Adding panels

Started by N1UB, October 21, 2015, 11:08:31 AM

Previous topic - Next topic

N1UB

I have a system that uses a Classic 150 and a pair of Trina 255 panels. I have found a good price on a pair of Solarworld 260's. Would this be a problem to add into the system with a slight miss match of panels in a separate string ? My panel wiring is <10' and goes directly to the E panel.

Thanks, Bart

ClassicCrazy

I added some panels of a different type to a friends system and had the same question. You need to keep the voltage Vmp  of each string within a certain percentage of each other ( I forget what percent that is now) . Otherwise the MPPT won't work correctly.

Here is a discussion that someone asked about adding panels.

http://www.midniteforum.com/index.php?topic=793.5%3bwap2

system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

Westbranch

keep the voltage Vmp  of each string within a certain percentage of each other

the rule of thumb used for percentage is  +- 10%....
In parallel connections it is the Vmp that makes the difference.
In serial connections the important number is the Imp .

hth