communication problem with ethernet and status panel application.

Started by bafaro, September 09, 2015, 11:59:05 AM

Previous topic - Next topic

bafaro

For several days, my two classic 150 on the four I own, no longer communicate with status panel application. He also refused to take an IP address in DHCP mode, indicating an ethernet communication problem.
Last night I made the last update Firmware revision in 2056, despite this there is still no communication. I need your help.

Thank you.

Westbranch

Are all the Classics set to "STATIC"  rather than DYNAMIC mode?

Are the Classics hard wired to a switch and then a bridge or ?

Have you done a Factory /reset (VMM)?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

bafaro

every oven classic have a different static IP address. They were all in working for a long time without problems. oven are linked to the floor by a oven- port switch that is connected to the route located on the ground floor.
Yes I did a factory restart after updating as usual for all the updates.

Thanks

bafaro

After turning off the power to the switch Internet connections, everything is back in order when I reconnected.

Westbranch

Bafaro, I don't understand...  A Factory reset involves shutting off  ALL the power to your Classic,  I turn off the PV and then the battery then turning the battery on first  and then the PV....   I don't understand how you would have had power to the switch, if that was the problem...  if you have a battery disconnect circuit breaker in the system...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

bafaro

My problem was the level of communication between the classic and the application for the status panel. As the Ethernet connection is made through a switch that is powered by electricity, so I thought disconnect and reconnect the cables for communication back.

mahendra

did all of that did not help i changed the ip address although it was different ,it seemed to work.
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

Westbranch

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

bafaro

I was talking about the Ethernet switch for my four classic.

Westbranch

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come