Imput capacity of the Classic 200

Started by morasolar, July 31, 2014, 12:11:01 PM

Previous topic - Next topic

morasolar

I am in the process of setting up a grid tie 48v solar system. Using 30.6v, 8.43a rated solar modules, how many modules can I string in series and how many strings will the Classic 200 safely handle?   

TomW

Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

vtmaps

Quote from: morasolar on July 31, 2014, 12:11:01 PM
I am in the process of setting up a grid tie 48v solar system. Using 30.6v, 8.43a rated solar modules, how many modules can I string in series and how many strings will the Classic 200 safely handle?   

Welcome to the forum,

After you use the string sizer, you will get a number of panels that you can put in series.  But just because you can use that many in series doesn't man you should.  All of the classics are more efficient and have greater watt-handling capacity with lower string voltages.

With a 48 volt battery and panel Vmp = 30.6 volt, your OPTIMUM configuration will be strings of 3 panels.  Using  Classic 150 you can handle 4800 watts with that configuration.

The only reason to use higher voltage strings is if the distance between the array and the controller is very large.  You will have less power handling capacity with higher voltage strings.  How far is the distance?

--vtMaps

morasolar

Thank you all for your response, my distance should be less than 75'.  Isn't higher voltage desirable, to decrease resistance. I was hopping for 4 or 5 strings of 4 modules, but the string sizing tool tells me that with the Classic 200, 3 strings of 4 modules is the right configuration for a hot Florida roof.

Westbranch

The closer the string Voltage is to the bank voltage, the less power that is lost to heat in the CC due to down conversion of ie 91V +- TO 48V WILL NOT GENERATE AS MUCH HEAT  as 120V or 150V will.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

vtmaps

#5
Quote from: Westbranch on July 31, 2014, 05:32:34 PM
The closer the string Voltage is to the bank voltage, the less power that is lost to heat in the CC due to down conversion of ie 91V +- TO 48V WILL NOT GENERATE AS MUCH HEAT  as 120V or 150V will.

Quite right.  To explain further: A higher voltage means a bit less line loss in the cable, but more loss in the controller.  The higher voltage very often means that you are trading heat production in the cable for heat production in the controller.

Suppose you had 15 panels (Vmp = 30.6 Imp = 8.43) which is an array size of 3870 watts.  Consider the numbers for 75 ft (one way) of #6 copper cable.  I will give the numbers for 5 strings of three panels (string voltage of 91.7999) and 3 strings of five panels (string voltage of 153 volts). 

With Vmp of 91.8 the Classic 150 can handle over 4800 watts.  The voltage drop will be 2.75%.  At full nameplate power (3870 watts, seldom achieved, and only briefly) the power loss in the #6 cable will be 107.4 watts.  Realize that the power lost in the cable goes as the square of the power that the controller is handling, so at more typical power levels the power lost in the cable is much, much less.  This is a good conservative design... your peak power is almost 1000 watts below what a Classic 150 can handle.

Consider what happens with the same array configured with a Vmp = 153.  The same #6 cable has a 1.0% voltage drop and at full nameplate power (3870 watts, seldom achieved, and only briefly) the power lost in the cable is 38.7 watts.  But what about the controller?  You will need a less efficient Classic 200 to handle the higher voltage.  The Classic 200 with a 153 volt input voltage is rated to handle just a bit below 3800 watts.  Your array is more than it can handle... not good conservative design.  The reason is efficiency.  Midnite has not produced efficiency curves for the Classic, but the Midnite engineers have indicated on these forums that the curves are probably similar to the Outback efficiency curves (no surprise... the cofounders of Midnite cofounded Outback). 

Getting back on topic, the Outback and probably the Classic are about 2% more efficient at the lower string voltage.  At full power, 2% of a 3870 watt array is 77.4 watts.  That's more than the difference in cable loss between the two voltages.  And the 2% efficiency difference is throughout most of the power range, where as the cable loss decreases as the square of the input power decreasing.  That means the advantage shifts much more in favor of the low voltage at the more typical power levels that an array runs at.

As I wrote in the first paragraph of this post: The higher voltage very often means that you are trading heat production in the cable for heat production in the controller.  If it makes you crazy to lose power in the cable, just use #4 cable instead of #6.

Getting back to conservative design, the reason that the Classic is rated to handle so much less power at higher voltages is the 2% hit to efficiency.  Try putting a 77 watt lightbulb inside a metal box the size of a classic... it gets very hot!  At higher voltages the controller has to be derated to handle all the extra heat.

Here's a quote from Robin Gudgel, co-founder of Outback and Midnite:
http://midniteforum.com/index.php?topic=324.msg1869#msg1869
QuoteMax power for the Classic 250 is somewhere between 3000 and 3500 watts depending on your system configuration.
<snip>
I would not put more than 3000 watts on the Classic 250 myself. It will just run hot. That is never a good idea to run the controller flat out at its maximum day after day.

--vtMaps

EDIT: I changed 91.eight) to 91.7999) because this forum turns the "point eight)" into some sort of smiley.

here's what happens if I type 91.eight) as all numbers:
91.8)

dgd

Vtmaps,

That was a good detailed explanation  :)

Sort of reminded me of when the MX60 appeared and the option was there to get it up to 70 amps output. Then it did heat up.
Various solutions for this heat dispersion were interesting, from the fitting of a small cross flow extraction fan to one of the wire openings to removing the bottom cover and rigging a boxer fan to push air around.
I just used some 10mm thick aluminum plate between the MX60 and plywood wall which seemed to disperse excess heat.
Have not seen the C150 get hot enough to consider this

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

mike90045

Quote from: dgd on August 01, 2014, 10:07:44 PM
....I just used some 10mm thick aluminum plate between the MX60 and plywood wall which seemed to disperse excess heat.
Have not seen the C150 get hot enough to consider

I think I'm going to get me some of that stuff and sandwich it into my wall mount.  Save the fans that run all day.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Westbranch

have a machinist or welder make it like this (bottom view)
     _______
__|             |__


where the heat source is on the top solid line and the feet are attached to the wall line and it will vent naturally when mounted vertically on the wall
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

mike90045

#9
I was thinking of a U channel, with fins about 2" outboard from the Classic:

|                      |
|___________|   easier to bend, and more free air contact, more convection.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Westbranch

Morning Mike, looks like we are the same thing, so just to be clear here is a bit more of what I meant


             _   Classic__
       ___|                   |__  < Angle Alum.
   
Wall---------------------------------------
       
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come