Charge rate specs AGM

Started by tecnodave, October 13, 2016, 02:11:25 PM

Previous topic - Next topic

tecnodave



I have recently scrounged a bunch of CD Technologies VRLA batteries.

The manufacturers charge rate spec is a bit baffling to me:

"C/5 @ 20 hour rate @ 25deg C."

I'm assuming that they are talking about the discharge rate for the 20 hour constant discharge

So: 5/5 .....1 amp??

Or maybe more like high flyer suggested C20/.025   2.5 amps. With max current C20/.035   3.5 amp

These are standby batteries that have a high discharge rate but apparently a slow charge rate


Model TEL-105-FS

109 a.h. @ 20 hour rate

These are from the Long Duration Series. Phone company backup batteries.

Dave
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

SuperTed

Hi
i'd think they mean (1/5 of c20) amps  = 109/5   = 21.8 amps max up to 14.4 or 14.8v per 12V battery
Cheers

Westbranch

go here.... and have a thorough read  :)   ;)  http://www.cdtechno.com/pdf/ref/41_2128_0212.pdf

to be found here  http://www.cdtechno.com/resource/support_doc.html   :D

I'll try to dig in but the value they are posting IMHO is for a GT charger tat can pump out constants Amps.

I use an EA of 5 with the WBjr on a 900Ah 24 V setup
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

tecnodave

im concerned because some of the batteries audibly vent at charge rates above 3.5 amps, apparently they have been abused, the best set will accept sustained 15 amp charge rate, with 4 batteries in series using settings from rolls-surrette battery manual for VRLA , in any case they have been abused....3 banks in parallel driving a 10 kW powermax inverter. (or whatever the name of that Chinese inverter that everyone seems to smoke).he had one smoked one there....charged by 2 FM-80's

WB,

thanks for that lead, I downloaded it into my battery library. It seems that that they recommend charge rates up to C/5 or C/4 for fast charging with voltage limited to 2.4 v.p.c.

Dave
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

mike90045

1) Generally, those are disposable telcom batteries,  they get cycled 3 or 4 times and then get replaced.  They are not deep cycle batteries and will fail after a couple hundred deep cycles, just designed to keep a telcom center working until the generators get running.

2) if you are getting venting from them, you are overcharging and loosing electrolyte (H2o as H & o2 gas)  each vent episode damages them more
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV