Midnight Classic 250 Xantrex freedom 3000 inverter charger????? 2.8 kw array

Started by tony, July 09, 2011, 12:47:26 PM

Previous topic - Next topic

Vic

Hi tony,

With these high voltage panels,  things can fall apart a bit.  Two panels in series is probably as good as it gets.  BUT,  now at this string voltage,  technically,  you will need the HV Breakers in the combiners,  and these breakers occupy two positions,  so you might need more or larger combiners,  and so on.

Good Luck   and Have Fun,  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Westbranch

Morning Tony,  I think you will need to draw both options out on paper and compare line loss, cost of wiring and combiner boxes etc, on paper before you head out shopping....

you want to avoid the Ready, Fire, Aim syndrome (thanks to Icarus).

BTW don't get too flustered , the learning curve is quite steep at the start.

Eric