Follow me - Bat temp not showing on second CC

Started by Corndog, November 19, 2026, 06:41:57 AM

Previous topic - Next topic

Corndog

Hello- We have added another 5000w array and classic 150. Initial communication cable set up was showing the battery temp on both classics but the blue light flashes were not the same. Main classic longer flash - helper classic quick flash. (I read these should be the same) . Installed two new quality cords, the flashes are now both the same (longer flash) Cords are set to middle port main to bottom port helper and middle helper to bottom of main.

I have Follow me on on the main, Helper- follow me and follow master BTS.

Any help would be appreciated
Our System
Off Grid
2 x Outback Flexware- VFX3648 Inverter
Mate 3
Power Hub 10
Hanwha solar panel 345 watts-- total array 5520 watts
Longi 5000w
Midnite CI150 Charge x 2
13 KW Diesel Gen
48-volt System:
Sixteen x S6 L16-HC (445 AH) batteries, bank capacity of 890 AH @ 48-volts.

Corndog

Problem solved - only one of my cords is a reverse RJ11 (6P4C). I had no idea these existed, Humbled quickly. And humbled again reread the instructions we want the quick blue light flash not the longer  :-\
Our System
Off Grid
2 x Outback Flexware- VFX3648 Inverter
Mate 3
Power Hub 10
Hanwha solar panel 345 watts-- total array 5520 watts
Longi 5000w
Midnite CI150 Charge x 2
13 KW Diesel Gen
48-volt System:
Sixteen x S6 L16-HC (445 AH) batteries, bank capacity of 890 AH @ 48-volts.

ClassicCrazy

I believe in follow me the flashes are different between master and the other one - one is shorter .
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

ClassicCrazy

from the Midnite Knowledge Base ( now only found in Wayback Machine )

Wayback Machine
5 captures
4 Jul 2022 - 17 Jul 2026
May    OCT    Jul
   13    
2024    2025    2026
About this capture

Guest User | Sign In

MidNite Solar Help


Frequently Asked Question
All Categories » CLASSIC CHARGE CONTROLLER - Features and Programming
CLASSIC - F-ME - How to setup Classics in true MASTER/SLAVE Mode
Last Updated 4 years ago

The Follow-Me concept does not embrace Master/Slave topology.  With a few "tweaks" you can have a simple master/slave setup which I find personally works better.  Below I will tell you how it's done and explain how it works. (this may have limited benefits for 2 Classics)

First, we need to pick a Classic to be our MASTER Controller.  It will be called the "BTS MASTER"  Why is this?  Because one of the neat advantages of having F-Me setup is we can use a single BTS (Battery Temperature Sensor) and not need 2 or 3 or 4 or xx sensors and all that extra wire tied up somewhere.  The BTS-NET option in the Classic allows a single BTS to provide data to all Classics.  The BTS-NET is also a easy way to check that the cables are good and the F-Me network is functional.

1 - Pick a BTS MASTER Classic, install the BTS and set it to MASTER in the TWEAKS MENU under BTS-NET (page down to get to the sub-menu)
All other Classics get this set to FOLLOW.  This should be self explanatory to most seasoned Solar Installers & Electricians.

2 - If the Whizbang Jr SHUNT Option is going to be installed, install it in this Classic. This Classic will be the "MASTER of all things". This will be required for ENDAMPS control.

3 - All charging voltages get set the same.  The only thing we set differently is CHARGE TIMES.

4 - Set your needed ABSORB TIME in the MASTER, the rest (SLAVES) get set with that plus 10 minutes.  See, what this does it lets the MASTER decide when to send everyone to FLOAT.  If for some reason F-Me breaks, all that happens is the SLAVES stay in Absorb for an extra 10 minutes.

A GF or Ground Fault seems to only shut down the offending Classic so we should not need to worry about down-stream Classics sending data back around. AF or Arc Fault seems to exhibit the same behavior, at least on my 5 Classic system.

There is a misconception that ABSORB is a F-me function, it is not.  ALL Classics MUST reach their ABSORB voltage independently.  ANY Classic that fails to maintain the programmed Absorb Voltage for 90 seconds with be forced BACK into BULK and this mode will be propagated from this Classic to the last in line. Hopefully this provides enough power to get back into ABSORB.

If using ENDAMPS and REBULK set it up ONLY in the MASTER, let it decide since it has the WhizbangJR (Needed for proper ENDAMPS Operation)  Don't use ENDAMPS unless you have a WBjr installed & setup to use the SHUNT.

I have removed the Follow-Me cable from the LAST Classic to the FIRST on my system.  Everything goes ONE-WAY from the MASTER on the LEFT to the others on the RIGHT or Down-Stream.  This seems to be working, this stops the "SLAVES" from sending modes back to the MASTER flipping it.  I like it better but it is not a Midnite official mode of operation but is supported now.  I like the MASTER to be in total control.  Use at your own risk...

Hope this helps, Jim Parish, MNS Tech Support

Copyright © 2025 MidNite Solar Inc. - All rights reserved.
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

ClassicCrazy

Frequently Asked Question
All Categories » CLASSIC CHARGE CONTROLLER - Features and Programming
CLASSIC - F-ME - Why are my Classics not sharing the work when networked with Follow-Me?
Last Updated 5 years ago

When Classics are connected together using Follow-Me cables you get the following features:

1) MODE coordination. All will follow for BULK, EQUALIZATION & FLOAT.
   NOTE: ABSORB is NOT a Follow-me MODE, EACH Classic MUST reach the Absorb voltage setting on its own.
              RESTING is NOT a Follow-me MODE, each Classic goes RESTING on its own.

2) BTS aka Battery Temperature Sensor sharing. Pick a Classic to install the BTS in, it can now be called "BTS MASTER".
   NOTE: There is no other designation of "Master" or "Slave" with the F-Me network, All Classics can switch modes and send that data around the network.

3) Installation suggestions:
A) Pick one Classic to be BTS MASTER. Set in TWEAKS to BTS NET = MASTER and all others to BTS FOLLOW. Install a BTS in this Classic ONLY.
B) If using a Whizbang JR install in this Classic. NOTE: SOC% and other WBjr info is NOT shared with other Classics.
C) SET BTS MASTER Classic Absorb time to what you need, set all others to 10 minutes longer.
D) If using REBULK set it in the BTS MASTER Classic ONLY.

The Blue LED at the top of the Classic circuit board will flash to indicate Follow-Me network operation.
1 second flash = no data, bad cable or F-Me not turned on in TWEAKS.  1/10th second blink = data okay.
NOTE: You can test a F-Me cable by connecting in a Classic looping the middle jack to the bottom jack. If the cable is good and the Classic is working in F-Me the BLUE LED will go from a 1 second blink to 1/10th second.

NOTE: It is common for an occasional 1-sec blink to be observed during normal operation.

4) Follow-Me is not going to make the Classics share the current they produce. Production watts & amps are going to be specific to each Classic's capabilities according to the installed input source.
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

ClassicCrazy

Also the yellow display of the Local Status app shows your Classic clock is set to wrong time.
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP