when should I use the 30 amp charge vs the 20 amp

Started by baltictim, October 01, 2016, 08:58:40 PM

Previous topic - Next topic

CDN-VT

Quote from: baltictim on October 06, 2016, 12:27:14 AM
All of the panels are presently connected in Parallel....all go to a combiner with just two wires going to the Brat. The Brat is set up now as a 20A charger....ie the load circuit is not in use...
I had a long talk with Roy at Midnite Solar today...the outcome seems to be that I would be best served by using my existing Brat only for the 160W panel plus purchase a KID MPPT controller, connect my 4x100W panels in series and run them through the KID as a 48v array....
I can buy the KID here in California for $360 usd all in....

Im with ROY also ,noting wrong with the BRAT but not in that setup .
Post your panel specs please on the 100 & 160 watt-ers

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels