Blank display - unit not working suddently

Started by zekeria, November 13, 2015, 11:56:15 AM

Previous topic - Next topic

zekeria

Quote from: b4solar on November 16, 2015, 11:05:45 AM
Zekeria

Thanks for the purchase.

How much voltage was applied to the input during cold weather conditions?

The highest value ever seen in the display have been around 141 volts with the former Tracer charger from Ep Solar.

zekeria

Hi.

My return request through the seller at Ebay has been denied.
How do i make formal RMA request through Midnite Solar themselves??

I have linked to this thread in mails to Ebay buyer panel.

But still the refund was denied and without reason?

I just want a functional unit and will gladly send this unit back if the shipping is paid for in accordance with international trade law for consumers.

:'(

Halfcrazy

You would need to email support@midnitesolar.com and give them a link to this thread and ask for an RMA

Changing the way wind turbines operate one smoke filled box at a time

dgd

Hi,

So what are the specs and model numbers of the solar panels?
Could the pv input voltage have risen too high as its winter with low temperatures?

dgd

Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

Halfcrazy

Changing the way wind turbines operate one smoke filled box at a time

Vic

 ...  THAT was my guess,  also,  dgd,  Ryan,  but this data has not been forthcoming.

OH  well ...   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Halfcrazy

Well we can check Max VOC when it makes its way back to the RMA dept
Changing the way wind turbines operate one smoke filled box at a time

zekeria

#22
Quote from: dgd on November 20, 2015, 11:53:32 PM
Hi,

So what are the specs and model numbers of the solar panels?
Could the pv input voltage have risen too high as its winter with low temperatures?

dgd

HI, here are the complete copy of what it says on the back of each panel so that we can try to determine if it is VOC before RMA

The panels are from a firm called "Sun We"'
Model number SF125X125-M(L)
Pmax 195 W
Imp 5.29A
Vmp 36.9V
Isc 5.64A
Voc 45.4V
NOCT 45+-2c
Power tolerance range +-3%
Test Condition 1000W/m2, AM1.5, 25c
Cell type Mono-Si

3 connected in series as said.

So theoretical maximum voltage is 136 Voc at 25 degrees.

The temperature has not been below 10c

Thanks for the support email, i will contact them as soon as we figure something out here.

From my humble experience it does not look like Voc.

The fault happen when the user came back from three days away and he saw imediatly that the "load" was blinking the light that he had attached on and of at a very high rate when several lights was turned on, where it before worked like a charm, he then looked at the charger and the display was all dead and then i was called to assist in figuring out what had went wrong.

Thanks in advance for the help and time  :D

zekeria

#23
Quote from: Halfcrazy on November 20, 2015, 12:36:33 PM
You would need to email support@midnitesolar.com and give them a link to this thread and ask for an RMA

Thanks a lot.

I will write them when some has looked at the panels and tried to give their guess.

zekeria

Quote from: Vic on November 21, 2015, 03:34:55 PM
...  THAT was my guess,  also,  dgd,  Ryan,  but this data has not been forthcoming.

OH  well ...   Vic

It is now  :D

So what do you think?

Westbranch

Just found this info for you,

http://www.pannellisolari.bologna.it/files/sunowe_mono_72.pdf

there are temperature coefficients that you need to use with the Kid Sizing tool

http://www.midnitesolar.com/sizingTool_kid/index.php

Looks like you are good to -5*C
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

zekeria

Quote from: Westbranch on November 26, 2015, 12:24:39 PM
Just found this info for you,

http://www.pannellisolari.bologna.it/files/sunowe_mono_72.pdf

there are temperature coefficients that you need to use with the Kid Sizing tool

http://www.midnitesolar.com/sizingTool_kid/index.php

Looks like you are good to -5*C

That was what i figured, so it can not be Voc then.
It must be something else.

Thank you so much for your help and time, if that is also what the rest can confirm, then i will RMA the unit.

Halfcrazy

45.4VOC times 3 is 136.2 volts. It would not take much cold to go over the safe voltage but that may not be the issue. Best solution is likely to get it back for a look see