Classic 150 output breaker keeps tripping

Started by malkierian, March 25, 2020, 02:04:00 PM

Previous topic - Next topic

malkierian

I've been having this problem where the breaker between my Classic 150's output and the battery bank keeps tripping. The breaker is 150 VDC 100A, and I have the Classic set to output 87 amps at most (though I've never seen it actually get above 40 or so with my panel setup). The problem is, this happens at night, when no power is coming in to the controller, and thus nothing should be going out. Anyone here have any idea why this breaker would keep tripping like this when there should be no load whatsoever?

boB


The Classic is working OK during the day ?

If so, it might be a faulty breaker.  Maybe...

The Classic doesn't draw much current at night of course so doesn't come anywhere near 100 or 87 amps at that time.

K7IQ 🌛  He/She/Me

ClassicCrazy

#2
Did you check all the wires and connections at the breaker to make sure they were tight ?


Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

malkierian

Yes, the Classic is working just fine during the day, under load. The breaker has never been tripped during the daytime. Only when we get up in the morning.

Yes, I double checked the connections just to make sure, they are secure.

ClassicCrazy

Do you have any pets there that are making jokes on you ?
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

malkierian

If only, but no animals have access to the electrical shed XD

ClassicCrazy

Does it do this consistently every night ?
Maybe try to eliminate possible causes from something else - switch off PV or switch off loads and see what happens . But if it is bad breaker you have to change that . Maybe you could disconnect PV and then use that breaker on battery output  for a night and see what happens .  I am just trying to think what I might do with what I had available at the time.
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

boB


I'm sure that we can just send you a new breaker.

Just call or email  support@midnitesolar.com

K7IQ 🌛  He/She/Me