Classic shut down: MODE = OFF Orange LED on MNGP blinking

Started by Westbranch, April 21, 2014, 07:44:43 PM

Previous topic - Next topic

boB


But  65  (decimal) is   41  (hexadecimal).

So, when possible, tell your age in hex rather than decimal.

boB
K7IQ 🌛  He/She/Me

Westbranch

Hi boB, re Temps, were you after current temps? or is there a historical listing?

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

boB

Quote from: Westbranch on April 29, 2014, 09:46:19 PM
Hi boB, re Temps, were you after current temps? or is there a historical listing?


If this was regarding the yellow LED, probably the temperatures read at that time would be great.
PCB temp and FET temp.
K7IQ 🌛  He/She/Me

Westbranch

Sorry, did not read them at the discovery of shutdown... 
BTW the fans have not come on AFAIK except at powerup/startup.  Basement is a cool 8*C pretty much full time till summer heat starts
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Resthome

Quote from: Westbranch on April 30, 2014, 11:35:35 AM
Sorry, did not read them at the discovery of shutdown... 
BTW the fans have not come on AFAIK except at powerup/startup.  Basement is a cool 8*C pretty much full time till summer heat starts

You can read the Hi FET temp history in the Daily Logs, but not the PCB Temp.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Vic

FWIW,  one Classic 150 here also went to rest,  Mode = Off.

This occurred while this Classic was in Absorb,  delivering about 20 CC Amp  (about half way through Absorb in time),  WHILE I was navigating from the Main Status page to the WBjr status page.  Heard the input relay open,  went back to the main status page,  saw Classic resting,  mode off.

RFR was 104.  Looked like the Classic went through at least part of a boot phase,  with the LEDs inside the front vent were swept,  and,  IIRC,  the Amber LED on the front left,  believe the Limit LED went on.

48 V system,  String Vmp = 106 V
Classic 3677  FW 1772
MNGP FW 1608

The ambient temp was about 64 F.  Vin was probably about 108 - 110 V.

Did not look at any of the Classic temps

Have never seen this in any Classic here.

Should UD the MNGP FW at the least ...   Thanks,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Resthome

Quote from: Vic on May 01, 2014, 04:32:27 PM
FWIW,  one Classic 150 here also went to rest,  Mode = Off.

This occurred while this Classic was in Absorb,  delivering about 20 CC Amp  (about half way through Absorb in time),  WHILE I was navigating from the Main Status page to the WBjr status page.  Heard the input relay open,  went back to the main status page,  saw Classic resting,  mode off.

RFR was 104.  Looked like the Classic went through at least part of a boot phase,  with the LEDs inside the front vent were swept,  and,  IIRC,  the Amber LED on the front left,  believe the Limit LED went on.

48 V system,  String Vmp = 106 V
Classic 3677  FW 1772
MNGP FW 1608

The ambient temp was about 64 F.  Vin was probably about 118 V.

Did not look at any of the Classic temps

Have never seen this in any Classic here.

Should UD the MNGP FW at the least ...   Thanks,   Vic
Vic.. the current beta FW has updates for Classic, MNGP, & Network that seem to be pretty stable here. Classic 1849  4/21/14, MNGP 1821  4/14/14, Network 1839

boB has been working hard to resolve a lot of the 104 Watch Dog Timer reset.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Vic

Hi John,

Yea,  have little to loose in doing updates to the Classic and MNGP ...  should have mentioned that I have not ever used the Local App.

Had followed much of the conversation about Resting events,  but somehow I had missed that these events were Mode Off events.   Realize that if the Classic is Resting,   it is not delivering power at that time,  but had FELT that the Classic might/probably would recover on its own,  at least,  in time.

Mode Off means to me that the Classic has no mechanism to recover to Mode ON,  on its own,  requiring manual intervention.

The system mentioned above is at a residence location,  and  is usually attended,  and therefore,  there is a good chance of a human intervening,  usually with no more than three or four days delay.

Anyway,  will probably do FW UDs in the next few days,  thanks for the guidance.     Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Resthome

Vic the HI FET temp is found in the Classic LOG menu under Daily so you can go back in time to see a historical view for each day. No need for the local app.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Vic

Hi John,

Saw that you mentioned that FET Temp is avail in the Log earlier in this Thread ...   expect that this was not the issue.   The A/C in that power room was on MAX,  and the temp there was 64 F ...  and the Turbo Fan just never runs.

The Vin on this system is a bit high,  so CCs run a bit warmer than most.

Will try to look at the Log to see ...  customarily,  the FETs are not so hot.

Thanks again.    Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Resthome

At peak bulk I see my FET temp around 45-46 C with the Classic pushing around 50A.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Westbranch

Andrew, my question about the PC recognizing a 'new device' has been connected to the PC seems to have got missed in the other chatter...

I got to step 13 in the FW install instructions, and the PC does not 'ding dong' and say ' New device  or whatever'  is connected...  it just does not 'see' the classic connection at all.

Any ideas as to what I can check?

tks
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Resthome

Quote from: Westbranch on May 04, 2014, 11:40:04 PM
Andrew, my question about the PC recognizing a 'new device' has been connected to the PC seems to have got missed in the other chatter...

I got to step 13 in the FW install instructions, and the PC does not 'ding dong' and say ' New device  or whatever'  is connected...  it just does not 'see' the classic connection at all.

Any ideas as to what I can check?

tks
If you have done firmware updates with this PC before the driver is already installed and you shouldn't see this step. Only happens with a new install. I just go to step 28. If you have never install the firmware updater on this PC then you might want to try another USB cable from the Classic to the PC.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Westbranch

Hi John, this is the first time through the process's of either FW update or LA use.

The USB cable is the one supplied by MN and I think is > 2 feet (it is still partially coiled/tied for neatness).  I got the same 'no response' from both classics, separate cables,  so I did not suspect the cables.  Bad install of GUI?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

boB


WB, what is your OS again ?
Windoze ?  *nix ?  etc ?
K7IQ 🌛  He/She/Me