WBjR shunt, 1 Classic200, 1 Classic250 for hydro
1 Outback FX3524 for domestic power (240VAC via transformer)
1 Magnum 4024PAE for shop power with phone/auto gen start
8 Switch SWE6-420 (4S-2P) for 840AH@20H-Lead Carbon

qcda1

Quote from: Rob Linschoten on April 18, 2024, 03:46:03 PMThe Magnum AGS is still available and we use one all winter. One useful aspect to that AGS is the ability to add external on/off control to it to overrride the auto programming.

In our case we have added a WiFi controlled override switch to start stop with a phone app when away from home. It triggers the Magnum's warmup and cooldown cycle as per normal. Graham's Android app keeps us informed.

In absolute repudiation of the KISS principle I tried to include the aux output of my master CC so that when I reached 98% SOC (using the WBjr)it would initiate a shutdown in series with the on/off overide.  It does do that but I have not figured out how to keep it from restarting when the SOC drops...trying not to buy the Magnum BMK.


Hello! Would it be possible to share the way you set up your "external on/off control to it to overrride the auto programming" on the ME-AGS-N? Have you just a relay switch in parallel to the AGS's outputs?

Thanks and best regards,

Daniel.
1,2kW on tracker, 1,4kW fixed, 2xMidnite Classic150, Magnum MS4448PAE, 4xMapleLeaf + 1 RUiXU 48VDC/100Ah LiFePO4 and Kohler 14RCA with homegrown monitoring/alerting system + HA.

Rob Linschoten

Just noticed your post....

The master Midnite controller uses the dry contacts on Aux 1 in SERIES with the Ewelink WiFi switch. The two switches in series are connected to the external 2 wire override terminal of the AGS-N. Therefore all the internal settings of the AGs are still operational. You have to buy a custom dongle from Magnum to enable the external function. It is meant for an external thermostat but works fine in this application. I can override the SOC setting remotely via the LocalApp. This arrangement does require a calibrated Midnite smart shunt.

Hope this helps.
7.8kW PV
3 Classic150, 1 WBjR shunt, 1 Classic200, 1 Classic250 for hydro
1 Outback FX3524 for domestic power (240VAC via transformer)
1 Magnum 4024PAE for shop power with phone/auto gen start
8 Switch SWE6-420 (4S-2P) for 840AH@20H-Lead Carbon

qcda1

Than you for your reply. From your original post, I looked again at the documentation and found the trick using the ME-PT1 or ME-PT2 connector (dongle) to the ME-AGS-N. Actually it uses the « temperature » driven option of the AGS and allow an external relay to start/stop the generator. And yes, I could use the Midnite Classic AUX output to drive it as I have the WbJr battery monitor. I still went on the route of using my monitor program that collect the SOC from the Classic, the BMK and my battery's BMS. Here is the link to the thing in the works. I'll add the idea of using the AUX of the Classic as well.
Note also that it is not obvious to find the ME-PT2, get it on eBay. Most of advertised suppliers in the search result show them as « unavailable »...

https://github.com/qcda1/MagAGS

Best regards,

Daniel.
1,2kW on tracker, 1,4kW fixed, 2xMidnite Classic150, Magnum MS4448PAE, 4xMapleLeaf + 1 RUiXU 48VDC/100Ah LiFePO4 and Kohler 14RCA with homegrown monitoring/alerting system + HA.