Started by Boompy, November 14, 2016, 09:30:49 PM

Previous topic - Next topic

Boompy

Hi all

I'm trying to standardise a system design using a single cable gauge (going to be building a lot of these).

I understand that the Battery Terminals on the Classic are spec'd for max 4AWG.

In this part of the world you can't readily purchase cable in standard AWG sizes. Plus it seems that standard crimp lugs don't exist for 4AWG.

I can readily purchase stranded 25mm2 cable, which has a greater cross sectional area by comparison to 4AWG (21.15mm2).

Can anybody advise if 25mm2 cable does work with these terminals? If not, is there a similarly sized standard metric size cable that will fit? Generally we go from 25mm2 to 16mm2, which is quite a jump.

Also, what is the max metric size the Classic's earth terminal will accommodate?

Thanks

Westbranch

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

CDN-VT

Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

Boompy

Quote from: Westbranch on November 15, 2016, 12:04:55 AM
CDN-VT posted this solution...

http://kb1uas.com/mnsforum/index.php?topic=3267.msg31462#msg31462

Thanks guys

Now I did see that thread earlier Westbranch. That surely is an ornate solution all be it a little convoluted for my purposes.

Can anybody vouch for the max diameter cable or cross sectional area they've managed to squeeze in these terminals? I'm guessing some just remove a few strands from their cables to squeeze the conductors in there.

Also how is the earth terminal sized (I don't have a Classic on hand to measure at the minute)?

ClassicCrazy

I looked back on a thread on here where I talked about only being able to squeeze in 4 gauge . Vic had said in another post that it has to be 19 strand type and that fine threaded cables of 4 gauge size won't fit in .

Not sure about the ground lug - don't remember if it was larger than the other terminals.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

CDN-VT

Ground Lug is larger .
Im running a follow me with one large Battery cable .
VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels