Flipping the 'inerds' of an E panel

Started by Westbranch, June 24, 2013, 08:34:47 PM

Previous topic - Next topic

Westbranch

Well there I was out at the cabin,  with Classic and Epanel MNE175 ST (for an Outback) in hand and reading the installation manual for the Epanel , where is says that the Cl should be mounted on the RIGHT hand side so that the heat sink is out in the open.
OOPS, my Epanel has the main breaker on the right side...??... OK, it should be on the left side for use with the Classic...
read a few more lines and it tells me that swapping things around CAN be done but it's not easy to do in the field...

So I started to move stuff, but i noticed that the 'flipping' will get more complex as I have the bypass breakers in the upper right corner.

Questions:
Is there a video of thee swapping process?
Does everything have to be swapped around? I am hoping that just the main breaker, shunt, and  grounding bar , (currently just below the top of the 175A breaker ) are all that is needed to be moved.

Ryan?

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Robin

I have never tried just flipping the main breaker? To flip it all, you would also need a new door. I would not do it unless it is really required. It is very confusing. Even our assembly people have trouble building a right hand unit after doing lefties for weeks at a time.
Robin Gudgel

Westbranch

thanks robin, I am a bit confused as the manual says that the Classic should be mounted on the right side (looking at the Epanel) so that the heat sink is on the outside.

However in the manual EPanel Instructions there are several examples of both right and left hand mounts... 

So which is right or is it just "better" to mount the Classic on the right side for best cooling?

PS FYI... there are still some of the wiring charts showing the Delta 302R Arrestor... ???
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

TomW

Quote from: Westbranch on June 30, 2013, 12:34:46 PM
thanks robin, I am a bit confused as the manual says that the Classic should be mounted on the right side (looking at the Epanel) so that the heat sink is on the outside.

I did not go back and reread the instructions but I thought they were talking about a different charge controller? MX60 maybe?

The Classic seems symetrical on the "fins" on the case. I have both methods in use with no ill results.

left hinged, right hinged E-Panels with the FX2524s on each mounted towards the hinge. So one Classic is to the left and one to the right of the FX2524s.

I found the instructions very confusing the way it jumps from one configuration to another in the same block of text Once I got doing it it all came together, however.

Just from here.

Tom
Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

Westbranch

Tom, last week I moved my temp setup to it permanent location and swapped out the MX.  ::)
Now I have 2 Cl 150's working on separate banks  ;D

According to the Instructions the Classics and MX/FM series all are right hand mount preferred, small wonder since boB had a lot to do with both...

Ya I too think the 'book' could do with a reorg/rewrite to simplify it and clarify it. Part of it is different models and applications.

It reads like there were a lot of scribes  :-\, all at different places and times with different skills ...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Westbranch

I am still looking for advice on whether it is necessary to move the AC bypass breakers to 'the other side'  to meet NEC issues or is it OK to flip the DC only?? 

As far as I can see there is lots of clearance , possibly need a separator between AC & DC?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Rybren

Midnite provides a plastic spacer to fit between the AC and DC breakers (it's a thin piece of black plastic).  The spacers should have been included with the E-Panel; if they weren't, Midnite will ship them to you.

+1 on the manual needing a rewrite.
4 x 210W PV, Classic 150, e-panel, Samlex PST-1500-24, 232AH 24V