42Vdc battery system

Started by SolarMusher, February 15, 2016, 05:28:58 PM

Previous topic - Next topic

SolarMusher

Hi all,
Does it matter for the Classic to be set for a 48V system with 42V battery settings?
One of my batteries goes dead today and I would like trying it in two strings x7 batteries for a 42Vdc system.
Bank was 2x 415Ah before and right now I'm using one string only and might be short on capacity, the time for a new bank to come.
Thanks for any input,
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

mike90045

as long as you set the voltages (Float, abs, Eq) to what you want, it should be fine - EXCEPT the temp comp will be a bit high thinking that there are 3  extra cells
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

dRdoS7

Hi,

Quote from: SolarMusher on February 15, 2016, 05:28:58 PM
Hi all,
Does it matter for the Classic to be set for a 48V system with 42V battery settings?
One of my batteries goes dead today and I would like trying it in two strings x7 batteries for a 42Vdc system.
Bank was 2x 415Ah before and right now I'm using one string only and might be short on capacity, the time for a new bank to come.
Thanks for any input,
Erik

Is there another device that will be charging the batteries? Can it charge to 42V?

What runs off the batteries? An inverter? Will 42v be OK?

dRdoS7

SolarMusher

My old Magnum 4448AE should be ok, voltage range is 36V to 67V. Outback is another story, Outback's manual is only talking about 42 to 68V for the vfx3648. The Magnum is my main inverter but I need the vfx to supply septic pumps and wire heater. I only use the Magnum for charging because of the gen that is 30A/240Vac, a bit low to power both chargers and loads.
Mike,  I believe temp comp could be set for 21 cells in the classic, right?
Main problem seems to be the Outback with its 42Vdc limit. Anyway, if another batterie goes dead suddenly on one string, I would still have spare batteries to keep the lights on.
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

mike90045

Quote from: SolarMusher on February 16, 2016, 07:31:07 AM...Mike,  I believe temp comp could be set for 21 cells in the classic, right?...

It's set by the battery voltage setting, which assumes 2V per cell, 12V gives you 6 cells.  And the temp comp is in 5mV increments, so you can only get close, not right on
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Vic

Quote from: mike90045 on February 16, 2016, 06:28:32 PM
Quote from: SolarMusher on February 16, 2016, 07:31:07 AM...Mike,  I believe temp comp could be set for 21 cells in the classic, right?...

It's set by the battery voltage setting, which assumes 2V per cell, 12V gives you 6 cells.  And the temp comp is in 5mV increments, so you can only get close, not right on

The Classics here have Temp Comp that can be set in 0.5 mV increments  --  500 microvolt steps up or down.

And,  YES,  the Classic knows the number of cells by the nominal battery voltage setting.

FWIW,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

SolarMusher

#6
Ok, but if it was set for 0.45mV with 21 cells, compensation should be "about" the same than for a real 0.5 mV x 24 cells.
Anyway, I'm afraid of a low disconnect voltage that would be too high for the Outback Vfx maximum lower 42V voltage limit when under loads. I would need to set the LBCO at 42.5V and that would be pretty high for a 42Vdc system, something around 75% SOC (+/- 200 amps at 42Vdc for a 830Ah bank capacity), not sure that it would worth it versus a single 415Ah/48Vdc string with a 40/50% DOD.
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

boB

I was going to say to set the Classic for 36V or 48V system and adjust the temp-comp -0.5 mV per degree C per cell appropriately but looks like Vic beat me to it !