Quote from: ClassicCrazy on October 21, 2025, 11:51:47 AMyeah a bit confusing - from manual at various places
I don't have a Rosie but was looking at this to try and figure out if I have my system grounding properly
It seems like it says you only need one 6 gauge ground wire from grounding busbar to a grounding rod ? As long as all the other interconnecting grounds are properly sized.
The pictorial is a bit confusing since there is a line that is showing the earth ( like in dirt ) but it almost looks like a conductor.
The green dotted line is not a conductor but just drawing a box around all the grounding points. So if you look at label #8 it shows the actual conductor going to ground rod . Some of the grounds in system pictorial are in black and some are in green . I didn't study it long enough to determine if that signifies internal grounds and external grounds in system .
Larry
MNROSIE7048 MANUAL
• The Rosie has two separate electrical systems – AC and DC; therefore, each electrical
system is required to be connected to a permanent, common, ground or earth reference
The easiest way to wire your ground system, and one that the NEC allows the smallest size
of GEC, is shown in Figure 10 below.
o Notice the single GEC-DC conductor (#8) – one connection in this entire system to
the ground rod
#8 – #6 AWG. Grounding Electrode Conductor (GEC-DC). Because the grounding system
has a common ground busbar (in the DC panel) and all EGCs, SBJs, and GECs are connected
to that ground busbar, and the system has only one GEC (the GEC-DC) to the ground rod,
the NEC allows for #6 AWG wire
Quote from: Brucey on October 07, 2025, 10:17:04 AMQuote from: BlackwaterPark on October 07, 2025, 06:58:53 AMI would suggest reading the Rosie manual it goes into great detail on system grounding and equipment grounding, starting on page 22:Quote from: aaapilot on October 06, 2025, 10:02:44 PMAnything metal in your system should be grounded. You are totally off-grid if I remember right. When you installed the main CB panel for the house, that panel has, or should have, a ground lug. I would either start there, or your main power source if it's not co-located, I.e. your inverter, start with the ground lug on that. Whichever is easiest to get to an outside ground bar. From that point, you simply run a ground wire to any metal box connected to the system. Ensure the size of the grounding wire is appropriate for the largest size of the wire you are using in your system.
yes, completely off grid, not near any poles at all actually. Question...if your objective is to connect every piece of metal to a ground bar, why can't you locate the ground bar indoors near your gear and then run a single lead to the rod? Wouldn't this save on copper and time? Also, the thickest wire in my system is OO for the battery leads (oversized for sure).... surely I wouldn't need a grounding lead of that heft...?
https://www.midnitesolar.com/pdfs/10-432-1_Rev_C_(MNROSIE7048_Manual)_22MAR2024.pdf
Quote from: Wizbandit on October 17, 2025, 05:10:27 PMIf ail you are trying to do is shut down a Rosie Inverter it's really simple. Rosie has a remote shutdown connection you just need to wire to the Bird House's aux relay. A tripped Birdhouse will engage the relay and shut down Rosie removing AC power from the house.Omg. I saw it before the two "pin", it never crossed my mind. I will use cat 5. 55 feet away between, and you say the " Bird House's aux relay" Okay. I'll try it in December when I see Rosie again. Thank you.
Quote from: Brucey on October 16, 2025, 04:56:03 PMQuote from: holdmode on October 15, 2025, 06:31:47 PMDoes it work on the mnedc125rts? I guess get those working first before you add the mnedc250rt for the rosie?Quote from: Brucey on October 15, 2025, 02:02:00 AMYes I have the MNBirdhouse connected to MNPV8HV-DLTL. But Rosie still alive. The picture from MidNite showing it is possible. I will wait For more inf. Thank you the input.Quote from: holdmode on October 12, 2025, 04:48:06 PMI did my search, what I need is (3) MN125rts and (3) MNBDM-48v. But the MNBDM, still working? Before starting buying I need confirmation this setting will be available to work.From what I can tell, one or more birdhouses initiate the signal over cat 5 to one or more mnbdms, to which the shunt trip breakers are connected. What's not clear to me is if/how many you can parallel multiple shunt trip breakers to a single mnbdm board. I would call or email Midnite to see.
Thank you for the suggestion and inputs.
Quote from: holdmode on October 15, 2025, 06:31:47 PMDoes it work on the mnedc125rts? I guess get those working first before you add the mnedc250rt for the rosie?Quote from: Brucey on October 15, 2025, 02:02:00 AMYes I have the MNBirdhouse connected to MNPV8HV-DLTL. But Rosie still alive. The picture from MidNite showing it is possible. I will wait For more inf. Thank you the input.Quote from: holdmode on October 12, 2025, 04:48:06 PMI did my search, what I need is (3) MN125rts and (3) MNBDM-48v. But the MNBDM, still working? Before starting buying I need confirmation this setting will be available to work.From what I can tell, one or more birdhouses initiate the signal over cat 5 to one or more mnbdms, to which the shunt trip breakers are connected. What's not clear to me is if/how many you can parallel multiple shunt trip breakers to a single mnbdm board. I would call or email Midnite to see.
Thank you for the suggestion and inputs.
Quote from: Wizbandit on October 16, 2025, 04:16:20 AMThanks for the info James. Is it possible to connect multiple midnite shunt trip breakers to the output of the MNBDM-48v? Say four of them? Any limits?Quote from: holdmode on October 15, 2025, 06:31:47 PMQuote from: Brucey on October 15, 2025, 02:02:00 AMYes I have the MNBirdhouse connected to MNPV8HV-DLTL. But Rosie still alive. The picture from MidNite showing it is possible. I will wait For more inf. Thank you the input.Quote from: holdmode on October 12, 2025, 04:48:06 PMI did my search, what I need is (3) MN125rts and (3) MNBDM-48v. But the MNBDM, still working? Before starting buying I need confirmation this setting will be available to work.From what I can tell, one or more birdhouses initiate the signal over cat 5 to one or more mnbdms, to which the shunt trip breakers are connected. What's not clear to me is if/how many you can parallel multiple shunt trip breakers to a single mnbdm board. I would call or email Midnite to see.
Thank you for the suggestion and inputs.
The BIRD HOUSE system was discontinued and last I checked all spare parts are used up. No plans on more...
Very little support available on any existing NOS you find. Only one person (me) left with any trouble-shooting knowledge...
CAUTION - The Remote Trip breakers can not be used with a switch of any kind, they use an electronic device to apply a 1/10th second pulse, much longer Will burn out the trip coil....
JAMES
Quote from: holdmode on October 15, 2025, 06:31:47 PMQuote from: Brucey on October 15, 2025, 02:02:00 AMYes I have the MNBirdhouse connected to MNPV8HV-DLTL. But Rosie still alive. The picture from MidNite showing it is possible. I will wait For more inf. Thank you the input.Quote from: holdmode on October 12, 2025, 04:48:06 PMI did my search, what I need is (3) MN125rts and (3) MNBDM-48v. But the MNBDM, still working? Before starting buying I need confirmation this setting will be available to work.From what I can tell, one or more birdhouses initiate the signal over cat 5 to one or more mnbdms, to which the shunt trip breakers are connected. What's not clear to me is if/how many you can parallel multiple shunt trip breakers to a single mnbdm board. I would call or email Midnite to see.
Thank you for the suggestion and inputs.