Classic shut down: MODE = OFF Orange LED on MNGP blinking

Started by Westbranch, April 21, 2014, 07:44:43 PM

Previous topic - Next topic

Westbranch

I returned to the cabin for Easter and went to check my 2 Classic 150's,
#1 was fine and happily in Float by noon
#2 however was not so happy as it has shut down , Mode = OFF showed on MNGP and the bottom LED was Blinking Orange
Jeez, no internet available and didn't bring a  laptop..... :o :o and a flat battery to boot

Off to the closest neighbour (5 miles) with internet , On Line manual states Blinking Orange indicates that there was an Over Amperage event  ???

I am puzzled as there are ONLY 2 140W (12V 8A) panels in series  and the CC Output was set to 90A and the Input set to 55A.

I reset the mode to ON and reset the battery charge parameters, it had defaulted to 12 volt settings.

Appears to be functioning OK for now.

Cl serial number  # 647, sorry could not remember the key strokes to retrieve the FW version.

Any ideas?  stumped here
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

boB


That blinking LED could mean it has either reached the current limit (unlikely with your small array)
or it has gotten (or thinks it has) gotten too hot.

Maybe it just thinks it is hot ?  Check the FET and PCB temperature readings.

Another thing that might (can't remember off the top) to make the orange LED come on is
over-voltage on the PV input which is also probably unlikely.

Check the PV voltage and temperature readings just for good measure.

boB
K7IQ 🌛  He/She/Me

Halfcrazy

Westbranch
Are you sure its the amber LED blinking? The bottom one? I can not say I have ever seen that one blink.

RYan
Changing the way wind turbines operate one smoke filled box at a time

Westbranch

#3
thanks boB, I will try to do a temp log  for a few hours next visit.

Ryan, for sure it was the bottom LED, Amber (or Orange) at the bottom of the MNGP, left side.

Forgot to add:

that the CL647 is a refurbished unit;

All 3 LEDs inside were in Blinky mode;

the CC had reset out of Solar mode as well (forget to what though, P&O?), corrected that too.

Ambient temps in basement were well below freezing all winter!  -5C to -30C

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

boB

Did you check the Reason For Resting ?

ReasonForResting = 27  is one in earlier Classics that can cause the MODE to
turn OFF...  but yours may be a bit too old for that if serial number 647....

   Can't remember when we added R132.

In fact, check this drawing and see if this resistor is in your Classic.

http://fusion.midnitesolar.com/Classic_R132.jpg

Another reason that the Classic can turn the mode to OFF is if the wind graph is
bogus and has a current step that is higher than 99 amps.  This could happen
even if your Classic was not in wind mode.   BUT, your Classic came back on so
that is probably NOT your problem.

Please check for R132.  I don't know why the LED would be ON or blinking though
for that reason but it could make its mode go to off.

boB
K7IQ 🌛  He/She/Me

Westbranch

#5
Quote from: boB on April 21, 2014, 08:56:43 PM
Did you check the Reason For Resting ?

ReasonForResting = 27  is one in earlier Classics that can cause the MODE to
turn OFF...  but yours may be a bit too old for that if serial number 647....
boB

boB, the only info was the PV and Battery voltages/amps and MODE = OFF.

There was no REASON showing on the main screen, so is there a way to 'drill deeper' on that machine to find the REASON?

Oh, and the 'internal Leds were cycling 1on, then 2 on and then 3 on, and then repeat (BLINKY mode?)
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Westbranch

Quote from: boB on April 21, 2014, 08:56:43 PM

In fact, check this drawing and see if this resistor is in your Classic.

http://fusion.midnitesolar.com/Classic_R132.jpg

Please check for R132.  I don't know why the LED would be ON or blinking though
for that reason but it could make its mode go to off.
boB

boB, re the presence or not of that R123:  If the pins are not showing,  the resistor is absent?

In the pic, it looks to me that there are 2 soldered pins, right?

thanks.
Eric
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Resthome

Quote from: Westbranch on April 22, 2014, 02:10:57 PM

There was no REASON showing on the main screen, so is there a way to 'drill deeper' on that machine to find the REASON?


To enter the reason for resting  screen from main status...

Hold down left arrow key and then press the enter key
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Westbranch

thanks RH,  I remember reading something about that before, just old-timers brain prevents it floating to the top....

Do you know how to get to FW version etc.?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

Quote from: Westbranch on April 22, 2014, 02:53:36 PM
   ...   Do you know how to get to FW version etc.?

WB,  just keep tapping the Status button,  the page for FW version(s) is about the seventh down,  or so.   There are other ways ...  believe that it is also displayed on App.
Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Westbranch

thanks Vic, :) I don't have a functioning laptop right now :( so I cant use the Local  App.

I should now be able to get the needed details to help solve this one.

Hope to be back out next weekend and finish a bulk gen charge.  Some birthday present!  :(
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

And,  WB,

RH John is correct about the RFR.   There MIGHT be a distinction between "pressing",  and tapping the Enter button.  In the past,  boB  has mentioned "tapping" Enter.   It is possible that if one held the Enter button for too long that it might change the state of the Classic (?).

Here is a Thread regarding RFR -- Reply #1 from boB explains the page that contains the RFR number:

http://www.midniteforum.com/index.php?topic=519.0

FWIW     Is your off-grid site  with the subject Classic prone to Spring lightning incidents?   And,  do you recall updating the FW in this Classic after you received it?   The Refurbed Classic here had the current Production FW as of the time it left MN,  after the repair.  Good Luck,   Happy Birthday!  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Westbranch

thanks Vic.
Quote from: boB on March 24, 2012, 07:46:06 PM
from the main status menu, HOLD down the LEFT ARROW button and TAP the ENTER key.

You will see a screen with some numbers on it with IN on the left and OUT on the right.  What you want to take note of is the number at the MIDDLE-TOP of the screen.   That number will give an idea of why it went to resting.
That number will always be active and represent the last time it went to resting.   i.e., the number will not get erased if you don't look at it right away.
boB

Right from what boB and RH said and your comments, I should be able to retrieve something.
I also found boB's  list of Reasons   via a search for ReasonforResting" here
http://midniteforum.com/index.php?topic=1728.msg15750#msg15750

Re lightning, no we do not get much.  I would have expected both Classics to have been affected as my small maintenance arrays are on the S wall and within 1 foot of each other and the wires to both Classics are closer than that. Both banks sit side by each ~ 1 foot apart, I immediately thought of that potential but after a short self talk dismissed it , if it hit one, the other would have been hit AFAICS
NO lighting protection installed so far, SPDs in a box at the ready...

YUP, officially an old fart now... what the heck, its the new 45 as my wife tells me before reminding me to slow down...

cheers.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

boB

Quote from: Westbranch on April 22, 2014, 05:01:47 PM

YUP, officially an old fart now... what the heck, its the new 45 as my wife tells me before reminding me to slow down...

cheers.

What ?   45 ?    ;D

dP     dP   .d888888   888888ba   888888ba  dP    dP
88     88  d8'    88   88    `8b  88    `8b Y8.  .8P
88aaaaa88a 88aaaaa88a a88aaaa8P' a88aaaa8P'  Y8aa8P 
88     88  88     88   88         88           88   
88     88  88     88   88         88           88   
dP     dP  88     88   dP         dP           


888888ba  dP  888888ba  d888888P dP     dP  888888ba   .d888888  dP    dP    dP
88    `8b 88  88    `8b    88    88     88  88    `8b d8'    88  Y8.  .8P    88
a88aaaa8P' 88 a88aaaa8P'    88    88aaaaa88a 88     88 88aaaaa88a  Y8aa8P     88
88   `8b. 88  88   `8b.    88    88     88  88     88 88     88     88       dP
88    .88 88  88     88    88    88     88  88    .8P 88     88     88         
88888888P dP  dP     dP    dP    dP     dP  8888888P  88     88     dP       oo
                                                                                 
                                                                                 

                                                   
K7IQ 🌛  He/She/Me

Westbranch

Tks boB... 65 is the new 45,  ya that expression was found in Zoomer (Canadian) Magazine by SWMBO and she keeps reminding me SHE isn't there just yet!
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter