Brucey

I'm running one of these to charge my batteries versus Rosie (I'd be limited to a 15A 120V input due to how shes setup right now)

https://www.ebay.com/itm/127129496258

I'd suggest multiple units to give you redundancy


BlackwaterPark

Quote from: Brucey on December 09, 2025, 04:55:54 PMI'm running one of these to charge my batteries versus Rosie (I'd be limited to a 15A 120V input due to how shes setup right now)

https://www.ebay.com/itm/127129496258

I'd suggest multiple units to give you redundancy



I've seen a LOT of people very unhappy with those ecoworthy chargers, as they seem to be very very picky about the THD output of the generator, much like all these inverter chargers. What kind of generator are you running through those?

Brucey

Quote from: BlackwaterPark on December 09, 2025, 05:08:42 PM
Quote from: Brucey on December 09, 2025, 04:55:54 PMI'm running one of these to charge my batteries versus Rosie (I'd be limited to a 15A 120V input due to how shes setup right now)

https://www.ebay.com/itm/127129496258

I'd suggest multiple units to give you redundancy



I've seen a LOT of people very unhappy with those ecoworthy chargers, as they seem to be very very picky about the THD output of the generator, much like all these inverter chargers. What kind of generator are you running through those?
Mines running via grid as double conversion at 30A output but also ran it on a Honda eu2200i generator for a bit to test, no worries. Mines a v1, the current v2 model also includes a soft ramp function so it doesnt hit generator hard if you have it set for the full 60A output on 240V for example.

There quite a few of us over on diysolarforum using them and I haven't heard of anyone having issues. Any particular forums or threads?

BlackwaterPark

Quote from: Brucey on December 09, 2025, 05:16:12 PM
Quote from: BlackwaterPark on December 09, 2025, 05:08:42 PM
Quote from: Brucey on December 09, 2025, 04:55:54 PMI'm running one of these to charge my batteries versus Rosie (I'd be limited to a 15A 120V input due to how shes setup right now)

https://www.ebay.com/itm/127129496258

I'd suggest multiple units to give you redundancy



I've seen a LOT of people very unhappy with those ecoworthy chargers, as they seem to be very very picky about the THD output of the generator, much like all these inverter chargers. What kind of generator are you running through those?
Mines running via grid as double conversion at 30A output but also ran it on a Honda eu2200i generator for a bit to test, no worries. Mines a v1, the current v2 model also includes a soft ramp function so it doesnt hit generator hard if you have it set for the full 60A output on 240V for example.

There quite a few of us over on diysolarforum using them and I haven't heard of anyone having issues. Any particular forums or threads?


youtube videos is where I'm seeing all the comments on it. There are two videos in which it is tested and doesn't want to work with some generators. I'm guessing they can adjust the firmware though, in order to broaden the range it will accept. If most folk are running quality inverter generators like hondas or yamahas, I doubt you would have a problem, but it's the conventional ones that become an issue...very ubiquitous gensets like the predators and champions.

BlackwaterPark

https://youtu.be/6D6YdLJWMY8?si=yFUWHScDWhYHD8oS

This was one such, but there are quite a few other videos from different channels that are less than glowing, but it's really in the comments section that I tend to scour where I find the similar sentiments based on poor user experience. A couple, and is whatever...but when there are dozens and over several different vids, that's when I kinda take notice. I was looking for a cheaper alternative to another chargerverter to have on hand, so I was hoping the ecoworthy was a viable option, which is what sent me down that particular rabbit hole in the first place.

Brucey

Quote from: BlackwaterPark on December 09, 2025, 05:49:58 PMhttps://youtu.be/6D6YdLJWMY8?si=yFUWHScDWhYHD8oS

This was one such, but there are quite a few other videos from different channels that are less than glowing, but it's really in the comments section that I tend to scour where I find the similar sentiments based on poor user experience. A couple, and is whatever...but when there are dozens and over several different vids, that's when I kinda take notice. I was looking for a cheaper alternative to another chargerverter to have on hand, so I was hoping the ecoworthy was a viable option, which is what sent me down that particular rabbit hole in the first place.
Oh that seems to mostly be about how the provided adaptor from 5-15 to l14-30 adaptor cord doesnt work and you need to replace the L14-30 with a 5-15 plug for 120V operation.

Brucey

Depending on budget might be worth trying to run the ecoworthy with his larger non inverter generator, and then return if it doesnt work. Or I guess pony up the big bucks for the eg4 if it does indeed have a wider operating range.

BlackwaterPark

Quote from: Brucey on December 09, 2025, 06:05:19 PMDepending on budget might be worth trying to run the ecoworthy with his larger non inverter generator, and then return if it doesnt work. Or I guess pony up the big bucks for the eg4 if it does indeed have a wider operating range.

The thing was a steal when it was $350. Almost double that, no longer much of a steal, but I wouldn't hesitate to buy another if I needed one. Does the ecoworthy run both 120 and 240 in? Have you ran it full bore for a couple hours? I do tend to run my chargeverter at a hair below maximum for 3.5 hours at a time, and it throws the heat out for sure, but i've run it that way many many times, so I can speak to its robustness...at least the first gen one.

Brucey

Quote from: BlackwaterPark on December 09, 2025, 07:41:57 PM
Quote from: Brucey on December 09, 2025, 06:05:19 PMDepending on budget might be worth trying to run the ecoworthy with his larger non inverter generator, and then return if it doesnt work. Or I guess pony up the big bucks for the eg4 if it does indeed have a wider operating range.

The thing was a steal when it was $350. Almost double that, no longer much of a steal, but I wouldn't hesitate to buy another if I needed one. Does the ecoworthy run both 120 and 240 in? Have you ran it full bore for a couple hours? I do tend to run my chargeverter at a hair below maximum for 3.5 hours at a time, and it throws the heat out for sure, but i've run it that way many many times, so I can speak to its robustness...at least the first gen one.
Yeah been running it for 20 hours+ at a time with most of my panels totally snow covered, but its limited to 30A output with 120V input. It needs 240V to get to 60A output, which it does support but it doesnt have quick swap cables like I think the eg4 may come with? Louder than I'd like from cooling fan noise but apparently the eg4 may be even worse in that regard.

BlackwaterPark

yea, mine is loud certainly...but nowhere near as loud as one of my inverters (I run two completely separate systems in the same house tied into my mains with a transfer switch) when I used to use it for charging. It's a low freq unit , custom made, with these ridiculous three fans, that sound like a 747 winding up on the tarmac. It's so loud it's actually more impressive than it is annoying. Well, at least for the first few minutes.

It's a good sign that you can run for long periods of time like that, and the design of being essentially a pair of 110 chargers, sounds exactly like the chargerverter. Mine didn't come with cables though...you would have to swap the plug end or get your own adaptor. I guess one advantage of a setup like that is that if one of the chargers bit the dust, you'd at least have the other, even if limited to half functionality.

FNG

Quote from: Weldman on December 09, 2025, 03:43:21 PM
Quote from: Brucey on December 09, 2025, 10:43:43 AMHas your beta Rosie ever been replaced? Wonder if theres something busted in it.
Yes it has been replaced once so far. The last time it was replaced they were trying to mimic the temperatures that are out here and supposedly were going to try it on dry ice. I asked to see what they came up when they got it and tested it, didn't hear anything back.
Quote from: BlackwaterPark on December 09, 2025, 01:44:45 PM
Quote from: Weldman on December 04, 2025, 10:24:49 PM
Quote from: bigbillsd on December 03, 2025, 12:13:54 PM
Quote from: Weldman on December 02, 2025, 07:20:46 AM
Quote from: bigbillsd on November 29, 2025, 04:21:10 PMA 9.5Kw Genny is a good size.  Larger than my 7.5Kw QD.  Are you saying you need to keep messing with the Charge Amps?  Why?  What is it doing that makes you change it? 
Keeps kicking it off when they are too high, some updates it can run it up to around 80A, some updates only get it to around 30A.

That's not good.  I want to order one, but I keep reading about Genny issues and I only have one, so it must work whenever I need it. 

Will it still pass thru the generator power and just not charge the batteries or does it kick off the same for that too? 
You can have it where it just passes through and not charge the batteries or it charges the batteries while you are pulling from the batteries. When it is charging the batteries while pulling from the battery is where my problem is. Yes I need to buy a standalone battery charger for where I live.
I live in Montana off grid as in nearest neighbor is 3 miles away, cell phone is non existent without satellite, and it's an hour to town.

If it's any help, I gave up on the charger part of the "inverter/charger" units, and I don't bother with the one on my Rosie either. I use stand alones because they just work. I used to use Iota chargers, but the last three years i've been using the Chargeverter and it's done a really nice job, for whatever that's worth to you. It doesn't give two shits what your thd is, and is efficiency is about 97% when running 95a, as I run mine.
That helps a LOT! Where did you get yours from?
Sorry we didn't respond on the cold temperature bug but we did find it after your explanation and fixed it in software shortly after.

FNG

Quote from: BlackwaterPark on December 09, 2025, 05:43:41 PM
Quote from: Brucey on December 09, 2025, 05:16:12 PM
Quote from: BlackwaterPark on December 09, 2025, 05:08:42 PM
Quote from: Brucey on December 09, 2025, 04:55:54 PMI'm running one of these to charge my batteries versus Rosie (I'd be limited to a 15A 120V input due to how shes setup right now)

https://www.ebay.com/itm/127129496258

I'd suggest multiple units to give you redundancy



I've seen a LOT of people very unhappy with those ecoworthy chargers, as they seem to be very very picky about the THD output of the generator, much like all these inverter chargers. What kind of generator are you running through those?
Mines running via grid as double conversion at 30A output but also ran it on a Honda eu2200i generator for a bit to test, no worries. Mines a v1, the current v2 model also includes a soft ramp function so it doesnt hit generator hard if you have it set for the full 60A output on 240V for example.

There quite a few of us over on diysolarforum using them and I haven't heard of anyone having issues. Any particular forums or threads?


youtube videos is where I'm seeing all the comments on it. There are two videos in which it is tested and doesn't want to work with some generators. I'm guessing they can adjust the firmware though, in order to broaden the range it will accept. If most folk are running quality inverter generators like hondas or yamahas, I doubt you would have a problem, but it's the conventional ones that become an issue...very ubiquitous gensets like the predators and champions.
You are correct, The older firmware would not work with a few AVR's on the market. We spent some time recently and now have not been able to find a generator that does not work, If you find one let us know the make and model and we will procure one to test against.

FNG

Quote from: Weldman on November 27, 2025, 08:34:23 PMBeen running the Beta Rosie for about 2 years now, each time an update comes out it is either good or bad on what AAC I can charge my 1010Ah battery. Sometimes it's 18 AAC and pushing in about 80 plus amps other times it's like recent it's only 6 AAC of only 20 something amps. Running 9.5kW generator and wanting to know is my generator too small, what size should I be running or the max I need?
Could it be the variable loads causing this? A few things to note in no particular order
1- Breaker size is king and the Rosie will throttle the charger down to not exceed the breaker size in AC INPUT menu. So on a smaller generator if set properly the charge amps will move around based on the AC Loads
2- Newer code adds some adjustments in generator mode to allow for the full 120A charge so at the same AC Charge rate we would see more DC charge current


BlackwaterPark

Quote from: FNG on December 11, 2025, 06:37:14 AM
Quote from: BlackwaterPark on December 09, 2025, 05:43:41 PM
Quote from: Brucey on December 09, 2025, 05:16:12 PM
Quote from: BlackwaterPark on December 09, 2025, 05:08:42 PM
Quote from: Brucey on December 09, 2025, 04:55:54 PMI'm running one of these to charge my batteries versus Rosie (I'd be limited to a 15A 120V input due to how shes setup right now)

https://www.ebay.com/itm/127129496258

I'd suggest multiple units to give you redundancy



I've seen a LOT of people very unhappy with those ecoworthy chargers, as they seem to be very very picky about the THD output of the generator, much like all these inverter chargers. What kind of generator are you running through those?
Mines running via grid as double conversion at 30A output but also ran it on a Honda eu2200i generator for a bit to test, no worries. Mines a v1, the current v2 model also includes a soft ramp function so it doesnt hit generator hard if you have it set for the full 60A output on 240V for example.

There quite a few of us over on diysolarforum using them and I haven't heard of anyone having issues. Any particular forums or threads?


youtube videos is where I'm seeing all the comments on it. There are two videos in which it is tested and doesn't want to work with some generators. I'm guessing they can adjust the firmware though, in order to broaden the range it will accept. If most folk are running quality inverter generators like hondas or yamahas, I doubt you would have a problem, but it's the conventional ones that become an issue...very ubiquitous gensets like the predators and champions.
You are correct, The older firmware would not work with a few AVR's on the market. We spent some time recently and now have not been able to find a generator that does not work, If you find one let us know the make and model and we will procure one to test against.

I look forward to trying mine out in that case, thanks for the update!

Weldman

#29
Quote from: FNG on December 11, 2025, 06:40:43 AM
Quote from: Weldman on November 27, 2025, 08:34:23 PMBeen running the Beta Rosie for about 2 years now, each time an update comes out it is either good or bad on what AAC I can charge my 1010Ah battery. Sometimes it's 18 AAC and pushing in about 80 plus amps other times it's like recent it's only 6 AAC of only 20 something amps. Running 9.5kW generator and wanting to know is my generator too small, what size should I be running or the max I need?
Could it be the variable loads causing this? A few things to note in no particular order
1- Breaker size is king and the Rosie will throttle the charger down to not exceed the breaker size in AC INPUT menu. So on a smaller generator if set properly the charge amps will move around based on the AC Loads
2- Newer code adds some adjustments in generator mode to allow for the full 120A charge so at the same AC Charge rate we would see more DC charge current


I have had this generator since Rosie has came out, the amount of power drawn has only changed by one freezer added to the power load in all the years. Breaker size in the AC INPUT menu has never changed it has always been 60AAC. The only change that is constant and changes is the updates. Each update brings different results of how many amps can go into the battery from charging and I have seen 80A on updates. This is the far worst one yet, I'm on 7 AAC and it's still kicking the generator off after a few minutes of running then picks it back up.

I need to record and post the results with settings I have with a video on here.