Temporary power for MNGP2

Started by Kent0, December 13, 2024, 01:28:51 PM

Previous topic - Next topic

Kent0

Is it possible to temporarily provide power to the MNGP2 with a 9V or 12V battery so that the firmware may be updated in the office?

ClassicCrazy

not sure how far your office is from your power room , but I run a cat 5 cable from my hawkes bay about 20 or 25 feet to where I have mngp2 remoted and have always upgraded firmware at that point.
But you have an interesting question , if you provide the 9v to mngp will it turn on and then update ?  I will be interested to know too if it needs the other Canbus comms connected back to device . My guess will be yes .
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

Wizbandit

PINS 7&8 and it does not need CAN COMMS to power up.
9 to 12VDC is okay

Kent0

After confirming that pin 7 (white/brown wire) is positive an pin 8 is negative (brown wire), I powered up a MNGP2 with a 9V battery and completed a firmware upgrade. In the future I'll make sure the MNGP2 firmware is upgraded before installation.