What size battery cable are you running from the Classic?

Started by Jacotenente, April 26, 2016, 02:35:20 PM

Previous topic - Next topic

Jacotenente

The blue terminal blocks on the Classics say 6 AWG (#6) wire. I just switched to #4 AWG (tight fit). According AWG and NEC, for power transmission #6 is good for 37 amps and #4 is good for 60 amps. The Classic 150 can output 90+ amps. Am I missing something here? Please advise.

Chris

ClassicCrazy

#1
What voltage are you running ?

I just plugged a few numbers in this calculator
12v , 90 amps,  6 feet, 3% loss and it shows 5 gauge wire.

http://www.freesunpower.com/wire_calc.php

Go higher in voltage and the wire size will come down. There are  voltage drop calculators on the internet where you can design the whole wiring system.

Also look here
http://www.affordable-solar.com/solar-tools/wire-sizing-charts/

Also search around on the group here - this discussion has been done before .

Larry

system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

Vic

In addition to what Larry mentioned,

The Ampacity Table is a good guide of what is Permissible for cables according to the NEC.  Here is such a table:
http://www.cerrowire.com/ampacity-charts

In this table,  you will see that THHN and similar COPPER cables have a Maximum Ampacity of 65 Amps for #6 AWG,  and 85 Amps for #4 AWG  --  use the 75 C column,  as this is usually the maximum temperature permitted for most circuit breaker terminals,  connectors,   and terminal blocks,  as are used on the Classic.

The above Ampacities are for only a maximum of three current-carrying conductors in a Raceway,  conduit,  etc.   More than three conductors,  up to six conductors,  derate the above ratings to 80% (multiply by 0.8).

There are also deratings for Ambient temperatures above 30 degrees C.

NEC  is generally considered to be very conservative regarding Ampacity of cables.

If you wish to use larger conductors than #4 on a Classic,  you can use a short piece of number 6 or 4 AWG to a junction box,   or perhaps,  the enclosure that contains the breaker for the cables that connects the Classic to the battery.  From the other side of this breaker,  you can get as crazy with as largea  cable as can be accommodated by that breaker's terminals.

For e-panels and similar "conduit & breaker boxes",   the Free Air Ampacity will usually apply,  which allows higher Ampacities,  as these cables are not contained in a small space (like in conduit),  and/or these cable runs are usually quite short,   and so on.

Am notta Code Maven,  but this is my read on things,   FWIW,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Jacotenente

#3
My system is a 24v (Outback Power VFX3524 + Mate 3). Roger that...thanks. I am using TEMCo #4 welding cable (lots of strands). Less than six feet for both POS and NEG. I run through a Baby Big Box and then down to the Blue Seas Systems 250A busbars. Just did the upgrade. But, I can already notice the improvement (power is up and heat is way down).

Vic

Hi again Chris,

Regarding the #4 Welding Cable.   If you are using this for the battery connection from the Classic to the battery breaker,  and from the battery breaker to the battery busbar,  would say that this is not such a good idea.   Fine-strand cable is not specified,  generally,  for these screw-compression type terminals.

The main reasons that it is best to NOT use fine strand cables on compression terminals,  is that,  first,   fine strand cable is larger in diameter,  and #4 b AWG fine cable will probably be a bit too large for the Classic terminal block.   And,  fine-strand cable cold-flows more than standard Building wire,  like THHN (19 strands,  generally),  such that,  there is a much greater chance that over  a period of time (weeks/months)  that the compression connection will become less tight,  causing increased resistance.  Higher R causes more local heating.  Temperature cycling can cause further loosening,  and more resistance,  and so on.   This is not a good situation,  and could cause damage,  poor performance,  and perhaps local burning of insulation,  terminals and/or busbars.

You may not have used this fine-strand cable for these connections,  but just FYI,  in case you did not know ...

Using fine cable in  Lugs that are designed for it,  and with Dies that are designed for those lugs  is the proper way to use fine-strand cable.

FWIW,    Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

zoneblue

Yes, fine strand , but use ferules, or some solder to hold the strand bundle together (people argue about this).

Or do what most people do, mount the classics on the side of the disco, and run very short classic cable (less than a foot), so cable gauge is less critical. HOwever if like here youll lose a few tens of mV in the (blasted) carling breaker, and this will be as likely as not be greater than any cable loss.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

CDN-VT

I use swedge ferules as in pix.
red small double red larger , blue , double blue etc. then yellow to green that is for #3AWG




Loading pix screwed up the post .
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

Jacotenente

Thanks! FYI - Had a stellar sunny day yesterday and my wiring and DC breakers in the Baby Big Box barely got warm at full power! So, the #4 AWG TEMCo welding cable is working. And working well.

Can I get a product link for those ferrules? Solderless? I can also "tin" the cable ends. I agree, with what you said about compression fittings on fine strand wire...good idea.

Thanks.

cb487

My Classic 150's 4 AWG wire got VERY warm whenever my Classic 150 outputs 70 Amps or more. So I changed all the wires to 2AWG, except for the -48V cable that connects the Classic to the -48V bus. That cable never passes more than a few Amps (only power that is consumed by the Classic itself). I left it at 4 AWG.

At this time of year, my Classic outputs 80+ Amps, and even 2 AWG wire gets warm.

The Classics don't actually support wire bigger than 4 AWG, so I used a wire stripper to cut just enough outer strands of the wire to fit the Classic wire terminals.

Running high power can challenge a system design. Originally I placed the two +48V 100 Amp breakers next to each other. I discovered that  they would trip before hitting 100 Amps because of heat buildup. I've since spaced them apart enough so that air can naturally flow between them to fix this.

Chris

dgd

I think there will be the same current flow in +ve and -ve cables to Classic
You should be able to use short lengths of #4 to the DC distribution box, epanel, mndc etc
Then from there use larger cables such as #00 or #000 to the battery bank
dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

cb487

If you have a DC-capable clamp meter, use it to measure the Amps running through the -48 lead on the Classic. E.g., when 80 Amps was passing through my Classic, the -48 lead showed only 4 Amps. Where is the rest of the current? It's flowing from the PV array -48 lead directly to my SW Plus Grid tie inverter. The 4 Amps is the PV power being consumed by the Classic itself.

Chris

dgd

Ok, I have not seen this before but then I have my PV array + and - wired into the Classic then the Classic Batt + and - 4gauge wired to Epanel. This means I see 70amps in both the + and - Batt wires to the Classic
In your config you have the PV- direct to Epanel?
I think I have seen this in some of the Midnite wiring diagrams but it never occured to me that this would mean only the Classic BATT+ connector would need to be a decent gauge cable with the BATT- possibly being much smaller 6 or 8 gauge.  :o

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

CDN-VT

POS + is the cable size to consider on this topic. ( the wiring schematic way ) I run 4 Gauge not fine strand.  I have used temp scene guns to see hot spots .

VT
& the  ferules are pre 80's .
We have many in Pico
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

cb487

Responding to dgd here ...
The copper between my battery bank and the inverter is 4/0 protected by 250A breaker. PV- is tied to the same place as Bat- and Classic-.

Actually you can't downsize the Classic -48 wire, even though it ordinarily carries only a few Amps. Here is why: There are fault conditions in which the Classic would need that wire to carry a current the equal of what either of the Classic 48+ wires ordinarily carry. In such a runaway fault situation, only one of the two Classic DC circuit breakers would be able to put a stop to that. If the Classic -48 wire was say a 10 AWG or 8 AWG, it could go incandescent without drawing enough current to trip the Classic +48 breakers.

Chris

dgd

So from what you are saying there is basically no advantage in wiring the PV- direct to the common
battery negative since its still necessary to have two same gauge cables, #4, to the Classic battery + and - connectors.
You may as well just wire the PV - and + to the PV inputs in the Classic.

Usually there will be a 500A Deltec shunt connected via 3/0, 4/0, 70mm2 or 90mm2
cable to the battery -ve.  The other side of the shunt will be the common negative point for inverter connection and other devices such as charge controllers etc
The battery +ve 70mm2 cable uses one end of the 250A breaker as a +ve common connection point with the other end of the breaker connecting to the inverter +ve

Your original post interested me because you seemed to believe the 4A you measured in the -ve wire was indicating the power consumed by the Classic. That didn't look right to me as it would mean the Classic was consuming about 200 watts.
Or did I misunderstand what you really thought this 4A current flow was really showing?

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000