Connecting PV Arrays through Breakers

Started by jramerman, June 06, 2020, 03:57:31 AM

Previous topic - Next topic

jramerman

Greetings all. I am just wondering if I have correctly connected my 2 PV arrays to a Classic 150 via 2 x breakers. Attached is a diagram of the connections up to the Classic 150. The diagram explains the equipment involved.

ClassicCrazy

#1
The way I do it and most combiner boxes is to have each array positive go to it's own breaker . The two positive breakers feed into a common wire  that goes back to the controller that has another breaker sized for that  wire. The negative  goes direct to controller with no breaker .

So PV one to 15 amp ( or 20 depending on wire size and array)   PV two to another 15 amp . The two positive  breakers feed into 6 gauge wire ( for maximum power input my classic can handle )  . That six gauge goes to 60 amp breaker that feeds the Classic. The two array negatives are tied together in combiner box with 6 gauge and go directly to Classic negative input .
There is more info and schematic here http://www.midnitesolar.com/pdfs/MNPV_Instructions_Rev_A.pdf

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

mike90045

http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

jramerman

Thank you ClassicCrazy and Mike 90045 for your input. Regards.