Hey,
I Started to have a problem with my classic 250 today.

Background info:

5 Classic 250s on Solar and 1 so far on wind.
16,000 watts of solar.
4000 amp hour bank @ 48 volts.

One of my classics is giving me an error, I made a video of the problem that repeats itself every 2 minutes or so.
See full problem @ the 1:09 mark:
http://youtu.be/PbatXPyzG4I?t=28s

TomW

I can't get that video to load properly seems to only be partially there?

Maybe its me?


Tom
Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

Westbranch

Tom I think he means when the screen goes red..., at the start and ~ 1 min in...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

tecnodave

Watch closely, when screen goes red , small box appears, FET drive error, and FET temp is 45.9 degrees (C)

td
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

TomW

Quote from: Westbranch on December 25, 2013, 03:11:53 PM
Tom I think he means when the screen goes red..., at the start and ~ 1 min in...

I mean I cannot get it to play. Period.

No matter, I probably cannot help anyway.

Tom
Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

Westbranch

Oh, Santa has blocked your machine so no surfing today...  ::) :'(
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

boB


The Local App could probably use some new wording.  that might actually be "OCP" or
Over Current Protection occurring.  Depends on the age/version of your Classic
and the firmware on it.

what is either the serial number or firmware date/version in that Classic ?

Has it been working OK for a while and this just started ?

If this is just an OCP, maybe you have some large battery side loads that
are turning on ?  That might cause this, or at least, OCP's.

BTW, I could see your video just fine here.

boB
K7IQ 🌛  He/She/Me

laszlo

FYI, I was also able to see the small popop with "Defcon 4".

Could it be a localapp bug , let's suppose, when it gets some out of range value? Or possibly a mini-sweep? I would try to isolate that classic to log onto a different localApp and see if you can still reproduce.
4.6KW offgrid PV system, Classic 200, MX60, dual Magnum PAE 4448 inverters, Midnite combiner and disconnect boxes, e-panel,  WBJr, and 8 MN SPDs

boB


Still would be good to know how old the Classic is and/or firmware version as
well as if you notice large loads coming on when you see the message.

Does it re-occur many times around the time you see it ?  If so, you might
also look at the MNGP to see if it is also giving a message in the status
screen.

Is the Classic turning off momentarily when this happens ?

The Reason For Resting number would also be helpful maybe if it does
go to Resting at this time.

boB