Dead Classic?

Started by phxmark, January 08, 2016, 11:25:40 PM

Previous topic - Next topic

phxmark

I just had a Classic do something strange. The network switch it was plugged into failed. When I plugged the network cable into the new switch, the Classic restarted and now is stuck on 52.7V overvoltage on a 24v system.  The Input Voltage is stuck at 111V whether the solar is on or off.  It is nighttime right now. I have tried rebooting the classic and I have checked all the connections.

Any ideas what could be wrong?

I searched the forums and could not find anything with overvoltage on solar.

Is the Classic blown?

Here is the register export:

16385,65535,app_version,65535,
16386,65535,net_version,65535,
16387,1923,app_rev,1923,
16388,0,,
16389,1839,net_rev,1839,
16390,0,,

4101,1224,UNIT_ID,1224,
4102,2014,UNIT_SW_DATE,18.12.2014,
4103,3090,,
4104,13,InfoFlagsBits3,13,
4105,0,,
4106,19143,UNIT_MAC_Address,60:1D:0F:00:4A:C7,
4107,3840,,
4108,24605,,
4109,1,UNIT_IP_Address,0.0.0.1,
4110,0,,
4111,35718,UNIT_Device_ID,-289502330,
4112,61118,,
4113,40960,,
4114,1999,RestartTimerms,1999,
4115,576,Battery Voltage,57.6,
4116,1117,Input Voltage,111.7,
4117,0,Output Current,0,
4118,0,kWh,0,
4119,0,Watts,0,
4120,2304,Charge Stage,9,
4121,0,Input Current,0,
4122,1116,LastVoc,111.6,
4123,1881,,188.1,
4124,0,MatchPointShadow,0,
4125,0,Amp Hours,0,
4126,33183,Total kWh,3318.3,
4127,0,,
4128,57002,Total Amp Hours,122538,
4129,1,,
4130,12288,InfoFlagsBits1,12288,
4131,45568,InfoFlagsBits2,45568,
4132,246,Battery Temperature,24.6,
4133,272,FET Temperature,27.2,
4134,354,PCB Temperature,35.4,
4135,0,NiteMinutesNoPwr,0,
4136,300,,
4137,502,ModbusTCPPort,502,
4138,1,TimeMinutesFloatToday,1,
4139,7183,AbsorbTime,7183,
4140,0,DaysSinceLastFloat,0,
4141,50,PWM,50,
4142,4,SunRiseTodayMsrd,4,
4143,3600,Equalize Time,3600,
4144,0,,
4145,1,,
4146,0,USB Comm Mode,0,
4147,0,NoDoubleClickTimer,0,
4148,780,Battery output Current Limit,78,
4149,294,Absorb Set Point Voltage,29.4,
4150,278,Float Voltage Set Point,27.8,
4151,296,Equalize Voltage Set Point,29.6,
4152,780,Sliding Current Limit,780,
4153,0,Minimum Absorb Time,0,
4154,7200,Maximum Absorb Time,7200,
4155,296,Maximum Battery Temperature Compensation Voltage,29.6,
4156,274,Minimum Battery Temperature Compensation Voltage,27.4,
4157,50,Battery Temp Comp Value for each 2V cell,50,
4158,0,Battery Type,0,
4159,0,Equalize Retry Days,0,
4160,0,Force Flag Bits,0,
4161,0,,
4162,3600,Equalize Time,3600,
4163,0,Equalize Interval Days,0,
4164,10,Mppt Mode,10,
4165,20993,Aux 1 and 2 Function,20993,
4166,293,Aux1VoltsLoAbs,29.3,
4167,1,Aux1DelayT,1,
4168,3000,Aux1HoldT,3000,
4169,1,Aux2PwmVwidth,1,
4170,0,,
4171,0,,
4172,296,Aux1VoltsHiAbs,29.6,
4173,900,Aux2VoltsHiAbs,90,
4174,65516,Aux1VoltsLoRel,-2,
4175,10,Aux1VoltsHiRel,1,
4176,65516,Aux2VoltsLoRel,-2,
4177,50,Aux2VoltsHiRel,5,
4178,587,Aux1VoltsLoPv,58.7,
4179,660,Aux1VoltsHiPv,66,
4180,357,,
4181,1400,Aux2VoltsHiPv,140,
4182,24576,FanSpeed1PwmCompare,24576,
4183,202,ArcFaultSenstvty,202,
4184,95,,
4185,0,,
4186,23244,Enable Flags 2,23244,
4187,64,Enable Flags 1,64,
4188,0,PWM Offset,0,
4189,0,Vbatt Offset,0,
4190,0,Vpv Offset,0,
4191,1116,VpvTargetRd,1116,
4192,1350,VpvTargetWr,135,
4193,0,VbattGainAdj,0,
4194,0,VpvGainAdj,0,
4195,0,IbattGainAdj,0,
4196,0,IpvGainAdj,0,
4197,4,LgcySweepIntervalSecs,4,
4198,100,MinSwpVoltage,10,
4199,990,MaxSwpVocPercentage,99,
4200,8,SweepDepth,8,
4201,8,PrePwmConnectOffsetAdjSS,8,
4202,776,ClipperMaxVoltage,776,
4203,0,WindNumberOfPoles,0,
4204,8,MppPercentVoc,8,
4205,0,WindTableToUse,0,
4206,0,WindTableLearn,0,
4207,3,LED Mode,3,
4208,1117,,
4209,0,,
4210,12851,Unit Name,32141,
4211,13361,,
4212,49,,
4213,0,,
4214,4882,CTIME0,68490002,
4215,1045,,
4216,264,CTIME1,132120840,
4217,2016,,
4218,111,CTIME2,111,
4219,0,BaudRateStopStartEtc,0,
4220,0,RemoteMenuMode,0,
4221,0,RemoteButtons,0,
4222,0,VbatOvrshootSenstvty,0,
4223,0,VpvStartupDeltaSS,0,
4224,1116,PreVoc,1116,
4225,0,Vt2PwmDiff,0,
4226,0,VauxA2Dinput,0,
4227,1,,
4228,1,,
4229,0,,
4230,1116,,
4231,1116,VocRD,1116,
4232,0,,
4233,1117,,
4234,16,,
4235,0,,
4236,7182,AbsorbTime,7182,
4237,50,AntiClickSenstvty,50,
4238,131,SiestaTime,131,
4239,20,SiestaAbortVocAdj,20,
4240,8320,flagsRD,8320,
4241,0,,
4242,0,,
4243,240,,
4244,291,VbattRegSetPTmpComp,291,
4245,24,VbattNominal,24,
4246,12,EndingAmps,1.2,
4247,5,EndingSoc,5,
4248,200,BattCapacityAhrs,200,
4249,262,RebulkVolts,26.2,
4250,88,BattAhrEfficiency,88,
4251,0,BattMonSOC,0,
4252,3,BattMonAmps,3,
4253,0,BattMonAHefficiency,0,
4254,0,,
4255,0,,
4256,0,,
4257,0,RebulkTimerSec,123273216,
4258,1881,,
4259,2,,
4260,0,,
4261,295,,
4262,1,,
4263,41,,
4264,0,Voc_Qualify_Timer_1ms,0,
4265,0,,
4266,0,MinVpvTurnOn,29.3,
4267,41,,
4268,41,,
4269,0,,
4270,0,,
4271,25000,,
4272,41,RestartTimerms,41,
4273,0,Ibatt,0,
4274,224,,
4275,36,ReasonForResting,36,
4276,578,Output Vbatt,57.8,
4277,1116,,
4278,200,Typeint,200,
4279,0,,
4280,75,MinLogZeroNdx,75,
4281,0,LogValueRead,0,
4282,0,PkHoldVdTcapVpvStamp,0,
4283,1118,VpvTargetRd,1118,
4284,0,SwpDeepTimeoutSec,0,
4285,0,TESTSHORT3,0,
4286,20,LowWatts,20,
4287,50,WindLowWatts,50,
4288,17,WindWindowWattsRef,17,
4289,57536,WindowWattsRO,57536,
4290,90,WindTimeOutRef,90,
4291,1800,WindTimeOut2Ref,1800,
4292,0,WindTimeOut,0,
4293,0,WindTimeOut2,0,
4294,750,MinVpvTurnOn,750,
4295,0,VpvB4TurnOff,0,
4296,65474,HydroSwpAmps10Time6,65474,
4297,0,EndingAmpsTimerSec,0,
4298,970,PkAmpsOverLimitHi,970,
4299,850,PkAmpsOverLimitLo,850,
4300,4,FactoryVbattOffset,4,
4301,23386,WindPowerTableV+0,23386,
4302,24156,WindPowerTableV+1,24156,
4303,25184,WindPowerTableV+2,25184,
4304,26212,WindPowerTableV+3,1717829832,
4305,27240,WindPowerTableV+4,27240,
4306,28268,WindPowerTableV+5,28268,
4307,29296,WindPowerTableV+6,29296,
4308,30836,WindPowerTableV+7,30836,
4309,512,WindPowerTableI+0,512,
4310,1796,WindPowerTableI+1,1796,
4311,3338,WindPowerTableI+2,3338,
4312,5393,WindPowerTableI+3,5393,
4313,7705,WindPowerTableI+4,7705,
4314,10275,WindPowerTableI+5,10275,
4315,12589,WindPowerTableI+6,12589,
4316,15159,WindPowerTableI+7,15159,
4317,0,UNIT_Reserved,0,
4318,1297,PkAmpsOverTrip,1297,
4319,0,UNIT_Reserved,0,
4320,0,mnlp_revision,0,
4321,0,ReadRamAddress,0,
4322,0,,
4323,0,ReadRamDataRO,0,
4324,0,,
4325,0,UNIT_Reserved,0,
4326,10,ClassicModbusAddr,10,
4327,32768,BatteryTempPassedT,32768,
4328,128,iFlagsRO,65664,
4329,1,,
4330,0,ModbusControl,0,
4331,0,ClassicFmePassedBits,0,
4332,0,WindSynchA,0,
4333,0,WindSynchV,0,
4334,0,FollowMePassRefS,0,
4335,0,SchedTimer03,0,
4336,0,SchedTimer04,0,
4337,100,SchedTimer05,100,
4338,1000,SchedTimer06,1000,
4339,32669,SchedTimer07,32669,
4340,64,SchedTimer08,64,
4341,10261,DabtU32Debug01,672484381,
4342,19485,,
4343,52156,DabtU32Debug02,-876852030,
4344,19650,,
4345,41296,DabtU32Debug03,-1588552380,
4346,40260,,
4347,41296,DabtU32Debug04,-1588552380,
4348,40260,,
4349,132,SchedTimer17,132,
4350,0,SchedTimer18,0,
4351,0,SchedTimer19,0,
4352,40106,SchedTimer20,40106,
4353,63037,SchedTimer21,63037,
4354,0,SchedTimer22,0,
4355,0,SchedTimer23,0,
4356,43,,
4357,65333,,
4358,19705,,
4359,134,,
4360,134,,
4361,53,,
4362,65529,,
4363,0,,
4364,0,,
4365,31294,WbJr AH(+),31294,
4366,0,,
4367,32790,WbJr AH (-),-32746,
4368,65535,,
4369,1,WbJr AH (net),1,
4370,0,,
4371,8,WbJr Amps,0.8,
4372,34380,WizBangJrRawCrcAndtemp,34380,
4373,99,WBJr SOC,99,
4374,696,WbJrAmpHourChrg,696,
4375,0,WbJrAmpHourChrgadj,0,
4376,1,WbJrAmpHourDisChrgadj,1,
4377,232,WbJr AH Remaing,232,
4378,28323,WbJrAmpHourDisChrg,28323,
4379,190,BatCapacityTrefMBus,19,
4380,30,WbJrBatAhrCompPcntMBus,3,
4381,233,UNIT_Reserved,233,
4382,56,UNIT_Reserved,56,
4383,0,UNIT_Reserved,0,
4384,0,UNIT_Reserved,0,
4385,0,UNIT_Reserved,0,
4386,0,UNIT_Reserved,0,
4387,0,DabtU32Debug05,0,
4388,0,,

20481,2,settings,2,
20482,43200,IP Address,192.168.0.55,
20483,14080,,
20484,43200,Gateway Address,192.168.0.1,
20485,256,,
20486,65535,Subnet,255.255.255.0,
20487,255,,
20488,43200,Primary DNS,192.168.0.1,
20489,256,,
20490,0,Secondary DNS,0.0.0.0,
20491,0,,



Magnum MS-4448PAE
Midnite Solar Classic 200
6 SunPower E20 327W Panels.  3 Strings/2 Panels each
4 200ah AGM Batteries
WhizBang Jr.
Sun-500G Grid-Tie Inverter Controlled
by Aux 1 using a SSR
Emerson/ASCO 185 100 Amp Automatic Transfer Switch
http://midniteforum.com/index.php?topic=1564.0

Westbranch

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

phxmark

Quote from: Westbranch on January 09, 2016, 12:33:45 AM
see the last post...

http://kb1uas.com/mnsforum/index.php?action=search2

hth

PS search "36" or "RFR 36"

RFR is 22 which seems to point to battery overvoltage. The Classic is reporting 57 v on a 24 v system. Volt meter is reporting 28v.  With it being dark, classic is reporting over 100v on the solar input and the volt meter reports 44v. It usually reports anywhere from 22 to 70 v when it is dark. I am guessing that when I plugged the Classic into the replacement network switch, something "shocked" the Classic logic board causing the reboot and the subsequent bad readings.

Time for a new Classic it would seem.
Magnum MS-4448PAE
Midnite Solar Classic 200
6 SunPower E20 327W Panels.  3 Strings/2 Panels each
4 200ah AGM Batteries
WhizBang Jr.
Sun-500G Grid-Tie Inverter Controlled
by Aux 1 using a SSR
Emerson/ASCO 185 100 Amp Automatic Transfer Switch
http://midniteforum.com/index.php?topic=1564.0

Halfcrazy

I had one do this after a network anomaly. I let it set off for 45 minutes and it went away. Try that and if not let me know (ryan@midnitesolar.com) I will issue an RMA
Changing the way wind turbines operate one smoke filled box at a time

phxmark

Quote from: Halfcrazy on January 09, 2016, 06:05:52 AM
I had one do this after a network anomaly. I let it set off for 45 minutes and it went away. Try that and if not let me know (ryan@midnitesolar.com) I will issue an RMA

It has been off all night long. This morning I turned it on, battery voltage at 57V, Solar reads 158V.  It seems it is reading about 30V high on the battery side and about 90v high on the solar side.


Magnum MS-4448PAE
Midnite Solar Classic 200
6 SunPower E20 327W Panels.  3 Strings/2 Panels each
4 200ah AGM Batteries
WhizBang Jr.
Sun-500G Grid-Tie Inverter Controlled
by Aux 1 using a SSR
Emerson/ASCO 185 100 Amp Automatic Transfer Switch
http://midniteforum.com/index.php?topic=1564.0

zoneblue

Id be inclined to try a VMM, to reset the registers to factory defaults. Just in case some odd packets spewed out of the thing in its dying breath.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

phxmark

Quote from: zoneblue on January 09, 2016, 10:12:12 PM
Id be inclined to try a VMM, to reset the registers to factory defaults. Just in case some odd packets spewed out of the thing in its dying breath.

Did the hardware jumper and soft < > VMM, still no change. I ordered a new one on ebay for $500, will wait for a RMA from Midnite and see how much it is going to cost to repair. Can't be without it for more than a week, that way I will have a spare in case one of the two I own fail again.

Magnum MS-4448PAE
Midnite Solar Classic 200
6 SunPower E20 327W Panels.  3 Strings/2 Panels each
4 200ah AGM Batteries
WhizBang Jr.
Sun-500G Grid-Tie Inverter Controlled
by Aux 1 using a SSR
Emerson/ASCO 185 100 Amp Automatic Transfer Switch
http://midniteforum.com/index.php?topic=1564.0

boB


If there are several readings displaying too high, it is probably a low-ish 3.3V to the processor.

If it is only the battery voltage, it is possibly an open or high value voltage divider resistor.

If the Ethernet switch problem is related then maybe the Ethernet PHY chip inside the Classic
went bad at the same time, taking the 3.3V down a bit and making the readings high.
Except that temperatures read lower I believe and  not higher.

Sounds like this might be a normal warranty covered thing to me.

boB
K7IQ 🌛  He/She/Me

phxmark

Quote from: boB on January 10, 2016, 01:37:16 AM

If there are several readings displaying too high, it is probably a low-ish 3.3V to the processor.

If it is only the battery voltage, it is possibly an open or high value voltage divider resistor.

If the Ethernet switch problem is related then maybe the Ethernet PHY chip inside the Classic
went bad at the same time, taking the 3.3V down a bit and making the readings high.
Except that temperatures read lower I believe and  not higher.

Sounds like this might be a normal warranty covered thing to me.

boB

I was reading that in another thread where it said the 3.3 v line being low would cause bad readings. I didn't verify the temperature readings, though. It is both the solar and battery voltages that are reading high.  Ryan is sending a new unit out Monday with an RMA. I did order a spare to go along with my spare inverter so downtime would be minimal next time.

Thanks a bunch for all the help.
Magnum MS-4448PAE
Midnite Solar Classic 200
6 SunPower E20 327W Panels.  3 Strings/2 Panels each
4 200ah AGM Batteries
WhizBang Jr.
Sun-500G Grid-Tie Inverter Controlled
by Aux 1 using a SSR
Emerson/ASCO 185 100 Amp Automatic Transfer Switch
http://midniteforum.com/index.php?topic=1564.0

phxmark

A BIG THANK YOU to Ryan for getting a new Classic out so quickly to replace the one that failed. New one is in and working like a charm!

Just a bit of history, the old one failed when I plugged it into a new ethernet switch.

I will now power down the classic whenever I must remove the ethernet or USB just to be on the safe side.

Again, Ryan, a BIG THANK YOU!!